Quote:
Originally Posted by P. Raz View Post
Wow. I have to say I'm surprised that the testing agencies, especially the ones funded by the insurance companies, allow this. I guess everything has mouse print these days. Raz,
Raz , When I was wiring houses ,we would buy receptacles in quanities of 10,000 at
27 cents each. They work fine in bedrooms and living rooms where the loads were small.
They did not hold up as well in kitchens where high wattage appliances were being used and were repeatedly pluged in and then un plugged. In our area , electric heat is presumed to be a continuous load due to the design temp of -30 deg F. When a cord connected heater runs continuously on high both the cord cap and the receptacle will get warm and over a period of time the receptacle looses its contact tension. For example hospital grade receptacle are tested for contact tension by plugging an 8lb weight into the face of the receptacle , turning the receptacle face down and the weight must stay in place for a stated time period. Hospital grade receptacles cost about $6 to $8 each. The same problem occurs with residential grade switches. If you load the switch above 80% of its rating and the switch is operated frequently ,especially on inductive loads ,the switch will not last very long. The theory that you get what you pay for holds true in electrical devices.
steve dunham is offline   Reply With Quote
Old 11-16-2015, 11:24 AM   #22
Senior Member
 
WaltP's Avatar
 
Name: Walter
Trailer: 2017 Escape 17B
SW Virginia
Posts: 2,254
Steve
Thanks for this great education on electric stuff. More than I knew for sure and very useful.

Walt
WaltP is offline   Reply With Quote
Old 11-16-2015, 12:45 PM   #23
Senior Member
 
Trailer: 2002 19 ft Scamp 19 ft 5th Wheel
Posts: 3,640
Send a message via Yahoo to Darwin Maring
Just replace your receptacle with a 20 Amp receptacle. They don't cost that much. Still use the 15 Amp circuit breaker.
Darwin Maring is offline   Reply With Quote
Old 11-16-2015, 01:08 PM   #24
Senior Member
 
WaltP's Avatar
 
Name: Walter
Trailer: 2017 Escape 17B
SW Virginia
Posts: 2,254
Exactly.
WaltP is offline   Reply With Quote
Old 11-16-2015, 01:31 PM   #25
Senior Member
 
Joe MacDonald's Avatar
 
Trailer: 1981 Trillium 5500
Posts: 1,158
if you dont buy the commercial grade, it still won't last. the t blade designates a 20 amp receptacle , in Ontario, that is what is used for kitchen counters, if close to a sink, then it is also a ground fault receptacle. this replaces the standard 15 amp split plug we used to use. without getting into heavy details, i have used a ceramic heater in my trailer since I got the trailer. my trailer plug only has a 15 amp standard end on it. i do not recall ever tripping a breaker.

Joe
Joe MacDonald is offline   Reply With Quote
Old 11-17-2015, 06:24 AM   #26
Senior Member
 
Trailer: No Trailer Yet
Posts: 721
If anyone cares the commercially supplied AC voltages in the US were originally 110/220 volts and raised in steps to the current 120/240.
(it goes back to Edison and his 100 VDC raised to 110 to make up for transmission loss)

This allows more current, amps, to be delivered over the same transmission lines because when the voltage is raised the amps goes down for the same wattage thus saving lots of $$'s in facilities.
It was done in steps to coincide with lower voltage appliances being replaced with new ones

But old habits are hard to break and many/some still refer to the supplied voltages as "110/220" volts

Joe
Joe Romas is offline   Reply With Quote
Old 11-18-2015, 10:42 AM   #27
Senior Member
 
Name: Steve
Trailer: 2018, 21ft escape— 2019 Ram 1500 Laramie
NW Wisconsin
Posts: 4,500
[QUOTE=Darwin Maring;558846]Just replace your receptacle with a 20 Amp receptacle. They don't cost that much. Still use the 15 Amp circuit breaker.[/)]

