Old 03-14-2009, 10:27 PM   #15
Senior Member
 
Dan Meyer's Avatar
 
Name: Dan
Trailer: Scamp
Minnesota
Posts: 559
I've got a Scamp 16 with A/C, and converted it to exclusively 15 amp operation. I installed a standard 15 amp power inlet into the port that the power cord goes thru. Read all about the conversion, including fusing to accomodate the smaller cord on my web site: http://scamp.n0kfb.org/ - click on modifications and repairs and scroll down 3/4th of the page.

-- Dan Meyer
__________________

__________________
Dan Meyer is offline   Reply With Quote
Old 03-15-2009, 08:29 AM   #16
Senior Member
 
Trailer: 2013 Escape 19
Posts: 362
Quote:
I've got a Scamp 16 with A/C, and converted it to exclusively 15 amp operation. I installed a standard 15 amp power inlet into the port that the power cord goes thru. Read all about the conversion, including fusing to accomodate the smaller cord on my web site: http://scamp.n0kfb.org/ - click on modifications and repairs and scroll down 3/4th of the page.

-- Dan Meyer
Dan,

I enjoyed reading through your website. Funny that you installed a fuse to match the new power cord. That's the same logic that led me to my original post on this subject! There are lots of ways to do this. Fortunately a non-air conditioned 13' Scamp is pretty simple, so I don't think this rocket surgery. I just want a more convenient setup than what we have now, whether that's a pigtail or fixed outlet for an extension cord connection. I'm about to swing the Scamp out of it's corner in the garage and get serious about this. I need to repair the cover for the existing power cord, meaning I'm likely to be removing it anyway, so I may go with the fixed outlet idea while I'm at it.

Funny, we're both hams (WD8JOL), Scamp owners, and Shopsmith owners. Scary!

Parker
__________________

__________________
Parker Buckley is offline   Reply With Quote
Old 03-15-2009, 08:37 AM   #17
Senior Member
 
Trailer: 2013 Escape 19
Posts: 362
Quote:
Parker,

You can replace the stock 30A shore power cable with a 20A cable as you described, just make sure the 120V circuit breaker(s) in your camper are sized accordingly. You probably have two or three 15A breakers in your camper's breaker box. One option you might want to think about is to run all the 120V circuits through just one of the 15A breakers; that would provide protection to a 20A shore power cable.

Pat
Pat,

There are only two 15A circuit breakers, but those are on the converter output side so it doesn't get fried by a fault somewhere downstream. There is no circuit protection on the input side of the converter. I could stick with a 30A extension cord, add a circuit breaker, or accept the logic that we often use extension cords sized appropriately for the load that are lighter duty than the breaker they're connected through, as Pete reminded.

Parker
__________________
Parker Buckley is offline   Reply With Quote
Old 03-15-2009, 08:44 AM   #18
Senior Member
 
Ed Harris's Avatar
 
Name: Ed
Trailer: 1982 Fiber Stream and 2002 Casita Freedom Deluxe,The driveway is a Dark & Lonely Place now!
Missouri
Posts: 1,776
Quote:
Dan,

Funny, we're both hams (WD8JOL), Scamp owners, and Shopsmith owners. Scary!

Parker
I got rid of my Shopsmith,it took up too much space but......

73
Ed
KC0UKR
__________________
Ed Harris is offline   Reply With Quote
Old 03-15-2009, 08:49 AM   #19
Senior Member
 
Trailer: 2013 Escape 19
Posts: 362
Quote:
I have seen this at Bass Pro Shops for under $20.00 and it is one way to do what you are asking cheaply.

I agree though that I would use the 30 amp twist-lock set myself and I have on each trailer I have had.

There is nothing though about this one I picture that you would have to worry about given your stated needs.

https://www.berrylandcampers.com/rv-parts/p...?productid=4419

This is also made by the same company that makes the twist-lock models so it seems to be very high quality,just for simpler loads.
Ed,

Thanks for the tip. They seem to be readily available. There is even a 20 amp version with different pin orientations, but I might as well stick with a 30 amp connector if I'm not going for the simplicity of the 15A model. I really think the 15A will serve our needs fine. Looks like a great price, and since it's already flanged this would be an easy one to adapt to the existing opening.

Parker
__________________
Parker Buckley is offline   Reply With Quote
Old 03-15-2009, 08:58 AM   #20
Senior Member
 
Dan Meyer's Avatar
 
Name: Dan
Trailer: Scamp
Minnesota
Posts: 559
Quote:
>snip<

Funny, we're both hams (WD8JOL), Scamp owners, and Shopsmith owners. Scary!

Parker
Actually, the Shopsmith belongs to my Dad. Not so scary anymore?

73 de n0kfb

-- Dan Meyer
__________________
Dan Meyer is offline   Reply With Quote
Old 03-15-2009, 01:01 PM   #21
Junior Member
 
Trailer: 1992 19 ft Scamp 19 ft 5th Wheel Deluxe
Posts: 16
Quote:
Pat,

There are only two 15A circuit breakers, but those are on the converter output side so it doesn't get fried by a fault somewhere downstream. There is no circuit protection on the input side of the converter. I could stick with a 30A extension cord, add a circuit breaker, or accept the logic that we often use extension cords sized appropriately for the load that are lighter duty than the breaker they're connected through, as Pete reminded.

Parker
Parker,

What year is your Scamp? I've had two Scamps (1992 & 1994) and both came from the factory with protection for the 120V circuits. Based on your previous post you evidently have 120V running to the fridge, at least one outlet (for your cube heater), and to the power converter. I would be very uncomfortable relying on the shore power cord as the "fuse" in the event of a 120V short or circuit overload inside the camper. The vision of a Scamp going up in flames is not a pleasant one for me.

