Old 08-18-2008, 08:15 AM   #1
Senior Member
 
Trailer: 19 ft Scamp 19 ft 5th Wheel Dlx / 2001 Ford Ranger 4x4
Posts: 1,125
I noticed my furnace was just blowing'air' the other nite..... the fan kicked on but no heat.. i was not outta propane... so is this a major repair or ??? I sure hope not!!
Christi V. is offline   Reply With Quote
Old 08-18-2008, 08:27 AM   #2
Senior Member
 
Trailer: 1960 28 ft Airstream
Posts: 336
Quote:
I noticed my furnace was just blowing'air' the other nite..... the fan kicked on but no heat.. i was not outta propane... so is this a major repair or ??? I sure hope not!!
Where you running on batteries or AC?

Pam
Pamela H is offline   Reply With Quote
Old 08-18-2008, 09:08 AM   #3
Senior Member
 
Trailer: 19 ft Scamp 19 ft 5th Wheel Dlx / 2001 Ford Ranger 4x4
Posts: 1,125
I aasume a/c as i was on shore power? it worked the last time I ran it.. so just baffled..

there was also a thread on water not staying in the toilet.... i seem to be having that problem again.. but couldnt find the thread.....

Christi V. is offline   Reply With Quote
Old 08-18-2008, 02:58 PM   #4
Senior Member
 
Trailer: 1960 28 ft Airstream
Posts: 336
Quote:
I aasume a/c as i was on shore power? it worked the last time I ran it.. so just baffled..

there was also a thread on water not staying in the toilet.... i seem to be having that problem again.. but couldnt find the thread.....
Doesn't sound promising...sounds like a trip to the furnace man...hopefully just part of your pilot system. Is the pilot lit? (always a good thing to check...)
Pamela H is offline   Reply With Quote
Old 08-18-2008, 04:26 PM   #5
Senior Member
 
Harry Young's Avatar
 
Trailer: 1971 Astro (ie. Campster/Hunter I)
Posts: 437
Send a message via MSN to Harry Young Send a message via Yahoo to Harry Young
Post

I repair these...I need the model number...Many units have a three strikes to light feature and you get locked out of operation its built into their starting computers, when air is present in the gas line it might take as many as 6 or 9 striking attempts (thats 3 cycles) Note: (a cycle is three individual trys to light) before air is purged...the retry procedure is simple...turn the thermostat off wait for (BLOWER/FAN TO STOP!!!) then 5 sec after blower stops running...turn on the thermostat again, the computer will attempt 3 more times to strike up a flame then it will lock out from trying to light until you shut off thermostat and do this again...it is a feature required and designed into the operation of the unit, its a saftey lock out. I have had to do this up to 12 times before the air purged enough out of the gas lines for the flame to strike...This is my number one service call on Suburbons...Remember three strikes and your out and you must start over.

Often I purge the lines...thats a later idea and needs detailed instructions and saftey precautions...do this first.


Harry


Quote:
Doesn't sound promising...sounds like a trip to the furnace man...hopefully just part of your pilot system. Is the pilot lit? (always a good thing to check...)
Harry Young is offline   Reply With Quote
Old 08-18-2008, 07:00 PM   #6
Senior Member
 
Victor Benz's Avatar
 
Trailer: Fiber Stream 1982 16 ft
Posts: 362
Registry
Totally agree with Harry! That is why sequence of the gas start-up is so important.

1. Light a stove burner (It is always manual, an no thermocouple)
2. Light Hot water heater (manual light, but has a thermostat)
3. Light the refrigerator (pezioelectric light and thermocouple)
4. Now all gas lines should be purged of air, light the furnace.

Vic
Victor Benz is offline   Reply With Quote
Old 08-19-2008, 03:19 PM   #7
Member
 
Shelley's Avatar
 
Trailer: 1977 Triple E Surfside
Posts: 66
I'd like to piggyback on this thread....

I can get my furnace lit and have heat :-) But when painting the interior I painted over a little metal tubelike part that I have since been told may be the thermostat

Do I need to replace it now to control the amount of heat? I've only used the furnace to take the chill off before going to bed...not continuously overnight...

