D said: I have a lot of ungrounded receptacles in my home!

The main thing to look for on those ungrounded receptacles is that the HOT / Neutral are not reversed.

If the GFCI internal breaker did not trip then it is OK.

If the circuit breaker on the AC panel is the one that tripped, then it may be the culprit.

If the wiring from the breaker panel to the receptacle is not able to carry the load then the breaker is saving you from having a fire or even worse.

Do you have a lower heat setting on the heater?
__________________

__________________
Darwin Maring is offline   Reply With Quote
Old 10-16-2013, 04:38 PM   #30
Senior Member
 
Bob Miller's Avatar
 
Name: Bob
Trailer: 1973 Hunter Compact II
California
Posts: 7,912
In a word YES, it's time for a new breaker.
__________________

__________________
Bob Miller is offline   Reply With Quote
Old 10-16-2013, 04:49 PM   #31
Senior Member
 
Name: Russ
Trailer: Scamp 16' side dinette, Airstream Safari 19'
California
Posts: 588
Quote:
Originally Posted by David Tilston View Post
I suspect that the reason that they don't want you to run on an extension cord is that a heater draws lots of power. If the cord is damaged, the heater could cause it to fail. Otherwise it is a resister in series with a load. The power cord could cause a voltage drop, but that is it. It would not cause additional current to flow to a heater. In fact exactly the opposite, less current.

A 30A service would just have a larger wire in the cord, therefor less resistance, less voltage drop. A 12/3 extension cord is all that a 15A trailer supply would require, but a 1500 W heater would be taking most of that capacity. 1500W/120VAC=12.5A
David, I'm trying to get my head around the less current when the voltage drops.
1500W/120VAC=12.5A
1500W/100VAC=15.0A I get more current when I figure it?
Not trying to hijack the thread, just get a better understanding of electron behavior.

Anyway Diane's problem probably isn't voltage drop, just likely a tired breaker as others have noted.
Russ
__________________
ruscal is offline   Reply With Quote
Old 10-16-2013, 05:02 PM   #32
Senior Member
 
Name: Darwin
Trailer: 2002 19 ft Scamp 19 ft 5th Wheel
Posts: 3,029
Send a message via Yahoo to Darwin Maring
Volts times Amps = Watts
120 x 15A = 1800W
__________________
Darwin Maring is offline   Reply With Quote
Old 10-16-2013, 05:07 PM   #33
Raz
Senior Member
 
Raz's Avatar
 
Name: Raz
Trailer: Trillium 2010
Vermont
Posts: 4,055
Quote:
Originally Posted by ruscal View Post
David, I'm trying to get my head around the less current when the voltage drops.
1500W/120VAC=12.5A
1500W/100VAC=15.0A I get more current when I figure it?
Not trying to hijack the thread, just get a better understanding of electron behavior.


Russ
The constant here is not the 1500 watt power disspation but rather the resistance of the heater.

V/I = R. 120/12.5 = 9.6 ohms

At 100 volts the current will drop to I = V/R = 100/9.6 = 10.4 amps.

Power, P = V x I = 100 x 10.4 =1040 watts.

Since power is the rate of using energy, you would expect that rate to drop with a reduced voltage. It does, from 1500 down to 1040 watt. Physically the heater will not get as hot. Raz
__________________
Raz is offline   Reply With Quote
Old 10-16-2013, 05:10 PM   #34
Senior Member
 
mszabo's Avatar
 
Name: Mike
Trailer: 1986 Bigfoot FT20
Michigan
Posts: 649
NEC says a breaker needs to trip at 80%. Which is 12.5 amps on a 15 amp breaker.
A breaker trips because of one of two things, heat or magnetic field.
Your equipment is working fine.
It sounds like a blood and turnip thing.
Only my opinion
__________________
mszabo is offline   Reply With Quote
Old 10-16-2013, 05:14 PM   #35
Senior Member
 
Bob Miller's Avatar
 
Name: Bob
Trailer: 1973 Hunter Compact II
California
Posts: 7,912
Opps, math mistake
__________________
Bob Miller is offline   Reply With Quote
Old 10-16-2013, 05:20 PM   #36
Senior Member
 
Name: Russ
Trailer: Scamp 16' side dinette, Airstream Safari 19'
California
Posts: 588
Raz.
I am beginning to understand this. I was thinking the heater watts was a constant value and it seemed too simple! Using the resistance at it's rated amperage in the equation makes sense. I'll have to do some exercises to get comfortable with these problems.
Thanks,
Russ
__________________
ruscal is offline   Reply With Quote
Old 10-16-2013, 05:21 PM   #37
Senior Member
 
Name: bob
Trailer: 1984 u-haul ct13; 1996 Casita 17 Spirit Deluxe; 1946 Modernistic teardrop
New York
Posts: 4,323
Our Uhaul had a little push button breaker mounted with the one and only 110 outlet on the end of the upper cabinet. It will not run an electric heater. And as I recall the power cord that plugs into the campground electric box goes directly to that breaker. If Diane has not changed that setup, it is surely the problem. It's been awhile since I rewired our Uhaul, so I may be wrong on the wire routing, but I think everything went through that little breaker, it's not a conventional breaker as we would think of one.
__________________
mary and bob is offline   Reply With Quote
Old 10-16-2013, 05:30 PM   #38
Senior Member
 
David Tilston's Avatar
 
Name: Dave W
Trailer: Trillium 4500 - 1977, 1978 (2), 1300 - 1977, 1973, and a 1972
Alberta
Posts: 5,314
Registry
Think of it like water, less pressure = less flow.

