Victron was supplying a water-tight enclosure for their shunt but absent from the package now.

jack
rabbit is offline   Reply With Quote
Old 11-14-2013, 02:30 PM   #82
Senior Member
 
Bob Miller's Avatar
 
Trailer: Class A Motorhome
Posts: 7,912
Most common shunts (i.e. 50 amp, 100 amp, 500 amp etc) are designed to drop a standard voltage value at the rated current flow. The most common value is 100mv. By designing meters and display devices to give full-scale readings at 100 mv a wide range of current capacities can be measured by selecting the correct shunt.

BUT.... shunts are precision resistive devices and leaving them exposed to the elements can quickly throw off it's very small resistive value by damaging the bonds between the terminals and the shunt material itself.

In short, never leave it exposed and, just the act of aggressive cleaning of a dirty shunt can destroy it's accuracy.

Best bet: New Shunt, either weatherproof protected or moved inside.
Second Best Bet: Get your cleaned up shunt retested for value.



Bob Miller is offline   Reply With Quote
Old 11-14-2013, 04:33 PM   #83
Senior Member
 
Byron Kinnaman's Avatar
 
Trailer: Scamp
Posts: 7,056
Registry
Quote:
Originally Posted by P. Raz View Post
That appears to be the higher current shunt ( 100 microvolts for each amp flowing through it). Basically a shunt is a precision resistor placed in the circuit you wish to measure the current through. The voltage across it is proportional to the current flowing through it (Ohm's law). The shunt has to be large enough to produce a significant voltage but not so large as to effect the current. With either of these shunts you are operating on the low end, with very small voltages. Voltages you could not measure accurately with the average DVM. It's a little like trying to measure the thickness of a penny with a yard stick.

Next time your battery needs charging, disconnect it from the trailer and charge it with the CTEK charger. Over night should do. In the morning, check it with the DVM. If it's 12.6 V. or higher I would say the charger is working fine. Good luck, Raz
Raz, When I looked at the cable it appears like it 4 wires. If so it's Kelvin which should negate noise in the measurement lines. Also according the web site the monitor is supposed to measure down to .5 amps. I agree with DVM not reading the voltage drop at any distance from the shunt. Short leads and right at the shunt, I think it would depend on the DVM.
__________________
Byron & Anne enjoying the everyday Saturday thing.
Byron Kinnaman is offline   Reply With Quote
Old 11-14-2013, 04:41 PM   #84
Senior Member
 
Byron Kinnaman's Avatar
 
Trailer: Scamp
Posts: 7,056
Registry
Quote:
Originally Posted by ruscal View Post
Jeez, I can't get this electrical stuff right! I found a voltage drop calculator at supercircuits.com and just plugged in 12v DC 200' 5amps 14ga and pushed the button. It says 5 volts drop. I believe it to be correct. It didn't have a choice for copper or al wire, so I figured it would be copper by default.
Russ

First off make up your mind is it 200' or 100' .

Second AWG 14 is .2525 ohms per 100' At 10 amps that 2.525 volts drop.

In your second post you said 200' that would about 5 volts. 200' is also long ways about 2/3 of a foot ball field.
__________________
Byron & Anne enjoying the everyday Saturday thing.
Byron Kinnaman is offline   Reply With Quote
Old 11-14-2013, 05:01 PM   #85
Raz
Senior Member
 
Raz's Avatar
 
Trailer: Trillium 2010
Posts: 5,185
Quote:
Originally Posted by Byron Kinnaman View Post
Raz, When I looked at the cable it appears like it 4 wires. If so it's Kelvin which should negate noise in the measurement lines. Also according the web site the monitor is supposed to measure down to .5 amps. I agree with DVM not reading the voltage drop at any distance from the shunt. Short leads and right at the shunt, I think it would depend on the DVM.
I'm not familiar with "Kelvin" other than a temperature scale. The wire they are using looks like twisted pair to me?? Is Kelvin a brand? Edit: Looked it up. 4 point probe. Got it.

When I read the Trimetric installation manual it appears that these instruments are intended for the solar industry with kilowatt arrays supplying banks of batteries. It recommends if you have a current as low as 70 amps to use the 100 amp, 100 mV shunt. Much higher than RV applications in most cases. .





Quote:
Originally Posted by Byron Kinnaman View Post
First off make up your mind is it 200' or 100' .

Second AWG 14 is .2525 ohms per 100' At 10 amps that 2.525 volts drop.