Shelley is offline   Reply With Quote
Old 08-19-2008, 07:19 PM   #8
Senior Member
 
Harry Young's Avatar
 
Trailer: 1971 Astro (ie. Campster/Hunter I)
Posts: 437
Send a message via MSN to Harry Young Send a message via Yahoo to Harry Young
I need the model number or trailer model and year to be smart in any help I might offer...to my knowledge there is no wire, thermocouple, or mercury sensing tube "all these look alike" you can paint that would snooker the furnace...I can go thru with you from the most probable and most common problems based on model and description of the issue with a short series of questions and trys...I love this stuff so its no problem, some people like puzzles... I like long distance tech...

Quote:
I'd like to piggyback on this thread....

I can get my furnace lit and have heat :-) But when painting the interior I painted over a little metal tubelike part that I have since been told may be the thermostat

Do I need to replace it now to control the amount of heat? I've only used the furnace to take the chill off before going to bed...not continuously overnight...
Harry Young is offline   Reply With Quote
Old 08-20-2008, 11:26 AM   #9
Senior Member
 
Gina D.'s Avatar
 
Trailer: Former Burro owner and fan!
Posts: 9,015
Registry
Christi, I have the same problem and I do as Harry suggests.

Sometimes it is almost impossible, even after I have it lit once, the next cycle it won't light in the 3 tries.

Frankly, I am about to rip the dang thing out. I like it when it runs, but trying to get it running is ridiculous.

A Wave 6 heater is in my future. No muss, no fuss, no bother, no electricity use.. and an increase in storage space ta boot!
Gina D. is offline   Reply With Quote
Old 08-20-2008, 03:42 PM   #10
Senior Member
 
Orlen Wolf's Avatar
 
Trailer: Eggcamper 2007 ('Wolf's Lair')
Posts: 329
Check your 12V at the furnace with the fan off and with the fan running. I'll bet you will find enough of a voltage drop to slow the fan down a bit, right down to the "maybe I'll work and maybe I won't" point.

Even if you are on shore power you can have a voltage drop in the line especially if your egg has been around a while. A little corrosion at a wiring connection or a high resistance at a fuse cap will slow the fan down enough so the air prove will not activate. No air prove = no signal to the gas solenoid so you get no heat.
Orlen Wolf is online now   Reply With Quote
Old 08-20-2008, 04:18 PM   #11
Senior Member
 
Trailer: 2002 19 ft Scamp 19 ft 5th Wheel
Posts: 3,640
Send a message via Yahoo to Darwin Maring
I had the problem with mine and found out there was water inside the furnace. Must have gotten in there during a rainstorm - through the air in exhaust out vents.

I removed the inspection plate inside the camper, removed the burner and soaked up the water with a rag and cleaned the burner and put it back together and it worked fine. Have had to do this twice through out the years.

Note, The gasket is fragile so have some high temp gasket material (Silicone in a tube) ready so you can get it back air tight.
Darwin Maring is offline   Reply With Quote
Old 08-20-2008, 10:54 PM   #12
Senior Member
 
Gina D.'s Avatar
 
Trailer: Former Burro owner and fan!
Posts: 9,015
Registry
Orlen, good thought, but voltage drop was my very first thought when it started happening regularly. I double and triple checked.. doesn't seem to be any rhyme or reason there. It sometimes hits at 12, and sometimes at 11.. or 13. I cleaned the connections and reseated all I could get to.

Nothing helps. I know better than to mess with propane and 'lectricty.. I know nothing of how these things safety precautions should be.

I want a non vented and passive cat heater anyway. I am a "low to no" current sucking freak. I was really happy with my wave 3 in my 13. It replaced a vented cat heater that had a fan.

Half the time now, as it is, I have to use my black cat heater because the furnace won't light.

I will note that one thing about my furnace that really scares me is it sometimes makes a huge explosion when trying to light.. like a backfire. Sounds like a gunshot when outside the rig, and it's a big "Whoosh" when inside. Like when your water heater fires up after lighting the pilot and it catches.

