Thank you to all who have helped with my wiring education so far. I put out a call for 110v stranded wire and got a lot more comments than I expected.

I just made a closer examination of the breaker box that came with the trailer. It has a 15 amp breaker in it. Since I'd like to add more outlets and lights, more juice is needed. I see now that I can put in another 15 amp breaker with another line coming out the other side of the box, going to these additional outlets.

Judging by the photos below, is this assumption correct? Also I presume this is the original box and breaker. Is it necessary to replace the original 15 amp breaker for a new one?

Fran
compact II '74

Attached Thumbnails
breakerbx1.jpg   breakerbx2.jpg  

breakerbx3.jpg  
francene is offline   Reply With Quote
Old 01-04-2010, 11:54 PM   #2
Senior Member
 
peterh's Avatar
 
Trailer: 2005 19 ft Scamp 19 ft 5th Wheel
Posts: 1,555
Registry
Hi Fran,

Generally circuit breakers divide the wiring in your house or trailer up into functions. In a house, for example, one 15 amp circuit might be used for all the outlets in the kitchen, but the microwave, stove, garbage disposal, and dishwasher each have their own, separate breaker. In a trailer it works in the same general manner. Our 5th wheel, for example, has four breakers: one for the 12v converter/charger, one for the the refrigerator, and one for the microwave.

Many older trailers, like our Surfside, have just one breaker that covers all the lights, outlets, 'fridge, and battery charger.

With that in mind I would suggest adding your new outlets to the same circuit your existing outlets are on, but would suggest that you add separate circuits for any other new equipment you might add, like a converter or 2/3-way 'fridge.
peterh is offline   Reply With Quote
Old 01-05-2010, 07:08 PM   #3
Senior Member
 
Joe MacDonald's Avatar
 
Trailer: 1981 Trillium 5500
Posts: 1,158
You can add another breaker to that box if you can find one, but watch the cost. a lot of the older breakers are just as expensive as getting a new 2 or 4 gang breaker box with breakers already in it. I was lucky enough to have extra breakers on hand for the box in my trillium, as I am an electrician, and keep all the older breakers I get (sorry, don't have your type).
I added a circuit for an outside plug, a water heater and a new charger unit.
Joe
Joe MacDonald is offline   Reply With Quote
Old 01-05-2010, 09:31 PM   #4
Senior Member
 
Trailer: 1973 Compact Jr
Posts: 532
Fran, if it's a Zinsco breaker, replace it with something better. I've had bad experiences with Zinsco breakers, and of course the breaker that was in my Compact Jr was a Zinsco. Made sense -- the Compact Jr was a cheap trailer and Zinsco was a cheap breaker.

In years past Square-D was a good brand, but I have not kept up with what's good currently.
Dana T is offline   Reply With Quote
Old 01-05-2010, 11:01 PM   #5
Senior Member
 
francene's Avatar
 
Trailer: 13 ft Compact II
Posts: 524
Registry
Hi Dana,
The breaker is a Stab-Lok by Federal Pacific Electric, and after looking it up online, it too does not have a good history- the word 'fire' came up, and the company is out of business, no surprise. I'll just get a new box and 2 breakers and start over.

Thanks,
Fran
francene is offline   Reply With Quote
Old 01-06-2010, 01:28 PM   #6
Senior Member
 
Vicki A.'s Avatar
 
Trailer: 1984 Perris Pacer ('Tillie')
Posts: 157
Okay...all of this talk about a larger breaker box, made me wonder if I need something larger also.
My pacer has a 15 amp breaker. Normally I would not have much on, a light or two. But there is an air conditioner hooked up. The side of the A/C says it is 6500 BTU and draws 6.1 amps. If nothing else, except maybe a light was on, do I need to up grade. Demo and building I can do, electrical stuff I'm a dud!
Thanks, Vicki
Vicki A. is offline   Reply With Quote
Old 01-06-2010, 02:25 PM   #7
Member
 
Don H.'s Avatar
 
Trailer: 1974 Hunter I
Posts: 70
Registry
Quote:
Hi Dana,
The breaker is a Stab-Lok by Federal Pacific Electric, and after looking it up online, it too does not have a good history- the word 'fire' came up, and the company is out of business, no surprise. I'll just get a new box and 2 breakers and start over.