In your second post you said 200' that would about 5 volts. 200' is also long ways about 2/3 of a foot ball field.
perhaps 100 ft of cord, two conductors, 200 feet?? Raz
Raz is offline   Reply With Quote
Old 11-14-2013, 05:12 PM   #86
Senior Member
 
Byron Kinnaman's Avatar
 
Trailer: Scamp
Posts: 7,056
Registry
Quote:
Originally Posted by P. Raz View Post
I'm not familiar with "Kelvin" other than a temperature scale. The wire they are using looks like twisted pair to me?? Is Kelvin a brand? Edit: Looked it up. 4 probe. Got it.

When I read the Trimetric installation manual it appears that these instruments are intended for the solar industry with kilowatt arrays supplying banks of batteries. It recommends if you have a current as low as 70 amps to use the 100 amp, 100 mV shunt. Much higher than RV applications in most cases. .







perhaps 100 ft of cord, two conductors, 200 feet?? Raz
Kelvin is using 4 wires for measurement. Two wires are sense wires and the other two are measurement wires. You eliminate the wire resistance and common mode noise.

I found a bit information, but I don't think it's complete. Also I would have to see the schematic for the trimetric measurement system. Here's a bit, I had to search on "Kelvin Clip".

I can't remember when the last time I used a Kelvin Clip or Kelvin measuring system, it's been a while.
__________________
Byron & Anne enjoying the everyday Saturday thing.
Byron Kinnaman is offline   Reply With Quote
Old 11-14-2013, 05:22 PM   #87
Senior Member
 
Byron Kinnaman's Avatar
 
Trailer: Scamp
Posts: 7,056
Registry
Trimetric's Manual

"Which shunt should
you use?
Most systems with medium and large inverters should use a 500A
-
50 mV shunt, which will
work for systems to 400 amps maximum (4000 watts with 12 V systems and 8000 watts for 24V systems.) With this
shunt you can measure current as low as 1/10 amps. You can use a 100 A/100mV shunt with smaller systems which don't
use or charge with over 75 amps, (800 watts for 12 system, or 1600 watts for 24 volt system) or if the shunt is used only
for measuring solar or wind input with currents less than 75 amps
. This shunt has the advantage that it will show an extra
digit to the right of the decimal point, and resolve currents as low as 1/100 amp"

This is of course ± the lest 1 of least significant digit. Other than that I have no idea how accurate it would be.
__________________
Byron & Anne enjoying the everyday Saturday thing.
Byron Kinnaman is offline   Reply With Quote
Old 11-14-2013, 05:51 PM   #88
Raz
Senior Member
 
Raz's Avatar
 
Trailer: Trillium 2010
Posts: 5,185
500amp, 50mV shunt R = 0.1 milliohms

At 1/10 amp (100 milliamps) there would be a voltage drop of 100 milliamps x 0.1 milliohms = 10 microvolts. Neat trick Raz
Raz is offline   Reply With Quote
Old 11-14-2013, 06:14 PM   #89
Senior Member
 
Byron Kinnaman's Avatar
 
Trailer: Scamp
Posts: 7,056
Registry
Quote:
Originally Posted by P. Raz View Post
500amp, 50mV shunt R = 0.1 milliohms

At 1/10 amp (100 milliamps) there would be a voltage drop of 100 milliamps x 0.1 milliohms = 10 microvolts. Neat trick Raz
You can measure pretty low voltages with a 4 wires and resistive bridge. (my memory is coming back). Then through an amplifier to get the voltage high enough for an A to D converter. Not that impossible.
The specs on my Fluke 87 say it's resolution is .1 mv and and .1 microamp, that's for a hand held 2 wire measurement.
__________________
Byron & Anne enjoying the everyday Saturday thing.
Byron Kinnaman is offline   Reply With Quote
Old 11-14-2013, 11:46 PM   #90
Senior Member
 
Name: Russ
Trailer: Scamp 16' side dinette, Airstream Safari 19'
California
Posts: 588
I just went out to the Scamp and read the Trimetric. 12.5v, 86% batt life, -.1A. I then turned on LED lights one by one. Each consumed .2A and read 1A with 5 lights on. I don't know if the -.1A is due to a phantom load, or just a calibration issue with the Trimetric or shunt contamination. When I get a chance I'll put the Fluke in series and see what it says. Just for grins I plugged in one of those cigarette lighter battery condition meters. It read 12.4v, one tenth volt lower than the Tri. I'll plug in the CTEK and let it run over night to get the battery back up.
ruscal is offline   Reply With Quote
Old 11-14-2013, 11:55 PM   #91
Senior Member
 