It DOES light after that boom, however.
Gina D. is offline   Reply With Quote
Old 08-21-2008, 05:38 AM   #13
Senior Member
 
Alf S.'s Avatar
 
Trailer: 2007 19 ft Escape 5.0 / 2002 GMC (1973 Boler project)
Posts: 4,148
Registry
Send a message via Yahoo to Alf S.
Hi: All...Propane isn't on my "DYI" project list. I have seen the side of a slide in camper where the fridge ran amok and it was chared and melted!!! This stuff is volitile and worth seeking a well trained and qualified Tech. for service!!!
Alf S. North shore of Lake Erie
Alf S. is offline   Reply With Quote
Old 08-21-2008, 12:22 PM   #14
Senior Member
 
Orlen Wolf's Avatar
 
Trailer: Eggcamper 2007 ('Wolf's Lair')
Posts: 329
Quote:
Orlen, good thought, but voltage drop was my very first thought when it started happening regularly. I double and triple checked.. doesn't seem to be any rhyme or reason there. It sometimes hits at 12, and sometimes at 11.. or 13. I cleaned the connections and reseated all I could get to.

Nothing helps. I know better than to mess with propane and 'lectricty.. I know nothing of how these things safety precautions should be.

I want a non vented and passive cat heater anyway. I am a "low to no" current sucking freak. I was really happy with my wave 3 in my 13. It replaced a vented cat heater that had a fan.

Half the time now, as it is, I have to use my black cat heater because the furnace won't light.

I will note that one thing about my furnace that really scares me is it sometimes makes a huge explosion when trying to light.. like a backfire. Sounds like a gunshot when outside the rig, and it's a big "Whoosh" when inside. Like when your water heater fires up after lighting the pilot and it catches.

It DOES light after that boom, however.
Gina D.

I guess I didn't make it clear that I was responding to Christi V's original post with the comment on checking the 12V line.

I've seen problems with voltage sag on a 12V system when lights are turned on or if the refrigerator (especially the refrigerator with it's high current draw) is set to 12V operation. It often takes a while to isolate the problem since the dynamic load on the 12V bus could be, and very often is, different every time the furnace tries to light. I know of at least two people who have bought new furnaces when they had intermittent ignition problems and the problems persisted with the new units. Eventually we were able to trace the fault to varying 12V and found a specific component/splice/condition that caused the voltage variation.



One comment on your situation where you describe the "explosion when trying to light.. like a backfire". The only way that would happen is if your blower isn't clearing the firebox before the ignition cycle starts. I've seen this happen if there is a partial obstruction in the firebox outside air intake or exhaust vent. The most common obstruction is a wasp nest and when that is the problem the nest usually moves around so the problem is intermittent. At least if that is the problem the heat usually kills the wasps so you have a vacant wasp condo to remove. The job could get exciting if the wasps were still occupying the nest.

I also agree with your comments on messing with propane and electricity. If you don't have the training and experience then save up your bucks and take the problem to a pro.

Rule for working with electricity: Always ensure that the circuit is disconnected from the source of power lest ye be deposited on your buttocks in a most undignified manner.

Rule for working with propane: Propane + air + spark = disaster
Orlen Wolf is online now   Reply With Quote
Old 08-21-2008, 09:38 PM   #15
Senior Member
 
Gina D.'s Avatar
 
Trailer: Former Burro owner and fan!
Posts: 9,015
Registry
'lectricity I have no issue with. I work with it all day for a living..

it's the nasty "spark" part near propane I am leary of

Thanks for the blockage info. I'll get the manual and see if this is something I should be looking at without violating safety things.
Gina D. is offline   Reply With Quote
Reply

Tags
furnace


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
RV Furnace Rick Helgren Classified Archives 0 06-16-2008 09:01 AM
furnace Arlyn R Problem Solving | Owners Helping Owners 3 03-22-2008 10:24 PM
Furnace next to bed Daniel V. Problem Solving | Owners Helping Owners 15 03-18-2008 05:51 PM
Looking for a furnace! brian barker Problem Solving | Owners Helping Owners 1 08-23-2007 03:56 PM
Furnace Timmy G Classified Archives 7 07-11-2006 03:59 PM

» Upcoming Events
No events scheduled in
the next 465 days.
» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 09:47 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.