Thanks,
Fran
Oops! I bought the FPE 2-circuit box below from a surplus company online. It's a NOS unit, apparently from military surplus, made in the 1960s. (Maybe be identical to the ones they put in the new Compacts?) I thought it was a bargain at $15, until I looked into the problems that you mention.

I see that the malfunctions seem to be in connection with Stab-lok breakers. Don't know if they made "Stab-lok" breakers back then, but I guess it doesn't matter, since they could be defective regardless of whatever trade name they might have used at the time.

I hope there's a way I can just test it to make sure it's operating correctly. Otherwise, looks like I'll also be searching for a new box.

BTW, this has two 15-amp breakers ganged together, but I separated them and am only using one 15-amp circuit, since I have nowhere near 15 amps draw on AC power - no 120v heater, A/C, or microwave, etc.


Click image for larger version

Name:	ele_102_2_lg.jpg
Views:	59
Size:	238.8 KB
ID:	25785
Don H. is offline   Reply With Quote
Old 01-06-2010, 06:02 PM   #8
Commercial Member
 
Robert Johans's Avatar
 
Trailer: 1988 Scamp 13 ft and 1982 Perris Pacer 13 ft
Posts: 822
Registry
Quote:
Okay...all of this talk about a larger breaker box, made me wonder if I need something larger also.
My pacer has a 15 amp breaker. Normally I would not have much on, a light or two. But there is an air conditioner hooked up. The side of the A/C says it is 6500 BTU and draws 6.1 amps. If nothing else, except maybe a light was on, do I need to up grade. Demo and building I can do, electrical stuff I'm a dud!
Thanks, Vicki

Vickie,
You are good to go as is...
Robert Johans is offline   Reply With Quote
Old 01-06-2010, 06:13 PM   #9
Senior Member
 
Vicki A.'s Avatar
 
Trailer: 1984 Perris Pacer ('Tillie')
Posts: 157
THANK YOU THANK YOU THANK YOU !!!
Vicki
Vicki A. is offline   Reply With Quote
Old 01-06-2010, 09:17 PM   #10
Senior Member
 
francene's Avatar
 
Trailer: 13 ft Compact II
Posts: 524
Registry
Quote:
Originally Posted by Don H. View Post
Oops! I bought the FPE 2-circuit box below from a surplus company online. It's a NOS unit, apparently from military surplus, made in the 1960s. (Maybe be identical to the ones they put in the new Compacts?) I thought it was a bargain at $15, until I looked into the problems that you mention.

I see that the malfunctions seem to be in connection with Stab-lok breakers. Don't know if they made "Stab-lok" breakers back then, but I guess it doesn't matter, since they could be defective regardless of whatever trade name they might have used at the time.

I hope there's a way I can just test it to make sure it's operating correctly. Otherwise, looks like I'll also be searching for a new box.

BTW, this has two 15-amp breakers ganged together, but I separated them and am only using one 15-amp circuit, since I have nowhere near 15 amps draw on AC power - no 120v heater, A/C, or microwave, etc.


Attachment 25785
Too bad, Don, but perhaps it's for the good to replace it now instead of risking fire. And you have done such nice electrical work in your trailer! Seems like everyone I mention it to says to avoid Federal Pacific replacements even though the breakers are still available.

I picked up a Siemens load box today plus 2 15 amp breakers. The box does not appear to have a gruond bar, though. Where do I connect the heavy ground wire?

Best,
Fran
francene is offline   Reply With Quote
Old 01-06-2010, 10:43 PM   #11
Senior Member
 
Roger C H's Avatar
 
Trailer: 2009 Trillium 13 ft ('Homelet') / 2000 Subaru Outback
Posts: 2,222
Registry
Unhappy

That is the problem with buying used. One never knows what was done. Our first house was the same way. They had the cold air return from the upstairs going down an outside wall! I guess that guaranteed that the air would be cold when it reached the basement. LOL

Not only that, but the switch box for the porch light had BX cable coming into it. The guy must have run out of cable clamps because he had the BX attached to the switch box with a steel wire wrapped around the BX and then out and around the cover plate tongue.

