Old 08-11-2015, 04:47 PM   #29
Commercial Member
 
tractors1's Avatar
 
Name: Charlie Y
Trailer: Escape 21 - Felicity
Oregon
Posts: 1,127
Quote:
Originally Posted by Darral T. View Post

I looked at the Progressive Industries EMS you listed. I wish there were some reviews on it somewhere. I like the sound of what it does. While I've never used one, I still dont think they're a bad idea. Just more insurance in my book.

To be honest, I was going to buy one of the nicer ones at Camping World and one of their techs just flat talked me out of it!
The Progressive EMS is the standard option for Escape trailers. I've had two shutdowns at campgrounds for an open ground (it displays an error code for what the problem is with the incoming power.) You can override it if you decide things are worth the risk by turning it off. When first powered up, it takes about 3 minutes to examine the incoming power before it will energize the trailer.
__________________

__________________
Charlie Y

Don't drill holes, try custom storage you design: http://RVWidgetWorks.com
tractors1 is offline   Reply With Quote
Old 08-11-2015, 08:01 PM   #30
Member
 
Vanderscamper's Avatar
 
Name: Carol & Jim
Trailer: New 2015 16' Scamp
Georgia
Posts: 33
Talked to David Smith in Backus today and said we should be done by Aug 19. He will have talked to the fella who does the delivery driving before then , so we should have the 16' layout 6 VanderScamp by Aug 23. So many things to worry about!@!!!
__________________

__________________
Vanderscamper is offline   Reply With Quote
Old 08-11-2015, 08:35 PM   #31
CPW
Senior Member
 
CPW's Avatar
 
Name: Carl
Trailer: 2015 Escape 5.0TA
Flori-duh!
Posts: 935
Registry
All this talk about 15, 20, and 30 amp circuits and A/C. The truth is that it is the circuit breaker (or fuse) which controls how much current is passing through the wire. Different gauge wires are approved for different amperages. For example, 12 gauge wire is rated for 20 amps, 10 gauge for 30, and 14 gauge for 15 amps. The breaker is designed to trip or the fuse to blow if its rating is exceeded, to prevent wires that are too small for the current passing through them from melting and causing a fire. For example, if an appliance is demanding 21 amps and the breaker is a 20 amp, the breaker will trip thereby cutting off all current. The bottom line is that if you plug your A/C into a 15 amp circuit and it runs without tripping the breaker, then its amperage demand is less than the 15 amps the breaker will allow to pass without tripping. Most small trailers have 30 amp plugs for 30 amp circuits because they are expected to supply adequate current for running the A/C, the microwave, lights, and all other on-board accessories at the same time. Theoretically, all of them do not add up to 30 amps. You run into trouble and trip breakers when everything inside is running, and you decide to blow dry your hair and the hair dryer pushes demand over 30 amps.
If you plug the trailer into a 20 amp outlet with a cord rated for 20 amps meaning it can deliver 20 amps and the A/C runs, you simply are NOT going to damage it. And even though adapters may be rated at 15 amps or whatever, they are totally capable of delivering 20 amps. The A/C in my trailer, when running, draws approximately 14 amps, so supplying it with 20 amps and not 30 amps is NOT detrimental.
__________________
CPW is offline   Reply With Quote
Old 08-11-2015, 08:51 PM   #32
Senior Member
 
Name: Gordon
Trailer: 2015 Scamp (16 Std Layout 4) with '15 Toyota Sienna LE Tug
North Carolina
Posts: 1,886
Quote:
Originally Posted by CPW View Post
... The A/C in my trailer, when running, draws approximately 14 amps, so supplying it with 20 amps and not 30 amps is NOT detrimental.
But when the AC starts up it draws the "Locked Rotor Amps (LRA)" which is about 70 amps.. the only reason the 20 amp breaker does not trip is that the breaker tolerates current surges over its rating for very brief periods of time.

A 15 amp breaker tolerates less surge current.

You don't want to repeatedly starts up an AC unit with a power source that cannot supply the LRA (for the very brief time it needs it).
__________________
gordon2 is online now   Reply With Quote
Old 08-11-2015, 09:21 PM   #33
CPW
Senior Member
 
CPW's Avatar
 
Name: Carl
Trailer: 2015 Escape 5.0TA
Flori-duh!
Posts: 935
Registry
Quote:
Originally Posted by gordon2 View Post
But when the AC starts up it draws the "Locked Rotor Amps (LRA)" which is about 70 amps.. the only reason the 20 amp breaker does not trip is that the breaker tolerates current surges over its rating for very brief periods of time.

