Electrical - adding AC wiring to 12 volt system - Fiberglass RV


Reply
 
Thread Tools Search this Thread Display Modes
 
Old 08-10-2013, 11:09 AM   #1
Senior Member
 
Name: Cathy
Trailer: 1973 Love Bug '13
Florida
Posts: 400
Registry
Electrical - adding AC wiring to 12 volt system

We are preparing to install electrical system in Love Bug. Already purchased a PD9245C, 30 amp, converter intending to run strictly 12v in the camper. Have since decided to add some AC power to the camper.

When operating on 12 volts we have minimal led lights and periodic charging of electronics.

1. can we run shore power to breaker panel with a single circuit or must we use 2 circuits dedicating one for the converter, and the other to the 110 auxiliary outlets in camper?

2. If we have 2 breakers, must we ad an outlet to plug the converter into or can we cut off converter plug and wire directly to breaker?


3. If we do wire the shore power inlet for 30 amp (using a 110 adapter when at a house) will we need multiple female plug adapters for different campgrounds or is there a standard 30 amp plug at all campgrounds having 30 amp service. (understanding the difference between 220 and 120 power supply)

Thanks,
Cat
__________________

Cat futrell is offline   Reply With Quote
Old 08-10-2013, 11:16 AM   #2
Senior Member
 
Byron Kinnaman's Avatar
 
Name: Byron
Trailer: 2006 Scamp 13' towed with a 2005 Dodge Dakota 4.7l Magnum W/full tow package (over kill)
Oregon
Posts: 6,308
Registry
1. Two circuits (2 breakers) is always better.
2. It would be easier to replace the converter with a plug on the end.
3. As far as I've been able to determine and observe 30 amp connections are all the same. It might be a good idea to also carry a 50 amp to 30 amp adapter.
__________________

__________________
Byron & Anne enjoying the everyday Saturday thing.
Byron Kinnaman is offline   Reply With Quote
Old 08-10-2013, 11:20 AM   #3
Senior Member
 
Name: Cathy
Trailer: 1973 Love Bug '13
Florida
Posts: 400
Registry
Thanks Byron, good info.
Cat futrell is offline   Reply With Quote
Old 08-10-2013, 11:52 AM   #4
Senior Member
 
Name: None
Trailer: None
None
Posts: 2,730
The load (amperage) of a single appliance (converter ) according to the NEC shall not exceed 50% of the branch circuit rating and also feed additional loads . IE if your converter draws more than 7,5 amps and is on a 15 amp branch circuit you cannot legally have that branch circuit feed other loads . Byron is correct ,put the converter on it's own separate circuit --it is just good practice.. 2) If the converter comes from the factory with a male cord cap attached so you can plug the converter into an outlet , you cannot legally cut off the cord cap and connect it directly to a breaker panel. Cord is not an approved permanent wiring method and by hooking it directly to the breaker panel you are violating the NEC and violating the UL listing of the converter . 3) All receptacles & cord caps are designed and manufactured to UL and NEMA standards so the 30 amp 120 VAC receptacle and cord cap required for your trailer only come in one configuration. You cannot plug your 30 amp cord cap into a receptacle with a different voltage or amperage, it will not fit . That's why they make adaptors and they are designed and manufactured for a vary limited number of applications . Splitting the 120 VAC into multiple circuits is the right way to go and will lessen your chances of nuisance tripping . I would buy a 30 amp 120 volt AC to 15 amp 120 volt AC adaptor
__________________
steve dunham is offline   Reply With Quote
Old 08-10-2013, 12:21 PM   #5
Senior Member
 
Jon Vermilye's Avatar
 
Name: Jon
Trailer: 2017 Escape 21
Oswego, NY
Posts: 1,407
Registry
Somewhat on the same topic - My Escape 17B was ordered with the removable power cord option - I wanted the space in the cord storage area for the installation of an inverter & power conditioner. After a couple of adapter failures, I made this one:

Since I always carry a 30', 20 amp standard extension cord in the RAV4, this works well for 15/20 amp campsites. It also gives me an efficient way to carry a replacement Marinco connector, something that can be hard to find in some areas.
Attached Thumbnails
ASG_6494.jpg  
Jon Vermilye is online now   Reply With Quote
Old 08-10-2013, 12:39 PM   #6
Senior Member
 
Name: Cathy
Trailer: 1973 Love Bug '13
Florida
Posts: 400
Registry
Thanks Jon.

Another question please.. Just realized (duh) that our converter is a 45 amp converter.

1. Does that mean that we must plug into a 50 amp service?

2. Converter draws 475 watts.. Does this convert to 6 + amps which means it must have a 15 amp breaker?

3. Will 50 amp service be adaptable to 110 house outlet?
Cat futrell is offline   Reply With Quote
Old 08-10-2013, 12:47 PM   #7
Senior Member
 
Byron Kinnaman's Avatar
 
Name: Byron
Trailer: 2006 Scamp 13' towed with a 2005 Dodge Dakota 4.7l Magnum W/full tow package (over kill)
Oregon
Posts: 6,308
Registry
Quote:
Originally Posted by Cat futrell View Post
Thanks Jon.

