Old 10-16-2013, 08:55 AM   #21
Senior Member
 
Name: Steve
Trailer: 2018, 21ft escape— 2019 Ram 1500 Laramie
NW Wisconsin
Posts: 4,500
Cord ampacity

Quote:
Originally Posted by ruscal View Post
Jim,
Shouldn't 12 ga. do 20 amps?
Russ
The ampacity for cords is listed in Art 400 of the NEC not in Art 310-16 ,which lists the ampacity of standard building wire . According to the NEC 12/3 standard cord @ listed ambient temperature has an ampacity of 20 amps .. Length of the cord and voltage drop are also issues to be considered . Using an extension cord at 100 % of ampacity usually destroys the male and female cord ends long before damaging the cord itself
steve dunham is offline   Reply With Quote
Old 10-16-2013, 09:27 AM   #22
Senior Member
 
David Tilston's Avatar
 
Name: Dave W
Trailer: Trillium 4500 - 1976, 1978, 1979, 1300 - 1977, and a 1973
Alberta
Posts: 6,926
Registry
If Diane was running an air conditioner, I would suspect low supply voltage. Motors will draw more current under low voltage conditions. But just a heater? To me, the only possible suspect becomes the camp ground supplying too high of a voltage. Especially if the heater runs fine at home.
David Tilston is offline   Reply With Quote
Old 10-16-2013, 09:50 AM   #23
Senior Member
 
Carol H's Avatar
 
Trailer: 92 16 ft Scamp
Posts: 11,756
Registry
Question for the electrical guru's.

Lets say for a moment that the trailer in question has been all rewired & has new 15 amp breakers etc and the owner had checked the issue wasnt with the campground power supply, could the problem simple be the use of an extension cord with the trailers main power 15 amp supply cord? I dont now enough about how a 15 amp trailer is normally set up (but in this case it sounds like the OP has a newer converter, so would have thought it to be the same as a 30 amp system) but I do know that most small electrical heaters have instructions indicating that they should not be used with an extension cord. If the converter is in place what happens that an appliance such as a heater would it even know there was an extension cord (with the correct amps for the heater) attached to the trailers main supply (assuming its not a real long one) & if no other power hungry appliances where in use? Would having a longer main trailer power supply cord, avoiding the use of the need for an extension cord change anything?
Enquiring minds want to know.
Carol H is offline   Reply With Quote
Old 10-16-2013, 10:01 AM   #24
Senior Member
 
David Tilston's Avatar
 
Name: Dave W
Trailer: Trillium 4500 - 1976, 1978, 1979, 1300 - 1977, and a 1973
Alberta
Posts: 6,926
Registry
I suspect that the reason that they don't want you to run on an extension cord is that a heater draws lots of power. If the cord is damaged, the heater could cause it to fail. Otherwise it is a resister in series with a load. The power cord could cause a voltage drop, but that is it. It would not cause additional current to flow to a heater. In fact exactly the opposite, less current.

A 30A service would just have a larger wire in the cord, therefor less resistance, less voltage drop. A 12/3 extension cord is all that a 15A trailer supply would require, but a 1500 W heater would be taking most of that capacity. 1500W/120VAC=12.5A
David Tilston is offline   Reply With Quote
Old 10-16-2013, 10:21 AM   #25
Senior Member
 
Bob Miller's Avatar
 
Trailer: Class A Motorhome
Posts: 7,912
In acting as a resistor the 10 amp power cord could also overheat, melt insulation, short out, start a fire, you name it.

As far as the original U-Haul breaker not supporting a heater... It shouldn't be a problem
A typical small space heater is 800-1500 watts max, that's less than 15 amps in all cases and more like 10 in most.

A good 15 amp breaker should have no problems with that load, unless, as mentioned, it's original and well worn, as all original one are by now.



Bob Miller is offline   Reply With Quote
Old 10-16-2013, 10:52 AM   #26
Senior Member
 
David Tilston's Avatar
 
Name: Dave W
Trailer: Trillium 4500 - 1976, 1978, 1979, 1300 - 1977, and a 1973
Alberta
Posts: 6,926
Registry
I should have mentioned that not all power cords can support 15A A 12/3 will, but an 18/3 will not. Extended use of an 18/3 cord with a 1500W heater, could lead to a fire.
David Tilston is offline   Reply With Quote
Old 10-16-2013, 11:16 AM   #27
Senior Member
 
floyd's Avatar
 
Trailer: 2004 13 ft Scamp Custom Deluxe
Posts: 8,520
Registry
Quote:
Originally Posted by cpaharley2008 View Post
it should but with a 100 foot cord it may not!
It's AC! It's 20A
floyd is offline   Reply With Quote
Old 10-16-2013, 02:12 PM   #28
Senior Member
 
