Furnace Trouble-Shooting

Time to get this thing running! If I can...

Last fall it would come on and the fan would run, but failed to ignite. Probably a problem with the circuit board. While I was poking around, having forgot to pull the fuse, I saw a spark. I was checking connections, pulling them with pliers. After that, nothing. Furnace wouldn't even turn on. No fan, nothing.

I replaced the board and sail switch, I tested the limit switch (it's fine), and I bypassed the thermostat. Still no power to the board. So at this point, so far as I can figure, it's either the time delay relay, or the motor itself.

So the questions...how to test the motor? If the motor is bad, would that cause the circuit board not to get power? Would a bad time delay relay cause the board not to get power?

My furnace is an Atwood Hydroflame, HF8012D. From a 91 camper.

Where I'm at is...IF it's the motor, everything I can find tells me it cannot be replaced. The 8012 II has a lot of compatible parts, but the motor ain't one. So if the motor is bad, I'm wasting my time and money on the furnace to trouble-shoot any further. So I'd like to test it. But I'm not sure if a bad motor would cause no power to the circuit board. ? The time delay relay also seems to be a no-longer-available part, but I'm still checking some places. The 8012 II is the same exact size, perfect-fit replacement for my furnace, but interior parts have changed.

If the motor is bad I'm looking at needing a replacement furnace. Suburban is affordable but means modifications to my cupboards and fiberglass shell. The 8012 II, direct-fit replacement from Atwood is over $700.

Any ideas?
ZachO is offline   Reply With Quote
Old 03-20-2018, 09:57 AM   #2
Senior Member
 
Name: bob
Trailer: Was A-Liner now 13f Scamp
Missouri
Posts: 3,209
my thoughts

zack have you checked at your final output off your board if you have 12v to your fan using a vom or a test light? if you do and the fan wont run then its your motor.

you can also run a clip from 12v to your fan motor directly to see if it will run. I hate all those circuit boards and new things makes it hard to work on them!

if that furnace is shot I would consider a wave 3 for heat with warning you need to vent top and window slightly for makeup air.

bob
k0wtz is offline   Reply With Quote
Old 03-20-2018, 10:18 AM   #3
Senior Member
 
Name: Steve
Trailer: Scamp 13
California
Posts: 1,890
Maybe this will help if you don't have one.
stevebaz is offline   Reply With Quote
Old 03-20-2018, 10:23 AM   #4
Senior Member
 
Byron Kinnaman's Avatar
 
Trailer: Scamp
Posts: 7,056
Registry
I would guess that you blew up control circuits. At this point the best thing to do is take the furnace to a Atwood repair center. Let them fix if for you. Yes it'll cost a few bucks but that's better than blowing up your trailer.
__________________
Byron & Anne enjoying the everyday Saturday thing.
Byron Kinnaman is offline   Reply With Quote
Old 03-20-2018, 10:32 AM   #5
Senior Member
 
mszabo's Avatar
 
Trailer: U-Haul VT16
Posts: 982
Zach, Bob has a good point. You need to test for voltage to the furnace.
You started by saying it was running. Until you were poking around with pliers.
And then a spark. Spark means short, means blown fuse.
Until you can determine if you have power to your unit. We can’t help, throwing parts at it isn’t the answer.
Things that will help us help you.
Verify 12 volt going to furnace.
Then let’s go from there.
mszabo is offline   Reply With Quote
Old 03-20-2018, 10:33 AM   #6
Senior Member
 
Name: Jack L
Trailer: Sold the Bigfoot 17-Looking for a new one
Washington
Posts: 1,561
How much time and money do you want to invest in a 27 year old furnace? If it was mine, I would consider a new $700 furnace.
Jack L is offline   Reply With Quote
Old 03-20-2018, 10:55 AM   #7
Senior Member
 
mszabo's Avatar
 
Trailer: U-Haul VT16
Posts: 982
Did you check this breaker?
Attached Thumbnails
8C6AE304-4ADC-41A5-AB71-E27AFCF0A6D9.jpg  
mszabo is offline   Reply With Quote
Old 03-20-2018, 03:52 PM   #8
Senior Member
 
Name: bob
Trailer: Was A-Liner now 13f Scamp
Missouri
Posts: 3,209
seen many things

I sold expensive restaurant cooking gear, 10k steam cookers and pots thrown out because I got them and had my repair guy who was a sharp electrician friend check them out.

guess what some minor 100.00 part blew and the place didn't have the sense to contact me or find someone who knew circuits to come check the piece of equipment out.