A 15 amp breaker tolerates less surge current.

You don't want to repeatedly starts up an AC unit with a power source that cannot supply the LRA (for the very brief time it needs it).
In theory, Gordon, yes, but in practical reality, not so much. Many of the RV A/C manufacturers are building in hard start capacitors, and they can be added to older units if there is any concern to provide any necessary start-up surge. I am far more worried about brown outs damaging my A/C unit than running it on a 20 amp circuit, and have never, in 40+ years of RVing ever damaged an A/C unit by running it on a circuit smaller than the trailer plug needs, and most of that time was without a hard start capacitor. And I would be more concerned about individuals trying to run A/C units with marginally powered generators. As I see it, there is no need to create unnecessary panic. That is my opinion, and if you do not see it that way, I can respect your opinion and your right to it. I just do not concur. And I thought all the hype over Y2K was a bunch of BS, also.


I also realize that a lot of older homes have 15 amp circuits. Most new construction has nothing smaller than 20 amp.
__________________
CPW is offline   Reply With Quote
Old 08-11-2015, 09:42 PM   #34
Senior Member
 
Name: Gordon
Trailer: 2015 Scamp (16 Std Layout 4) with '15 Toyota Sienna LE Tug
North Carolina
Posts: 1,886
Quote:
Originally Posted by CPW View Post
1. I am far more worried about brown outs damaging my A/C unit than running it on a 20 amp circuit,...

2. And I would be more concerned about individuals trying to run A/C units with marginally powered generators. ...

3. And I thought all the hype over Y2K was a bunch of BS, also.

4. I also realize that a lot of older homes have 15 amp circuits. Most new construction has nothing smaller than 20 amp.
I could not agree more with points 1 and 2. You are right on there.
Thats the reason I plan to add this to my trailer before running the AC.
(And for the record.. the 20 amp circuit is what I understand is supposed to be used for most RV AV units, at least the rooftop ones. Using a 15 amp circuit is questionable IMHO)

RE: # 3... I was one of the few who laughed at all the panic before Y2k.

Re #4: I think that some of this discussion was prompted by the report that Scamp was only using a 15 amp circuit for the AC in their trailers even though the AC manufacturer called for 20.
__________________
gordon2 is online now   Reply With Quote
Old 08-12-2015, 12:10 AM   #35
Senior Member
 
Name: Darral
Trailer: Scamp Standard 13' 2010
Tennessee
Posts: 1,443
You're EXACTLY right Gordon. I was the one that discovered that Scamp put a 15A breaker and 14ga wire in my Scamp when Coleman explicitly states in their documentation to not use less than a 20A breaker and 12Ga wire.

I run the heat strip and it pushes the envelope at 14A when it's running! My point was, I had spoken to Kent Eveland and told him about it. He brushed it off. But I made it clear to him that day that IF I was to ever purchase another Scamp, he'd put the recommended wire/breaker in there that the equipment manufacturer called for or I would leave it sitting in Backus!! That still stands.

So CPW, I'm sorry but I disagree with you. And if you concur that it's ok what Scamp did and doesnt see the need to or simply wont change it, then in my opinion, you are wrong! And it has nothing to do with panic...no one's in a panic.
__________________
Darral T. is offline   Reply With Quote
Old 08-12-2015, 02:31 PM   #36
CPW
Senior Member
 
CPW's Avatar
 
Name: Carl
Trailer: 2015 Escape 5.0TA
Flori-duh!
Posts: 935
Registry
Delivery in 1 week

Quote:
Originally Posted by Darral T. View Post
So CPW, I'm sorry but I disagree with you. And if you concur that it's ok what Scamp did and doesnt see the need to or simply wont change it, then in my opinion, you are wrong! And it has nothing to do with panic...no one's in a panic.

No apology necessary, Darral T, but had you read my post carefully, you would see that I was not advocating running an A/C on 15 amps, I said it would not be detrimental to run it on 20 amps. I did say that if it were run on 15 amps and it did not trip the breaker, then it was "demanding" less current than the 15 amp would allow to flow. And the panic to which I referred was the implication in previous posts that if you don't plug into a 30 amp outlet, A/C damage would occur. Some people with little understanding of electrical circuits do panic over this type of misinformation. I do not in any way condone what Scamp does. I owned a Scamp and sold it after I came to the conclusion that Scamp was an acronym, and my acronym is not complimentary of what Kent and his cohorts do in Backus. While I won't post my "interpretation" (my opinion) as to what Scamp stands for publically, PM me if you just cannot live without knowing what I feel the name really means. With that you might just agree.