Name: Drew
Trailer: Trillium
Alberta
Posts: 112
Registry
Don't forget your trimetric consumes power. It will show a negative amp reading if all of your appliances are off. If I recall correctly mine draws .03 to .04 amps. I get the extra digit on my meter with the 100 amp shunt.
__________________
Where we’re going, we don’t need a plug-in.
multi-task is offline   Reply With Quote
Old 11-15-2013, 12:07 AM   #92
Senior Member
 
Name: Russ
Trailer: Scamp 16' side dinette, Airstream Safari 19'
California
Posts: 588
I plugged in the CTEK about 10 minutes ago. It has already ramped through 3 steps. First step 14.2v Tri reading -.1A Second and third step 14.3v Tri reading -.1A. The charger is obviously putting current into the battery, but the Trimetric shows the opposite. ??? I will remove the shunt and clean it when I get some time. I may just send it back to Deltec for a calibration. Then I will remount it properly protected.
Russ
ruscal is offline   Reply With Quote
Old 11-15-2013, 12:08 AM   #93
Senior Member
 
Name: Russ
Trailer: Scamp 16' side dinette, Airstream Safari 19'
California
Posts: 588
Quote:
Originally Posted by multi-task View Post
Don't forget your trimetric consumes power. It will show a negative amp reading if all of your appliances are off. If I recall correctly mine draws .03 to .04 amps. I get the extra digit on my meter with the 100 amp shunt.
Drew,
Is that with the meter LED turned off?
Russ
ruscal is offline   Reply With Quote
Old 11-15-2013, 12:44 AM   #94
Senior Member
 
Name: Drew
Trailer: Trillium
Alberta
Posts: 112
Registry
That's when it's on and displaying the numbers. I'm winterized (batteries pulled out) or I'd just go and look to be sure.

I've used a few different chargers and they've always shown positive amps going in with the green charging light illuminated.
__________________
Where we’re going, we don’t need a plug-in.
multi-task is offline   Reply With Quote
Old 11-15-2013, 02:01 AM   #95
Senior Member
 
Name: Russ
Trailer: Scamp 16' side dinette, Airstream Safari 19'
California
Posts: 588
Drew,
I just went out to check charging progress. After 1.5 hours it picked up just 1% to 87%. Charge voltage read 14.2 and amps still negative .1. The green charge light is not lit. I put my Fluke 337 true RMS clamp meter on the CTEK charge line and got 1.9A, So the Trimetric is probably being fooled by the shunt about 2 amps worth. I had forgotten the Fluke could read DC, so didn't think to use it previously.
Russ
ruscal is offline   Reply With Quote
Old 11-15-2013, 05:51 AM   #96
Raz
Senior Member
 
Raz's Avatar
 
Trailer: Trillium 2010
Posts: 5,185
Quote:
Originally Posted by Byron Kinnaman View Post
You can measure pretty low voltages with a 4 wires and resistive bridge. (my memory is coming back). Then through an amplifier to get the voltage high enough for an A to D converter. Not that impossible.
The specs on my Fluke 87 say it's resolution is .1 mv and and .1 microamp, that's for a hand held 2 wire measurement.
I took a second look and I'm not sure they are doing a 4 point probe measurement as suggested in the link you provided. That appears to be for impedance measurements. I think they are using two wires for shunt voltage and two wires for battery voltage and keeping them separate at the meter because the two are orders of magnitude apart. When you get yours check it out and let me know if I'm wrong . Raz
Raz is offline   Reply With Quote
Old 11-15-2013, 10:43 AM   #97
Senior Member
 
Byron Kinnaman's Avatar
 
Trailer: Scamp
Posts: 7,056
Registry
Quote:
Originally Posted by P. Raz View Post
I took a second look and I'm not sure they are doing a 4 point probe measurement as suggested in the link you provided. That appears to be for impedance measurements. I think they are using two wires for shunt voltage and two wires for battery voltage and keeping them separate at the meter because the two are orders of magnitude apart. When you get yours check it out and let me know if I'm wrong . Raz
You could be right. I counted 4 wires in the picture of the cable.
I'm not about to buy one. It's too easy to buy all this stuff and get into an information overload rather than enjoying the great outdoors.
__________________
Byron & Anne enjoying the everyday Saturday thing.
Byron Kinnaman is offline   Reply With Quote
Old 11-15-2013, 11:14 AM   #98
Senior Member
 