D Davis's Avatar
 
Name: Diane
Trailer: Casita, previously u-haul ct13
Virginia
Posts: 1,020
Okay guys, I bought the little GFCI tester, read the instructions. Man I have a lot of ungrounded receptacles in my home! Found a wired right one in the home and connected the Camper cable to it. Tested the main GFCI located at the end of the upper cabinet. It tested as being wired Okay. Then as Bob said, connected the heater...it blew the breaker in camper in 30 minutes. The heater is a 120 V 1500 watt 12.5 Ag label on the back. I did not use any extension cord. So DO YOU THINK I NEED TO REPLACE THE BREAKER AND GFCI RECEPTACLE which appears to be the original to the CT13? ALL other wiring including 12V is new.Thanks guys each and everyone of you! Have tester will travel! LOL Thanks
D Davis is offline   Reply With Quote
Old 10-16-2013, 02:39 PM   #29
Senior Member
 
Trailer: 2002 19 ft Scamp 19 ft 5th Wheel
Posts: 3,640
Send a message via Yahoo to Darwin Maring
D said: I have a lot of ungrounded receptacles in my home!

The main thing to look for on those ungrounded receptacles is that the HOT / Neutral are not reversed.

If the GFCI internal breaker did not trip then it is OK.

If the circuit breaker on the AC panel is the one that tripped, then it may be the culprit.

If the wiring from the breaker panel to the receptacle is not able to carry the load then the breaker is saving you from having a fire or even worse.

Do you have a lower heat setting on the heater?
Darwin Maring is offline   Reply With Quote
Old 10-16-2013, 03:38 PM   #30
Senior Member
 
Bob Miller's Avatar
 
Trailer: Class A Motorhome
Posts: 7,912
In a word YES, it's time for a new breaker.



Bob Miller is offline   Reply With Quote
Old 10-16-2013, 03:49 PM   #31
Senior Member
 
Name: Russ
Trailer: Scamp 16' side dinette, Airstream Safari 19'
California
Posts: 588
Quote:
Originally Posted by David Tilston View Post
I suspect that the reason that they don't want you to run on an extension cord is that a heater draws lots of power. If the cord is damaged, the heater could cause it to fail. Otherwise it is a resister in series with a load. The power cord could cause a voltage drop, but that is it. It would not cause additional current to flow to a heater. In fact exactly the opposite, less current.

A 30A service would just have a larger wire in the cord, therefor less resistance, less voltage drop. A 12/3 extension cord is all that a 15A trailer supply would require, but a 1500 W heater would be taking most of that capacity. 1500W/120VAC=12.5A
David, I'm trying to get my head around the less current when the voltage drops.
1500W/120VAC=12.5A
1500W/100VAC=15.0A I get more current when I figure it?
Not trying to hijack the thread, just get a better understanding of electron behavior.

Anyway Diane's problem probably isn't voltage drop, just likely a tired breaker as others have noted.
Russ
ruscal is offline   Reply With Quote
Old 10-16-2013, 04:02 PM   #32
Senior Member
 
Trailer: 2002 19 ft Scamp 19 ft 5th Wheel
Posts: 3,640
Send a message via Yahoo to Darwin Maring
Volts times Amps = Watts
120 x 15A = 1800W
Darwin Maring is offline   Reply With Quote
Old 10-16-2013, 04:07 PM   #33
Raz
Senior Member
 
Raz's Avatar
 
Trailer: Trillium 2010
Posts: 5,185
Quote:
Originally Posted by ruscal View Post
David, I'm trying to get my head around the less current when the voltage drops.
1500W/120VAC=12.5A
1500W/100VAC=15.0A I get more current when I figure it?
Not trying to hijack the thread, just get a better understanding of electron behavior.


Russ
The constant here is not the 1500 watt power disspation but rather the resistance of the heater.

V/I = R. 120/12.5 = 9.6 ohms

At 100 volts the current will drop to I = V/R = 100/9.6 = 10.4 amps.

Power, P = V x I = 100 x 10.4 =1040 watts.