Sent from my iPhone using Fiberglass RV
__________________
CPW is offline   Reply With Quote
Old 08-12-2015, 02:50 PM   #37
Senior Member
 
Name: Darral
Trailer: Scamp Standard 13' 2010
Tennessee
Posts: 1,443
We're not far off base from out point of views.

It's VERY easy to wander off track during online forum topics from misunderstandings.

I agree 100% with you on being able to run off of 15A circuits. I do it all the time with my Scamp and 15A adapter at home. I've taken it to son-in-law's house...15A on their carport. But, I dont feel comfortable running my heat strip over night with 15A....20A yes. But the A/C (except for the 'stall' amps (LRA) I believe it was) doesnt pull continuously what my heat strip does...I've checked them both. But I agree with Gordon; I'd STILL much prefer a larger breaker and not run close to the edge! Kent Eveland could not be convinced of that! I bet he's STILL putting 15A on A/C's with heatstrips. I'd love to know!

All in all, if you had to plug into a 30A ONLY? My A/C would have been gone YEARS ago.

I just recently laid another myth aside. I've heard if your generator runs out of gas it will burn up your A/C. I have an old cheap one going out (freezing up) so I decided to test it. For about 7-8 times, I would shut the fuel off on my Champion 3500-4000 and let it "run out" of gas with the A/C AND compressor running. One thing I noticed, the generator- once it started pulsating when it was running out...it would get to a point, shut down and quickly come to a stop! Not so not under a load and with a normal shutdown....it coasts considerably. Maybe it's because the generator is under the load and it acts as a brake. Regardless, it never hurt the A/C. Fun stuff!
__________________
Darral T. is offline   Reply With Quote
Old 08-12-2015, 04:04 PM   #38
CPW
Senior Member
 
CPW's Avatar
 
Name: Carl
Trailer: 2015 Escape 5.0TA
Flori-duh!
Posts: 935
Registry
Quote:
Originally Posted by Darral T. View Post
It's VERY easy to wander off track during online forum topics from misunderstandings.
Totally agree with you on this. I've often thought (and said) that if these discussions were around a campfire rather than a computer keyboard, any statements made could be immediately questioned and clarified. Also, disagreements do not get people as hot under the collar when in a social setting rather than an electronic setting. But unfortunately we cannot always be camping at the same place or all year long, so unfortunately, misunderstandings will always exist on this type of forum. That, and a lot of people, myself included, do not always convey exactly what they mean to convey. Still, I find the exchange of opinions, experiences, ideas, and knowledge here to be informative and beneficial.
__________________
CPW is offline   Reply With Quote
Old 08-12-2015, 05:07 PM   #39
Senior Member
 
Name: Gordon
Trailer: 2015 Scamp (16 Std Layout 4) with '15 Toyota Sienna LE Tug
North Carolina
Posts: 1,886
Quote:
Originally Posted by CPW View Post
Totally agree with you on this. I've often thought (and said) that if these discussions were around a campfire ....

Speaking of campfires... what do you think of .... oh wait, if we get THAT far off topic we will never find our way back

In fact, right now I have no idea what this thread is about but I seem to recall it being something about the energy resulting from the existence of charged particles (such as electrons or protons), either statically as an accumulation of charge or dynamically as a current, and how to transfer that power and harness it to reduce the average kinetic energy in an enclosed space.

Anyway William, if you have not run away yet, how is the Casita working out for you?
__________________

__________________
gordon2 is online now   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Week Camping in Alaska - 3 Week Stay Adrian W Camping, Campout Reports 16 08-11-2011 05:33 PM
New greywater tank delivery! Christine V General Chat 0 08-28-2007 09:32 AM
Help with Trillium Delivery Brenda Novakovski General Chat 0 07-04-2007 12:10 PM
A Quantum Delivery Hershal Byrd General Chat 3 10-01-2006 08:18 PM
todays delivery! Christi V. General Chat 8 02-19-2006 11:32 PM

» Upcoming Events
No events scheduled in
the next 465 days.
» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 07:15 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.