Name: Drew
Trailer: Trillium
Alberta
Posts: 112
Registry
Quote:
Originally Posted by ruscal View Post
Drew,
I just went out to check charging progress. After 1.5 hours it picked up just 1% to 87%. Charge voltage read 14.2 and amps still negative .1. The green charge light is not lit. I put my Fluke 337 true RMS clamp meter on the CTEK charge line and got 1.9A, So the Trimetric is probably being fooled by the shunt about 2 amps worth. I had forgotten the Fluke could read DC, so didn't think to use it previously.
Russ
Just to make sure you've set it up right, did you connect your chargers negative wire to the shunt? I've seen this type of behavior if the charger was directly connected to the battery bypassing the shunt. I'd also make sure all of the smaller wires connected to the shunt are in good condition. If those are corroded or broken (they are pretty thin) it might cause an issue.

It does sound like your charger is working or you wouldn't have such a high voltage. The battery % likely won't be accurate if the meter isn't recording amps going in.

If you're sure the meter is programmed correctly and the shunt is wired according to the diagram in the manual I'd likely replace the shunt as a next step. Sounds like it might have gone bad or perhaps was a lemon to start with. With some luck it's just the shunt and not a bad meter.
__________________
Where we’re going, we don’t need a plug-in.
multi-task is offline   Reply With Quote
Old 11-15-2013, 09:50 PM   #99
Senior Member
 
Name: Russ
Trailer: Scamp 16' side dinette, Airstream Safari 19'
California
Posts: 588
Drew,
I talked to Bogart Engineering today. I described the symptoms I was having. He told me to take 2 aspirins, no wait, he said exactly what you said. Any items you want monitored must have their ground wires going through the shunt. So if you hook up your charger the positive lead connects to the battery plus post. The negative must connect to the shunt lug farthest from the battery. (the large shunt lug) If not the charger is not being monitored. He said only the only wire connected to the battery negative post should be coming from the shunt. All other grounds should connect to the shunt lug farthest from the battery. I'll have to check my installation when I get back home tomorrow and see what I did. It totally made sense what he told me.

Disclaimer: I think I understood what the man was telling me, but I have not verified the info in my case. So please don't take anything I said above to be factual. I will see if it solves the problem I was experiencing and report back.
Russ
ruscal is offline   Reply With Quote
Old 11-15-2013, 10:51 PM   #100
Senior Member
 
Byron Kinnaman's Avatar
 
Trailer: Scamp
Posts: 7,056
Registry
Quote:
Originally Posted by ruscal View Post
Drew,
I talked to Bogart Engineering today. I described the symptoms I was having. He told me to take 2 aspirins, no wait, he said exactly what you said. Any items you want monitored must have their ground wires going through the shunt. So if you hook up your charger the positive lead connects to the battery plus post. The negative must connect to the shunt lug farthest from the battery. (the large shunt lug) If not the charger is not being monitored. He said only the only wire connected to the battery negative post should be coming from the shunt. All other grounds should connect to the shunt lug farthest from the battery. I'll have to check my installation when I get back home tomorrow and see what I did. It totally made sense what he told me.

Disclaimer: I think I understood what the man was telling me, but I have not verified the info in my case. So please don't take anything I said above to be factual. I will see if it solves the problem I was experiencing and report back.
Russ
What you said above would be true.
__________________
Byron & Anne enjoying the everyday Saturday thing.
Byron Kinnaman is offline   Reply With Quote
Reply

Tags
battery


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Battery Charging? nzwasp Electrical | Charging, Systems, Solar and Generators 4 07-17-2013 09:35 AM
Battery Charging SurfsideEd Electrical | Charging, Systems, Solar and Generators 19 08-23-2012 06:41 PM
Charging Battery and running battery lights when plugged in Nor_Cal_Todd Problem Solving | Owners Helping Owners 2 08-25-2010 01:44 PM
Battery Charging Chester Taje Problem Solving | Owners Helping Owners 4 08-01-2007 05:56 PM
charging the battery Mo22 Electrical | Charging, Systems, Solar and Generators 9 07-08-2007 06:10 PM

» Upcoming Events
No events scheduled in
the next 465 days.
» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:16 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.