The power output of the heater is not fixed. It can be considered a resister.

Ohms Law
Current (I) = Voltage (V) / Resistance (R)
V=I xR
R=V/I

R=V/I = 120/12.5 = 9.6 ohms

If the wire were also 9.6 ohms, then the current would be half, and the heater would be producing 1/4 of its rated output. This is because twice the resistance would lower the current by half. Also half the voltage, (and power) would be dropped in the wire.
I = V/R = 120/19.2 = 6.25 (half of 12.5)

Watts (P) = V x I
Subing in V = I x R (ohms law from above)

P = (I x R) x I
P = I^2 x R
P = 6.25^2 x 9.6 = 39 x 9.6 = 375 W (1/4 of the rated output)

Of course the extension cord is also making 375 W. It is going to get very hot.

Because half the total current is flowing, half the total power is being made.

I hope that I have not confused you further.
__________________
David Tilston is offline   Reply With Quote
Old 10-16-2013, 05:38 PM   #39
Senior Member
 
Name: Russ
Trailer: Scamp 16' side dinette, Airstream Safari 19'
California
Posts: 588
Dave,
Since the heater would be half as hot you could coil the cord in bed and recover the heat.
Russ
__________________
ruscal is offline   Reply With Quote
Old 10-16-2013, 05:41 PM   #40
Senior Member
 
David Tilston's Avatar
 
Name: Dave W
Trailer: Trillium 4500 - 1977, 1978 (2), 1300 - 1977, 1973, and a 1972
Alberta
Posts: 5,314
Registry
Quote:
Originally Posted by ruscal View Post
Dave,
Since the heater would be half as hot you could coil the cord in bed and recover the heat.
Russ
Yah, ummm...... if you don't mind the smell of burning plastic, (and or flesh).

And the total system would be half as hot. The heater would be 1/4 as hot.
__________________
David Tilston is offline   Reply With Quote
Old 10-16-2013, 05:42 PM   #41
Senior Member
 
Name: None
Trailer: None
None
Posts: 2,727
Quote:
Originally Posted by mszabo View Post
NEC says a breaker needs to trip at 80%. Which is 12.5 amps on a 15 amp breaker.
A breaker trips because of one of two things, heat or magnetic field.
Your equipment is working fine.
It sounds like a blood and turnip thing.
Only my opinion
The NEC does not state that a breaker needs to trip at 80% of its rating. The NEC says a Breaker which is subject to continuous load ( Continuous load definition = 3 hours or more ) shall not be loaded past 80% of the breaker rating IE a 20 amp breaker is not to have a continuous load of more than 16 amps . A 15 amp circuit breaker's trip point is not precisely at 15 amps, being a mechanical device the trip point varies and UL standards allow for this variance. Ambient temperature and how heavily loaded the adjoining breakers in the panel also affect trip point . I've seen a 15 amp breaker in -30 Deg F ambient not trip when subject to a load of almost 30 amps. Residential circuit breakers are thermomagnetic HELP ME OUT HERE RAZ
__________________
steve dunham is offline   Reply With Quote
Old 10-16-2013, 06:12 PM   #42
Senior Member
 
Jon Vermilye's Avatar
 
Name: Jon
Trailer: 2017 Escape 21
Oswego, NY
Posts: 1,406
Registry
More than most will want to know about circuit breakers:
There are 3 basic types of mechanical circuit breakers - the Thermal, the Magnetic, and the Thermal/Magnetic. Each has both advantages & disadvantages, however most home and RV breaker panels use the Thermal/Magnetic type.

As its name implies, the thermal/magnetic circuit breaker can react to thermal or magnetic overloads. The thermal section trips at minot overloads (under 200%) while the magnetic trips on major overloads (400%-500% or more). Since small overloads only activate the thermal part of the breaker, this is why Steve's description of breakers holding overloads at low temperatures happens.

The reason for combining the two trip methods is economic. A pure thermal (which is often found on power tools, motor protection, etc) doesn't react fast enough at high overloads. While a pure magnetic circuit breaker is very fast, they are also very expensive. They are often used to protect sensitive electronics. The thermal/magnetic breaker has a very simple magnetic section that only works for large overloads, leaving the smaller overloads to the thermal section.
__________________

Jon Vermilye is offline   Reply With Quote
Reply

Tags
electrical


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical Breaker Problems Debbie Ray Problem Solving | Owners Helping Owners 6 07-09-2014 06:30 PM
Wonders near home Perry J General Chat 16 11-02-2011 04:02 PM
breaker works too well Paula Bindrich Problem Solving | Owners Helping Owners 13 07-06-2007 11:48 AM
Seven wonders of Canada CharlynnT General Chat 14 04-29-2007 09:52 PM
Where does the circuit breaker go? Legacy Posts Problem Solving | Owners Helping Owners 7 07-17-2003 09:47 PM

» Upcoming Events
No events scheduled in
the next 465 days.
» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 02:11 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.