I have had schools with 50 year old ranges in them they would keep squacking this didn't work throw it out. I would order a new shut off valve or a new thermocouple and maintance would get them going again.

unless that exchanger is burned out I bet that furnace is fixable! a hospital kitchen just had to have new ovens with a bunch of electronics in them expensive. I told them they were buy a service nightmare those electronics wouldn't cope with all that heat. sure enough repairs all the time!


bob
k0wtz is offline   Reply With Quote
Old 03-20-2018, 06:02 PM   #9
Senior Member
 
Trailer: Boler 13 ft / Casita FD
Posts: 2,038
If all goes bad. I found a used suburban that came out of a pop-up and it was the exact size and shape of the hydroflame in my Boler, at a RV dealer shop who sells used parts.
Paid $200 and it's been working great for 4 years now. New furnace has electronic ignition and old one had a standing pilot.
Gerry is offline   Reply With Quote
Old 03-20-2018, 06:20 PM   #10
Senior Member
 
ZachO's Avatar
 
Name: Z
Trailer: Sasquatch
Montana
Posts: 2,556
Thanks everyone. A couple thoughts...

I don't want to invest any time or money in a 27 year old furnace. But it's visibly in almost brand new condition, and I can't afford $700.

My thinking is replacing the circuit board, known to fail and known to cause my initial issue of the furnace kicking on but being unable to fire, and while I'm at it, put in a new sail switch since they also fail, is reasonable. So I've invested under $110. I think that was a safe bet. Except it didn't pay off But it was worth it to me with $100/hr repair rates.

It's a fairly simple appliance as far the electronics. Circuit board, sail switch, limit switch, time delay relay, motor, fuse, thermostat. I'm just testing and replacing electronics as whole units, a couple screws and a couple plugs. I don't figure that's doing anything dangerous.

Ok, so- I forgot to mention that the fuse is good. Assuming the fuse in the diagram is the one I think it is. There are three fuses: one on the circuit board (brand new and functional), one in the power center (functional) and the breaker in the furnace (functional). I tested all these with a multi-meter using a continuity test.

So now how to do I tell if the furnace is getting 12v?

What I know is:

good fuses
limit switch has continuity
new circuit board
new sail switch

The light on the circuit board isn't lighting up so it's not getting 12V to the board.

So I guess I look at the diagram to see where 12V first comes into the furnace...which I'm afraid means pulling it again but I'll check...First I'll check at the thermostat, though.

Thanks.
ZachO is offline   Reply With Quote
Old 03-20-2018, 06:37 PM   #11
Senior Member
 
mszabo's Avatar
 
Trailer: U-Haul VT16
Posts: 982
Zach, you should have four wires running into the furnace.
Two are thermostat and the other two will be your 12v dc.
The heavier gauge wire should be the dc circuit.
Test at that point for 12v dc. If you have it there then it’s in the furnace.
If no power trace back to power source.
If power, next test for 12v dc at relay.
If you have power to furnace, you may have trashed the thermostat. Put both wires together, see if it fires.
You’ll get it, take your time and use your meter or test light.
mszabo is offline   Reply With Quote
Old 03-20-2018, 07:06 PM   #12
Senior Member
 
mszabo's Avatar
 
Trailer: U-Haul VT16
Posts: 982
This may help

http://bryantrv.com/docs2/docs/hflameservice.pdf
mszabo is offline   Reply With Quote
Old 03-20-2018, 07:34 PM   #13
Senior Member
 
ZachO's Avatar
 
Name: Z
Trailer: Sasquatch
Montana
Posts: 2,556
Thank you.

I did hold the two wires at the thermostat together and still no light on the circuit board.

The wires going into the furnace are accessible by taking the furnace out...so I’ll look over the wiring diagram and see where they first connect in the furnace and test for 12v there. Looks like it may be at the breaker.

I have the original manual, which is slightly better than that link, since the link is for the newer model. But thank you!

Click image for larger version

Name:	DFD8D0D3-BEAC-4E7A-A02C-7D0BD5CC0263.jpg
Views:	31
Size:	220.1 KB
ID:	116928
ZachO is offline   Reply With Quote
Old 03-20-2018, 07:42 PM   #14
Senior Member
 
mszabo's Avatar
 
Trailer: U-Haul VT16
Posts: 982
You’ll get it!
mszabo is offline   Reply With Quote
Old 03-20-2018, 07:42 PM   #15
Senior Member
 
ZachO's Avatar
 
Name: Z
Trailer: Sasquatch
Montana
Posts: 2,556
Quote:
Originally Posted by mszabo View Post
If you have power to furnace, you may have trashed the thermostat. Put both wires together, see if it fires.
Hey just making sure this is correct. I’ve been assuming that if the furnace is getting power, the thermostat must be good. Is that wrong?