Since power is the rate of using energy, you would expect that rate to drop with a reduced voltage. It does, from 1500 down to 1040 watt. Physically the heater will not get as hot. Raz
Raz is offline   Reply With Quote
Old 10-16-2013, 04:10 PM   #34
Senior Member
 
mszabo's Avatar
 
Trailer: U-Haul VT16
Posts: 982
NEC says a breaker needs to trip at 80%. Which is 12.5 amps on a 15 amp breaker.
A breaker trips because of one of two things, heat or magnetic field.
Your equipment is working fine.
It sounds like a blood and turnip thing.
Only my opinion
mszabo is offline   Reply With Quote
Old 10-16-2013, 04:14 PM   #35
Senior Member
 
Bob Miller's Avatar
 
Trailer: Class A Motorhome
Posts: 7,912
Opps, math mistake



Bob Miller is offline   Reply With Quote
Old 10-16-2013, 04:20 PM   #36
Senior Member
 
Name: Russ
Trailer: Scamp 16' side dinette, Airstream Safari 19'
California
Posts: 588
Raz.
I am beginning to understand this. I was thinking the heater watts was a constant value and it seemed too simple! Using the resistance at it's rated amperage in the equation makes sense. I'll have to do some exercises to get comfortable with these problems.
Thanks,
Russ
ruscal is offline   Reply With Quote
Old 10-16-2013, 04:21 PM   #37
Senior Member
 
Name: bob
Trailer: 1996 Casita 17 Spirit Deluxe; 1946 Modernistic teardrop
New York
Posts: 5,413
Our Uhaul had a little push button breaker mounted with the one and only 110 outlet on the end of the upper cabinet. It will not run an electric heater. And as I recall the power cord that plugs into the campground electric box goes directly to that breaker. If Diane has not changed that setup, it is surely the problem. It's been awhile since I rewired our Uhaul, so I may be wrong on the wire routing, but I think everything went through that little breaker, it's not a conventional breaker as we would think of one.
mary and bob is offline   Reply With Quote
Old 10-16-2013, 04:30 PM   #38
Senior Member
 
David Tilston's Avatar
 
Name: Dave W
Trailer: Trillium 4500 - 1976, 1978, 1979, 1300 - 1977, and a 1973
Alberta
Posts: 6,926
Registry
Think of it like water, less pressure = less flow.

The power output of the heater is not fixed. It can be considered a resister.

Ohms Law
Current (I) = Voltage (V) / Resistance (R)
V=I xR
R=V/I

R=V/I = 120/12.5 = 9.6 ohms

If the wire were also 9.6 ohms, then the current would be half, and the heater would be producing 1/4 of its rated output. This is because twice the resistance would lower the current by half. Also half the voltage, (and power) would be dropped in the wire.
I = V/R = 120/19.2 = 6.25 (half of 12.5)

Watts (P) = V x I
Subing in V = I x R (ohms law from above)

P = (I x R) x I
P = I^2 x R
P = 6.25^2 x 9.6 = 39 x 9.6 = 375 W (1/4 of the rated output)

Of course the extension cord is also making 375 W. It is going to get very hot.

Because half the total current is flowing, half the total power is being made.

I hope that I have not confused you further.
David Tilston is offline   Reply With Quote
Old 10-16-2013, 04:38 PM   #39
Senior Member
 
Name: Russ
Trailer: Scamp 16' side dinette, Airstream Safari 19'
California
Posts: 588
Dave,
Since the heater would be half as hot you could coil the cord in bed and recover the heat.
Russ
ruscal is offline   Reply With Quote
Old 10-16-2013, 04:41 PM   #40
Senior Member
 
David Tilston's Avatar
 
Name: Dave W
Trailer: Trillium 4500 - 1976, 1978, 1979, 1300 - 1977, and a 1973
Alberta
Posts: 6,926
Registry
Quote:
Originally Posted by ruscal View Post
Dave,
Since the heater would be half as hot you could coil the cord in bed and recover the heat.
Russ
Yah, ummm...... if you don't mind the smell of burning plastic, (and or flesh).

And the total system would be half as hot. The heater would be 1/4 as hot.
David Tilston is offline   Reply With Quote
Reply

Tags
electrical


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical Breaker Problems Debbie Ray Problem Solving | Owners Helping Owners 6 07-09-2014 05:30 PM
Wonders near home Perry J General Chat 16 11-02-2011 03:02 PM
breaker works too well Paula Bindrich Problem Solving | Owners Helping Owners 13 07-06-2007 10:48 AM
Seven wonders of Canada CharlynnT General Chat 14 04-29-2007 08:52 PM
Where does the circuit breaker go? Legacy Posts Problem Solving | Owners Helping Owners 7 07-17-2003 08:47 PM

» Upcoming Events
No events scheduled in
the next 465 days.
» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 06:48 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.