The plumbing was a nightmare! He had short runs made up with 45° and 90° elbows, several of them all put together. And this was the builder! Of course he was an amateur.

I remember the guy who helped me replace the porch light saying that the switch being off was sufficient, and he proved it by touching the two wires together. But I would not touch either wire to a ground because I had no confidence that the builder had placed the switch on the hot side like he should have. Such things do make for interesting times.
__________________
A charter member of the Buffalo Plaid Brigade!

Whether you think you can or think you can't, you're right.
Roger C H is offline   Reply With Quote
Old 06-21-2011, 03:51 PM   #12
Senior Member
 
Name: Steve
Trailer: 2018, 21ft escape— 2019 Ram 1500 Laramie
NW Wisconsin
Posts: 4,500
Fpe zinsco

Fpe losts its ul listing many years ago . You could not sell them in usa so we ordered them from canada. Fpe stab lock breakers would not always interupt at rated current and in some panels the breakers would fall out of the panel if you removed the dead front cover. They were installed because of cost not because they were a good product.
Zinsco has a simular story . I once took a 14 -2 romex cable protected by a 15 amp zinsco breaker and directly grounded the hot conductor (black wire) (bolted fault) .
The wire burned off but the zinsco breaker never tripped.
The best circuit breaker on the market is probably square d
qo series . They been making them for 50 years and are to me the cadillac of circuit breakers
thanks steve d
steve dunham is offline   Reply With Quote
Old 06-23-2011, 11:43 AM   #13
Senior Member
 
Trailer: 1977 Scamp 13 ft
Posts: 267
Quote:
Originally Posted by steve dunham View Post
Fpe losts its ul listing many years ago . You could not sell them in usa so we ordered them from canada. Fpe stab lock breakers would not always interupt at rated current and in some panels the breakers would fall out of the panel if you removed the dead front cover. They were installed because of cost not because they were a good product.
Zinsco has a simular story . I once took a 14 -2 romex cable protected by a 15 amp zinsco breaker and directly grounded the hot conductor (black wire) (bolted fault) .
The wire burned off but the zinsco breaker never tripped.
The best circuit breaker on the market is probably square d
qo series . They been making them for 50 years and are to me the cadillac of circuit breakers
thanks steve d
I just about lost my house recently due to a Federal Pacific breaker panel. After learning the horrific problems associated with that brand and Zinsco I would STRONGLY recommend having a professional replace any panel with those names on them.

FPE breakers are widely known for not working.... at all...

There is one very important note about RV panels. Often I see the neutral and ground wires connected to the same buss. This is extremely dangerous, the only place where this connection (Called "Bonding") can occur is in the primary panel (IE your home or RV park pedestal) make sure that any replacement panel has both a neutral and ground bars separated. All RV panels are "Sub Panels" so when choosing a panel make sure it is setup properly.
David Morgan is offline   Reply With Quote
Old 06-23-2011, 02:27 PM   #14
Senior Member
 
cpaharley2008's Avatar
 
Name: jim
Trailer: 2022 Escape19 pulled by 2014 Dodge Ram Hemi Sport
Pennsylvania
Posts: 6,710
Registry
If you want to put your worries to rest, install a new 15 amp circuit with a CFCI circuit breaker. Any short will cut off the electric. You can add another 15 amp circuit or add additional outlets to the one you have. I think up to 10 outlets can be on one 15 amp-check your local codes for the rules. here is one Amazon.com: GE Industrial Dept. THQL1120GF Circuit Breaker: Home Improvement- please note-the one pictured is 20 amp, you will want a 15 amp
cpaharley2008 is offline   Reply With Quote
Old 06-24-2011, 03:57 AM   #15
Senior Member
 
james kent's Avatar
 
Trailer: Boler 1984
Posts: 2,938
Our breaker box has two 15 amp fuses in it. One for the fridge and one for the 110v outlets.
james kent is offline   Reply With Quote
Old 06-25-2011, 12:13 AM   #16
Senior Member
 