I thought all power went first through the thermostat then to the furnace for the first time.

Let me know. I’m used to being wrong but want to make sure that wasn’t a typo!
ZachO is offline   Reply With Quote
Old 03-20-2018, 07:46 PM   #16
Senior Member
 
Name: bob
Trailer: Was A-Liner now 13f Scamp
Missouri
Posts: 3,209
Keep thinking and studying you will get it bob
k0wtz is offline   Reply With Quote
Old 03-21-2018, 03:48 PM   #17
Senior Member
 
ZachO's Avatar
 
Name: Z
Trailer: Sasquatch
Montana
Posts: 2,556
I have 12.6 volts on both sides of the fuse in the power center. I have something that settles around 178 mV at the thermostat...

Seems like anywhere I’m checking for 12v where there isn’t any (?), my meter shows me some mV number. Might be some fluke with how my meter works, I don’t know.

So I still don’t know if power goes to the thermostat before going inside the furnace.

I have continuity through the thermostat, but no 12v. So obviously no 12v coming through the thermostat to the breaker in the furnace.

What next? What’s between the power center fuse and the thermostat?
ZachO is offline   Reply With Quote
Old 03-21-2018, 04:32 PM   #18
Senior Member
 
mszabo's Avatar
 
Trailer: U-Haul VT16
Posts: 982
Zach, the milamp at thermastat is what you want.
Those wires wont carry the load to motor.
If you read through the manual, once the thermostat calls for heat it’s 18 seconds before relay makes contact. Which then will put 12v to the motor, and sail switch.
Make sure you have the 12v at the relay, see picture. If you do, you can jump or remove wire and touch other side. Bypassing relay and putting 12v to motor.
Also turn on thermostat and check for voltage at relay. If you have it, 15 seconds later it should pull in coil.
My money is on that relay.
mszabo is offline   Reply With Quote
Old 03-22-2018, 09:03 AM   #19
Senior Member
 
ZachO's Avatar
 
Name: Z
Trailer: Sasquatch
Montana
Posts: 2,556
Well I'll admit I'm not quite sure what you're saying on a lot of this, but I'll keep checking stuff.

If the furnace calls for 12V for a few seconds then gives up, am I in a rush to test at the thermostat? Will there be 12V when I first turn it on, then it'll stop when the furnace fails to do anything?

Well, I'm taking another unadvisable step. It's fairly safe to assume that the wire from the power center to the thermostat didn't melt, and that the connections are still good, and that whatever shorted is in the furnace itself. I don't see a tiny spark causing a wire or connection that far away from the furnace to melt or break, though one last test I'll do is a resistance or continuity check on that wire.

Other than the electronics on the propane valve in the furnace, I've tested or replaced every switch, circuit board and fuse associated with the furnace, except the time delay relay. That's a $30 part. I'll throw $30 more at this thing, then if it doesn't run I'll decide whether to pay a technician or just buy a new furnace. I'm moving back in at the end of the month so it's time to get the camper functional.

Thanks for the help!
ZachO is offline   Reply With Quote
Old 03-22-2018, 09:44 AM   #20
Senior Member
 
Name: bob
Trailer: Was A-Liner now 13f Scamp
Missouri
Posts: 3,209
I admit I have never messed around with those relay circuits or el. circuits in a furnace I really don't understand them. they involve very low voltages such as millivolts to make things work including opening up the gas valve.


in your case I would pay a furnace guy to troubleshoot it for you I took out a bunch of el. stuff on my Vermont castings heating stove in order to put in a simple operated gas valve. all the operating controls are on the gas valve no electronics after looking at it he may or may not suggest how to fix it!


bob
k0wtz is offline   Reply With Quote
Reply

Tags
furnace


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water Shooting Out of Fresh Water Connection sal6342 Plumbing | Systems and Fixtures 2 04-28-2017 12:29 PM
Trouble shooting DC Electrical problems Daniel the Texan Problem Solving | Owners Helping Owners 27 12-16-2016 08:02 PM
Trillium trouble-shooting PatriciaSK Problem Solving | Owners Helping Owners 3 05-31-2016 09:38 AM
Shooting Sports Green Frog Hobbies & Passions 1 07-08-2011 05:26 PM
Water heater trouble shooting (Suburban 6 gallon) Legacy Posts Problem Solving | Owners Helping Owners 12 02-14-2003 11:06 AM

» Trailer Showcase

Daisy

Pomfritz

Galileo

Shredne
» Upcoming Events
No events scheduled in
the next 465 days.
» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 01:21 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.