Scamp wired my AC with 14/2 and it is just not heavy enough for me to run the AC on my 2000W Inverter Generator so I would like to pigtail the 1 pair of 15gage wires together to use for the hot lead and run just 1 additional 8,10 or 12 gauge wire for the return.

If I pigtail the 14/2 AC wires together what Gauge wire would I wind up with?
__________________

__________________
Darwin Maring is offline   Reply With Quote
Old 07-06-2008, 11:11 PM   #2
Junior Member
 
James Harper's Avatar
 
Trailer: 1984 Fiber Stream
Posts: 29
Send a message via MSN to James Harper Send a message via Yahoo to James Harper
your inverter wont take the power surge to start the compressoror prob run it.. no matter what size wire you use....I run mine off of 110 ac and only have 14/2 as do most every trailer and motorhome made...

__________________

__________________
James Harper is offline   Reply With Quote
Old 07-07-2008, 04:41 AM   #3
Senior Member
 
Joe MacDonald's Avatar
 
Trailer: Trillium
Ontario
Posts: 754
Pairing the wires is a bad idea, and if done, it has to be done to both wires.. the return (or neutral) still has to carry the same current as the hot.
If you are going to the trouble, use a new #12awg for feed and return

Joe
__________________
Joe MacDonald is offline   Reply With Quote
Old 07-07-2008, 08:28 AM   #4
Senior Member
 
Trailer: 1960 28 ft Airstream
Posts: 336
Quote:
Pairing the wires is a bad idea, and if done, it has to be done to both wires.. the return (or neutral) still has to carry the same current as the hot.
If you are going to the trouble, use a new #12awg for feed and return

Joe
Pairing the wires is not advised for many reasons. The big one, is that it is not standard, and if you end up with a fire, your insurance may not cover. Another biggie is that someone can get a very bad shock if they aren't aware of your "change". The neutral does have to be the same size as your hot conductor, because it too carries current. (Just not current that you see.) In the event of a fault or short it can end up carrying as much if not more than your hot line can see. These little trailers are fairly easy to run wire...duct tape is wonderful to place it on the wall in the storage bins. Keep in mind that wire sizing is done to carry or manage the heat generated. Too small a wire, and it heats up and eventually torches.

Pam
__________________
Pamela H is offline   Reply With Quote
Old 07-07-2008, 08:41 AM   #5
Senior Member
 
Trailer: Casita 17 ft Spirit Deluxe
Posts: 509
Quote:
Keep in mind that wire sizing is done to carry or manage the heat generated. Too small a wire, and it heats up and eventually torches.

Pam
HUH!

Wire size is selected based on anticipated (design) loads and has nothiong to do with heat generated.

If you are having a problem running your Scamp air conditioner (8,000 BTU or less) on 14 ga. solid copper wire there is some wrong other than the A/C. I would suspect the 'inverter/generator' doesn't provide enough power (watts).
__________________
CD and Joyce Smith - Lily, Violet, and Rose
1999 Casita 17' SD - "The Little Egg"
2007 Escalade - 6.2L V8 - 6L80E Trans - 3.42 Diff
CD Smith is offline   Reply With Quote
Old 07-07-2008, 09:25 AM   #6
Senior Member
 
Steve L.'s Avatar
 
Name: Steve
Trailer: 2003 Casita 16' SD
Michigan
Posts: 1,690
Registry
Wire should be sized for load, but it is also well understood that undersized wire can/will heat up and can cause a fire as well as restrict current that can do damage to some motors.
__________________
Quando omni flunkus, moritati
Steve L. is offline   Reply With Quote
Old 07-07-2008, 12:55 PM   #7
Senior Member
 
Trailer: 1960 28 ft Airstream
Posts: 336
Quote:
HUH!

Wire size is selected based on anticipated (design) loads and has nothiong to do with heat generated.
The anticipated load is generally defined as watts. Watts is power, power is energy, energy produces heat. Smaller wires with larger loads get hot. This is why you don't put extension cords under material, esp. flammable material. In the event of an overload, you generate alot of current, and when there is current and voltage, you get power and alot of it. Have you ever noticed an extension cord to get hot? Get a bigger one. This is a simplified explanation, but if you overload an extension cord, I promise...it will get hot. Hot enough and it catches fire. For a simple calculation, you can take the current rating of the cord, multiply it by 110 and you will get your max. power rating in watts.

yes, it is sized by load...if you are curious I can probably send you a chart for wiring vs. load out of the NEC.




__________________
Pamela H is offline   Reply With Quote
Old 07-07-2008, 03:14 PM   #8
Senior Member
 
Name: Michael
Trailer: 1993 Bigfoot 17 ftCB / 2011 Toyota Sienna
Ontario
Posts: 207
Without getting into whether it's a good idea or not, the general rule is that each 3 gauges of wire double the cross-section area or half it in the other direction! #11 is half the cross-section area of #8 or double #14 gauge!
So 2 of #14 gauge wires equate to one #11 wire.
This is in resistance per 100' and in physical cross-section area NOT in current carrying capacity. Current carrying capacity also depends on the ability to dissipate heat.

Mike.....>

Quote:
Scamp wired my AC with 14/2 and it is just not heavy enough for me to run the AC on my 2000W Inverter Generator so I would like to pigtail the 1 pair of 15gage wires together to use for the hot lead and run just 1 additional 8,10 or 12 gauge wire for the return.

If I pigtail the 14/2 AC wires together what Gauge wire would I wind up with?
__________________
Michael Pupeza is online now   Reply With Quote
Old 07-07-2008, 06:56 PM   #9
Junior Member
 
James Harper's Avatar
 
Trailer: 1984 Fiber Stream
Posts: 29
Send a message via MSN to James Harper Send a message via Yahoo to James Harper
Go to the document center....there are the specs for alot of a/c units....the min. generator rating I see is 3.5kw The power drops alot after start up,,,but to get it going you need the full power....your inverter won't do it!!!!

__________________
James Harper is offline   Reply With Quote
Old 07-07-2008, 08:37 PM   #10
Senior Member
 
Trailer: Casita 17 ft Spirit Deluxe
Posts: 509
Quote:
Wire should be sized for load, but it is also well understood that undersized wire can/will heat up and can cause a fire as well as restrict current that can do damage to some motors.
Bang on Steve!

Undersized wire that is not fused or has a circuit breaker in the circuit can make very good radiant heaters and fire starters.

The best thing is to not abuse the wiring.
__________________

__________________
CD and Joyce Smith - Lily, Violet, and Rose
1999 Casita 17' SD - "The Little Egg"
2007 Escalade - 6.2L V8 - 6L80E Trans - 3.42 Diff
CD Smith is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Re-wire Vicki A. Electrical | Charging, Systems, Solar and Generators 11 02-10-2010 03:07 PM
wire rack ronsmith100 General Chat 16 05-10-2009 03:05 PM
110 VAC re-wire job done Gerry Modifications, Alterations and Updates 0 06-21-2007 04:41 AM
A Neat Wire Job Gerry Modifications, Alterations and Updates 2 08-27-2006 09:18 PM
What is the yellow wire? Victor Benz Problem Solving | Owners Helping Owners 15 06-29-2006 02:30 PM

» Upcoming Events
No events scheduled in
the next 465 days.
» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 07:30 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.