AndyGee's Avatar
 
Name: Andy
Trailer: 1979 Ventura 13'
Alberta
Posts: 133
Quote:
Originally Posted by Vicki A.
Okay...all of this talk about a larger breaker box, made me wonder if I need something larger also.
My pacer has a 15 amp breaker. Normally I would not have much on, a light or two. But there is an air conditioner hooked up. The side of the A/C says it is 6500 BTU and draws 6.1 amps. If nothing else, except maybe a light was on, do I need to up grade. Demo and building I can do, electrical stuff I'm a dud!
Thanks, Vicki
You're good to 12 amps total on a 15 amp breaker the rule being 80% of the breaker rating. Also each outlet counts as 1.5 amps so that = 8 on a 15 amp circuit.
AndyGee is offline   Reply With Quote
Old 06-25-2011, 11:00 AM   #17
Senior Member
 
Name: Steve
Trailer: 2018, 21ft escape— 2019 Ram 1500 Laramie
NW Wisconsin
Posts: 4,500
The 1.5 amp rule (180 va) applies to commercial work (load calculations) not residential according to the National electrical code. Too many people put way too much trust in GFCI breakers. In the OSHA class I teach ,I take a hair dryer which is turned on and protected by a GFCI and drop it in a 5 gallon bucket filled with water. After five minutes I remove the hair dryer from the bucket and it is still running (GFCI NEVER TRIPPED) GFCI plugs are designed for hot to ground faults not hot to neutral (grounded conductor) faults and are not the total answer to safety.
steve dunham is offline   Reply With Quote
Old 06-25-2011, 12:07 PM   #18
Senior Member
 
Name: Steve
Trailer: 2018, 21ft escape— 2019 Ram 1500 Laramie
NW Wisconsin
Posts: 4,500
NO ,the national electrical code says that an appliance( AIR CONDITIONER , garbage disposal ,dishwasher etc is not to exceed 50 % of the branch circuit rating , when the circuit also feeds general lighting loads. 50 % of 15 amps = 7.5 amps max current for the appliance . Your AC draws 6.1 amps so your okay. Best practice would be to have the AC on it's own circuit but if the trailer has only a 15 amp feeder-service ( main power supply) it does not matter 15 amps is 15 amps and the feeder is the limiting factor. If you have a 30 amp service then splitting the loads into two circuits may be benificial. Travel trailers are not subject to a lot of the code rules regarding
standard residential construction
steve dunham is offline   Reply With Quote
Old 06-25-2011, 05:08 PM   #19
Senior Member
 
AndyGee's Avatar
 
Name: Andy
Trailer: 1979 Ventura 13'
Alberta
Posts: 133
The Canadian Electrical code has an entire section dealing with trailers and mobile homes, however it has to do mostly with power distribution in parks and hook ups. CSA ( Canadian Standards Association) deals with construction and approval.
AndyGee is offline   Reply With Quote
Old 07-07-2011, 05:19 PM   #20
Member
 
Trailer: Trillium Jubilee
Posts: 53
Send a message via MSN to Bill Reilly
Adding Circuits

Francene

Your discussion on adding circuits became a look into the various circuit breakers and other electrical appliances.

Steve Dunham summed it up rather nicely. If you want more power (presumably to run two or more devices simualtaneously) you have to have more than a 15 amp feed from the source.

I am on my third reno and I started each by installing a 30 amp service. In this way I can have as many circuits as I want, knowing that I can operate two or more appliances concurrently (provided the total load is less than 30 amps).

Bill Reilly
Picton, Ontario
Bill Reilly is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Power Converter & Breaker Box $60 kentj Classified Archives 2 04-28-2008 10:51 PM
circuit breaker Ken & Sherry B. Problem Solving | Owners Helping Owners 11 10-16-2007 08:18 PM
breaker works too well Paula Bindrich Problem Solving | Owners Helping Owners 13 07-06-2007 10:48 AM
Circuit Breaker overload? TorreyT Problem Solving | Owners Helping Owners 10 05-20-2007 02:33 PM
Where does the circuit breaker go? Legacy Posts Problem Solving | Owners Helping Owners 7 07-17-2003 08:47 PM