Pat
__________________
Pat J is offline   Reply With Quote
Old 03-15-2009, 03:56 PM   #22
Senior Member
 
Trailer: 2013 Escape 19
Posts: 362
Quote:
Parker,

What year is your Scamp? I've had two Scamps (1992 & 1994) and both came from the factory with protection for the 120V circuits. Based on your previous post you evidently have 120V running to the fridge, at least one outlet (for your cube heater), and to the power converter. I would be very uncomfortable relying on the shore power cord as the "fuse" in the event of a 120V short or circuit overload inside the camper. The vision of a Scamp going up in flames is not a pleasant one for me.

Pat
Pat,

It's a 2004 model. There is circuit protection for both 120V lines, which come out of the converter. I don't see any sort of fuse or circuit breaker on the power cord which runs from the backside of the converter to the pedestal, nor do I see why one one be necessary if everything is rated for 30A. That's the job of the breaker in the pedestal, at least from what I can tell. We can still discuss the wisdom of running a 15A cord from the converter to the pedestal, if it's connected to the 30A breaker there, rather than the 15A one that usually sits next to it. I'm still puzzling over how great an idea that is, but I think it's done quite often, othewise they wouldn't sell so many adapters to make it easy.

Parker
__________________
Parker Buckley is offline   Reply With Quote
Old 03-15-2009, 05:35 PM   #23
Junior Member
 
Trailer: 1992 19 ft Scamp 19 ft 5th Wheel Deluxe
Posts: 16
Quote:
Pat,

It's a 2004 model. There is circuit protection for both 120V lines, which come out of the converter. I don't see any sort of fuse or circuit breaker on the power cord which runs from the backside of the converter to the pedestal, nor do I see why one one be necessary if everything is rated for 30A. That's the job of the breaker in the pedestal, at least from what I can tell. We can still discuss the wisdom of running a 15A cord from the converter to the pedestal, if it's connected to the 30A breaker there, rather than the 15A one that usually sits next to it. I'm still puzzling over how great an idea that is, but I think it's done quite often, othewise they wouldn't sell so many adapters to make it easy.

Parker

OK, now I think I understand. The newer Scamps, like yours, have the 120V breakers in the same unit as the power converter; the older ones, like mine, have a 120V breaker box that is separate (and upstream, electrically speaking) from the power converter. The two 15A breakers you describe are what protect your 30A shore power cord (even if it is connected to a 50A campground pedestal).

Pat
__________________
Pat J is offline   Reply With Quote
Old 03-15-2009, 07:12 PM   #24
Senior Member
 
Pete Dumbleton's Avatar
 
Trailer: Scamp
Posts: 3,072
Send a message via Yahoo to Pete Dumbleton
Breakers are intended to protect *wiring* downstream, not upstream. The breakers inside the Scamp, be they in the converter (later models) or in a separate box (earlier models) are there to protect the Scamp's internal wiring, not the shore cable.

There is no dedicated protection for the shore cable, anymore than there is for your home appliances, like a toaster, lamp, TV set, water heater, dryer, etc., or for the wires feeding them.

The pedestal sees your Egg as an appliance, that just happens to have some internal protection for its internal wiring but not for its plug and cord.

BTW, electrically, it doesn't matter if the circuit breakers are inside the converter or outside, they are wired so the shore cable goes to the breaker(s) before the converter.
__________________
Pete Dumbleton is offline   Reply With Quote
Old 03-21-2009, 08:34 PM   #25
Senior Member
 
Trailer: 2013 Escape 19
Posts: 362
Okay, the deed is done. I pulled out the 30 amp cable and installed a Marinco battery charging outlet as mentioned in an earlier post. This was really easy to do by making up a plywood flange to mate with the original holes in the Scamp. I'm now set up for a 15 amp extension cord arrangement. I also installed a bulkhead under the bench so we can use that area for storage without worrying about blocking the cooling air behind the converter. None of this is permanent or costly, so if at some point I feel like I need to return to 30 amp service, it will be easy to do. The pictures show the external outlet and the installation under the seat, including the new bulkhead. I took these pictures with 120V lighting plugged into the Scamp system. Please note the absence of smoke.

Thanks everyone for all your suggestions.

Parker
Attached Thumbnails
P1000719.JPG   P1000722.JPG  

P1000723.JPG   P1000724.JPG  

__________________
Parker Buckley is offline   Reply With Quote
Old 03-21-2009, 08:55 PM   #26
Senior Member
 
Ed Harris's Avatar
 
Name: Ed
Trailer: 1982 Fiber Stream and 2002 Casita Freedom Deluxe,The driveway is a Dark & Lonely Place now!
Missouri
Posts: 1,776
Nice and you didn't let the smoke out either!


__________________

__________________
Ed Harris is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Shore-power connector replaces pull-out cord peterh Modifications, Alterations and Updates 72 12-18-2016 12:43 PM
30 amp Power Cord francene Problem Solving | Owners Helping Owners 13 01-31-2010 07:50 AM
Sealing the Power Cord Door when in use Keith Williams Care and Feeding of Molded Fiberglass Trailers 21 09-29-2009 12:47 PM
Lost my power cord cover Kevin K General Chat 8 07-06-2009 11:53 AM
Power cord hatch/door Legacy Posts Electrical | Charging, Systems, Solar and Generators 11 10-17-2002 06:46 AM

» Upcoming Events
No events scheduled in
the next 465 days.
» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 08:55 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.