Is there a rule of thumb to determine what gauge the ground wire should be both in the trailer and through the harness?
__________________

__________________
DaMScampers is offline   Reply With Quote
Old 04-23-2014, 09:00 AM   #2
Senior Member
 
Name: Greg
Trailer: 2008 Casita 17 SD
Washington
Posts: 1,047
Registry
10 gauge is typical.
__________________

__________________
Casita Greg is offline   Reply With Quote
Old 04-24-2014, 06:26 AM   #3
Senior Member
 
DaMScampers's Avatar
 
Name: David
Trailer: Scamp
Michigan
Posts: 140
Is this a safety issue? Would 12 gauge cut it?
__________________
DaMScampers is offline   Reply With Quote
Old 04-24-2014, 07:32 AM   #4
Senior Member
 
Name: Randy
Trailer: 1980Trillium 1300
Ontario
Posts: 355
Very good question. Here is simple quote...".. Remember that common ground wires must be adequate to carry the TOTAL amperage of the circuit, even when separate hot wires are used..."...
Wire Gauge Specification - TECHNICAL REFERENCE
__________________
Thinh is offline   Reply With Quote
Old 04-24-2014, 08:00 AM   #5
Senior Member
 
DaMScampers's Avatar
 
Name: David
Trailer: Scamp
Michigan
Posts: 140
Thank you! There's my answer!
__________________
DaMScampers is offline   Reply With Quote
Old 04-24-2014, 08:28 AM   #6
Senior Member
 
Steve L.'s Avatar
 
Name: Steve
Trailer: 2003 Casita 16' SD
Michigan
Posts: 1,690
Registry
You question can be answered with as much complication as you desire. If youíre looking for a simple, no-thought answer I think 10 ga. is a good one.

In general (and Iím no EE) you get to make your first decision as to how much voltage drop you want to tolerate. Voltage drop is a function of wire gauge, round trip wire length and amperage. There are all sorts of tables and calculators to help determine what wire gauge to use. West Marine has one I use, mostly because Iíve had a sailboat for longer than Iíve had the trailer. I generally shoot for 3% drop in the 12V side. Why? No reason. I did more boondocking in the past and I wanted as little loss as practical without going into room temperature superconductors. From the table, assuming a 32 foot round trip (I have a Casita 16í SD) and 10 amps moving to the trailer from the tow, then that puts me right in the green band, or 10 ga.

I have one circuit I have fused for 20 amps that supplies the macerator pump I sometimes use to dump uphill or to speed the dump process. The outlet for that is right behind the fuse panel on the streetside of the trailer. Round trip length of inside and outside wiring is about 12-14 feet. That puts me again in the 10 ga band which is what I used.

Do you need 3% drop? No. Paraphrasing the Gallagher routine, itís about style. Just watch out for the Sledge-O-Matic and the exploding watermelonÖ
Attached Thumbnails
West Marine Wire Ga vs Loss.JPG  
__________________
Steve L. is offline   Reply With Quote
Old 04-24-2014, 10:39 AM   #7
Senior Member
 
DaMScampers's Avatar
 
Name: David
Trailer: Scamp
Michigan
Posts: 140
Again, thanks.
__________________
DaMScampers is offline   Reply With Quote
Old 04-24-2014, 10:45 AM   #8
Senior Member
 
Name: None
Trailer: None
None
Posts: 2,730
Quote:
Originally Posted by Steve L. View Post
You question can be answered with as much complication as you desire. If youíre looking for a simple, no-thought answer I think 10 ga. is a good one.

In general (and Iím no EE) you get to make your first decision as to how much voltage drop you want to tolerate. Voltage drop is a function of wire gauge, round trip wire length and amperage. There are all sorts of tables and calculators to help determine what wire gauge to use. West Marine has one I use, mostly because Iíve had a sailboat for longer than Iíve had the trailer. I generally shoot for 3% drop in the 12V side. Why? No reason. I did more boondocking in the past and I wanted as little loss as practical without going into room temperature superconductors. From the table, assuming a 32 foot round trip (I have a Casita 16í SD) and 10 amps moving to the trailer from the tow, then that puts me right in the green band, or 10 ga.

I have one circuit I have fused for 20 amps that supplies the macerator pump I sometimes use to dump uphill or to speed the dump process. The outlet for that is right behind the fuse panel on the streetside of the trailer. Round trip length of inside and outside wiring is about 12-14 feet. That puts me again in the 10 ga band which is what I used.

Do you need 3% drop? No. Paraphrasing the Gallagher routine, itís about style. Just watch out for the Sledge-O-Matic and the exploding watermelonÖ
'll

The 3% voltage drop rule is a standard from the NEC .The NEC has rules for allowable % voltage drop for both feeders and branch circuits. A # 10 AWG
is sufficient based on voltage drop ,ampacity and mechanical strength. Using a larger gauge wire in many cases does nothing but increase the cost.
__________________
steve dunham is offline   Reply With Quote
Old 04-24-2014, 11:39 AM   #9
Senior Member
 
Steve L.'s Avatar
 
Name: Steve
Trailer: 2003 Casita 16' SD
Michigan
Posts: 1,690
Registry
Quote:
Originally Posted by steve dunham View Post
'll

The 3% voltage drop rule is a standard from the NEC .The NEC has rules for allowable % voltage drop for both feeders and branch circuits. A # 10 AWG
is sufficient based on voltage drop ,ampacity and mechanical strength. Using a larger gauge wire in many cases does nothing but increase the cost.
Cool! I love it when I do the right thing for the wrong reason. Sort of offsets the karma of those doing the wrong thing for no reason...
__________________

__________________
Steve L. is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Frame Ground/Chassis Wire multi-task Electrical | Charging, Systems, Solar and Generators 35 04-28-2013 05:44 PM
Will this work? Ground wire Bobbie Mayer Electrical | Charging, Systems, Solar and Generators 21 09-25-2012 01:23 PM
Wire Gauge For Interior use? francene Problem Solving | Owners Helping Owners 21 08-18-2009 06:09 PM
What gauge wire should I use? Kevin K Electrical | Charging, Systems, Solar and Generators 14 10-15-2007 02:13 PM
What gauge wire should I use? Kevin K General Chat 0 12-31-1969 07:00 PM

» Upcoming Events
No events scheduled in
the next 465 days.
» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 05:25 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.