Refer to Table 210.21((3 . It is a violation of the NEC to install a 20 amp receptacle on a 15
amp circuit. The code allows both 15 & 20 amp receptacles to be installed on 20 amp branch circuits if the circuit has multiple receptacles. If a 20 amp circuit feeds a single receptacle ,then the receptacle must be rated for 20 amps.
Table 210(((2) states that the maximum load for a cord connected appliance on a 15 amp
receptacle is 12 amps or 1440 watts . A 1500 watt heater exceeds 12 amps
steve dunham is offline   Reply With Quote
Old 11-18-2015, 11:23 AM   #28
Raz
Senior Member
 
Raz's Avatar
 
Trailer: Trillium 2010
Posts: 5,185
Quote:
Originally Posted by steve dunham View Post
Refer to Table 210.21((3 . It is a violation of the NEC to install a 20 amp receptacle on a 15
amp circuit. The code allows both 15 & 20 amp receptacles to be installed on 20 amp branch circuits if the circuit has multiple receptacles. If a 20 amp circuit feeds a single receptacle ,then the receptacle must be rated for 20 amps.
Table 210(((2) states that the maximum load for a cord connected appliance on a 15 amp
receptacle is 12 amps or 1440 watts . A 1500 watt heater exceeds 12 amps
This sounds more like something passed by Congress. Raz
Raz is offline   Reply With Quote
Old 11-18-2015, 12:43 PM   #29
Senior Member
 
Name: Steve
Trailer: 2018, 21ft escape— 2019 Ram 1500 Laramie
NW Wisconsin
Posts: 4,500
Quote:
Originally Posted by P. Raz View Post
This sounds more like something passed by Congress. Raz
The language used in the code is often refered to as "Codeze". The code is used as a legal document and is written as such . The interpretation of the code is under the local authority having legal jurisdiction. This leads to various and stricter interpretations of the code .
Often electrical advice on this forum is contrary to the code and leads to unsafe installations.
Many times electricians will make an installation that exceeds code standards and follow best practice because we know what works . Example: Many shops I worked for did not use the push in terminals on receptacles because it often led to poor connections and call backs.
The code finally recognized the issues with pushin terminations and changed the code and limited their use.
steve dunham is offline   Reply With Quote
Old 11-18-2015, 05:30 PM   #30
Senior Member
 
Trailer: 2002 19 ft Scamp 19 ft 5th Wheel
Posts: 3,640
Send a message via Yahoo to Darwin Maring
Steve, Thanks for the info..
Darwin Maring is offline   Reply With Quote
Old 11-18-2015, 05:33 PM   #31
Senior Member
 
Trailer: 2002 19 ft Scamp 19 ft 5th Wheel
Posts: 3,640
Send a message via Yahoo to Darwin Maring
All my wiring is 12 Gauge or larger and that is also in the house we built ourselves.
Darwin Maring is offline   Reply With Quote
Old 11-19-2015, 11:10 AM   #32
Senior Member
 
floyd's Avatar
 
Trailer: 2004 13 ft Scamp Custom Deluxe
Posts: 8,520
Registry
Those little cube heaters are absolutely ubiquitous among fiberglass trailers. In fact many eschew the furnace or the heat strip in favor of them. So they have certainly been adequately field tested!
floyd is offline   Reply With Quote
Reply

Tags
casita


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Does adding multi-outlet to 12v outlet diminish output? Kudzu Asheville Electrical | Charging, Systems, Solar and Generators 8 05-08-2014 05:05 AM
Source for a 110v exterior outlet FlyboyTJ Modifications, Alterations and Updates 49 10-20-2012 06:38 PM
Ceramic Heater Safety melissab General Chat 24 11-08-2011 09:12 PM
Ceramic heater recommendations? Cam A Care and Feeding of Molded Fiberglass Trailers 16 04-19-2006 03:38 PM

» Upcoming Events
No events scheduled in
the next 465 days.
» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 06:19 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.