I have only towed our Scamp16 SD twice, both times I have ended up with 2 to 4" of water laying in the shower floor which I believe is coming from the drain line from the grey water holding tank. The previous owner installed a new check valve inline right after the little shower pump which should be stopping the grey water back flow...but isn't. I have unhooked the hose from one end of the check valve and used a screw driver to check the valve flap and seems to be working..the only thing I think may be wrong is the check valve isn't firmly mounted horizontal or vertical its hanging at an angle...is this the problem do you think? Or I guess the it just could be faulty. Anyone else ever have grey water back flow into the shower? Or what do you have inline to prevent grey water from running up into the shower when going downhill?
|
|
|
05-31-2011, 06:48 PM
|
#2
|
Senior Member
Trailer: 2009 Scamp 16 ft / 2003 Durango
Posts: 696
|
That check valve in the picture is upside down.
Bill K
|
|
|
05-31-2011, 07:48 PM
|
#3
|
Senior Member
Name: Tom
Trailer: none
Minnesota
Posts: 250
|
I dont have a inline check valve, but dont tow (so far ) with water in grey tank, doesnt the pump (mine is shurflow ) act as a check valve?
|
|
|
05-31-2011, 08:17 PM
|
#4
|
Senior Member
Trailer: 92 16 ft Scamp
Posts: 11,756
|
I dont have a check valve on mine either but I also dont tow with more than a tiny bit of water in the grey water tank so I have not had it back up to the shower while towing. Would not putting the plug into the shower base not stop it from coming up?
I know for sure though that the shurflow pump does not act as a check valve - found that out one day when I let the grey water tank got to full while camping. :-)
|
|
|
05-31-2011, 08:50 PM
|
#5
|
Senior Member
Name: Tom
Trailer: none
Minnesota
Posts: 250
|
installing check valve then...............replaced original drain so dont have a Plug, dont need any reverse flow issues!!
|
|
|
06-01-2011, 04:26 AM
|
#6
|
Member
Name: Baj
Trailer: 96 Scamp 16' SD
North Carolina
Posts: 79
|
I have the same, my drain wont except a plug....I took the check valve completely off to take a better look and I believe its broken since the valve gate is loose and flops around freely. I also ran water straight through it, up or down.
|
|
|
06-01-2011, 08:51 AM
|
#7
|
Senior Member
Name: Aaron
Trailer: 2002 Casita 17' Spirit Deluxe
Michigan
Posts: 161
|
That is a swing check and it is upside down. The cap must be rotated up, It works with a little gate that relies on gravity. Or you could replace it with a soft seated spring check, that is held closed in all directions with a spring. The way it is now will never work as you have discovered, the swing gate will never be closed unless your trailer is upside down.
|
|
|
06-01-2011, 11:33 AM
|
#8
|
Member
Name: Baj
Trailer: 96 Scamp 16' SD
North Carolina
Posts: 79
|
Thanks Bill n iplumb! I will reinstall it right side up and test it...
|
|
|
06-01-2011, 05:51 PM
|
#9
|
Senior Member
Trailer: 2009 Scamp 16 ft / 2003 Durango
Posts: 696
|
When you have it off reach in and clean the seating ring where the gate seals against the body as there may be soap scum on the seat.
Bill K
Quote:
Originally Posted by Baj
Thanks Bill n iplumb! I will reinstall it right side up and test it...
|
|
|
|
06-02-2011, 07:22 AM
|
#10
|
Member
Name: Baj
Trailer: 96 Scamp 16' SD
North Carolina
Posts: 79
|
Ok will do, thanks again Bill!
|
|
|
06-04-2011, 12:18 PM
|
#11
|
Senior Member
Name: Lew
Trailer: none
Pennsylvania
Posts: 199
|
I would consider
Quote:
Originally Posted by Baj
Ok will do, thanks again Bill!
|
I would consider using a ball valve if the check valve isn't going to work (Though it should once you turn it over).
You could close the ball valve while travelling.....and when you get to your camp spot, just reach under and open the lever.
Pretty simple.
have a good one.
|
|
|
06-05-2011, 03:01 PM
|
#12
|
Member
Name: Baj
Trailer: 96 Scamp 16' SD
North Carolina
Posts: 79
|
Good idea! Atleast manually closing a ball valve would eliminate the worry of the more complex swing check valve failing while in transit.
Thanks BigLew!
Hope your having a good one too!
|
|
|
10-03-2016, 02:27 PM
|
#13
|
Junior Member
Name: Glenn
Trailer: 2017 Bigfoot 25RQ
Virginia
Posts: 13
|
I have this same issue and I'm going to install a hepvo to replace the p trap. That should eliminate the back flow and eliminate a freeze point for winterization. Doesn't solve residual water in the pump and drain line though.
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
» Upcoming Events |
No events scheduled in the next 465 days.
|
|
All times are GMT -6. The time now is 03:23 PM.