Another question please.. Just realized (duh) that our converter is a 45 amp converter.

1. Does that mean that we must plug into a 50 amp service?

2. Converter draws 475 watts.. Does this convert to 6 + amps which means it must have a 15 amp breaker?

3. Will 50 amp service be adaptable to 110 house outlet?
1. NO
2. This converts to 3.58 Amps at 120Volts and 35.8 Amps at 12 volts. A 15 Amp breaker would be fine.
3. See 1 above. No need to worry about 50 amp service. The size of the service in Amperes is the maximum the service will supply. Your trailer will probably never need the fully 20 Amps provided for in most 13' trailers. As we speak my trailer is plugged into a 20 Amp circuit at my house.
__________________
Byron & Anne enjoying the everyday Saturday thing.
Byron Kinnaman is offline   Reply With Quote
Old 08-10-2013, 12:58 PM   #8
Senior Member
 
Name: Cathy
Trailer: 1973 Love Bug '13
Florida
Posts: 400
Registry
Here is why...

Originally we were planning only off grid camping. No fridge, no heater, no t.v. We have since decided that we want to take the camper to some locations with power supply. Well, if there is a power supply then we can take some small electric conveniences that we would not use off grid.

We are going from scratch and have already run the 12 volt wires, fiberglass over them and installed ensolite. All of the 12 volt wires have been attached to the 12 volt fuse panel. Each 12 volt light/ outlet having its own circuit. We want to add four 110 outlets. Planning to put all four of them all on 1 circuit.

Advice please
Cat futrell is offline   Reply With Quote
Old 08-10-2013, 01:00 PM   #9
Senior Member
 
Joe MacDonald's Avatar
 
Trailer: Trillium
Ontario
Posts: 754
When I re-did my Trillium , this is what I ended up with:
Shore power cord: 1)15 amps, wired with #12 SO cable (120 Volts)
2) 6 circuit breaker panel
3) a separate breaker for converter, outside plug, water heater, fridge, A.C.(not installed yet), inside plugs.

So far, I have never tripped a 15 amp breaker at a campground, I'm not sure what will happen when I add the A.C.
I have a PD 9245 that i purchased from a fellow member of our group.

Over all, NEC not withstanding, not trying to cause any controversy, it is all on 1 -15 amp plug in cable that is factory , just with a better converter.

Joe
__________________
Joe MacDonald is offline   Reply With Quote
Old 08-10-2013, 01:02 PM   #10
Senior Member
 
Jon Vermilye's Avatar
 
Name: Jon
Trailer: 2017 Escape 21
Oswego, NY
Posts: 1,407
Registry
And as to question 3 - There are adapters that will allow a 30 amp trailer male connector to be plugged into a campground 50 amp receptacle. The adapter uses only one leg of the 120/240v 50 amp receptacle, so it provides 120V.

While some are concerned about plugging a 30 amp cord into a 50 amp receptacle, as long as you have a 30 amp main breaker in the trailer there are very few situations where it would cause a problem since the 30 amp trailer main protects the internal trailer wiring.

That said, it is also rare to find a campsite that has only 50 amp receptacles. Most sites that have a 50 amp receptacle will also have a 30 amp & 15 amp in the pedestal. One advantage of carrying a 50 amp to 30 amp adapter is that some 30 amp campground receptacles are very worn & will not make a good, secure connection. Since the 50 amp receptacle is not used as much, it may be better to use the adapter. Also, because the wire size is larger & sometimes newer, the 50 amp receptacle may have less voltage drop when the campground electrical system is strained, letting you use your AC.
Jon Vermilye is online now   Reply With Quote
Old 08-10-2013, 01:23 PM   #11
Senior Member
 
Name: None
Trailer: None
None
Posts: 2,730
Quote:
Originally Posted by Cat futrell View Post
Here is why...

Originally we were planning only off grid camping. No fridge, no heater, no t.v. We have since decided that we want to take the camper to some locations with power supply. Well, if there is a power supply then we can take some small electric conveniences that we would not use off grid.

We are going from scratch and have already run the 12 volt wires, fiberglass over them and installed ensolite. All of the 12 volt wires have been attached to the 12 volt fuse panel. Each 12 volt light/ outlet having its own circuit. We want to add four 110 outlets. Planning to put all four of them all on 1 circuit.

Advice please
The receptacle in the kitchen area and the outside GFCI outlet should each be on their own separate circuit . The largest current draw besides the A/C is in the kitchen IE coffee pot ,toaster , electric fry pan , electric griddle.
I just spent part of a day adding a kitchen receptacle on a separate circuit to our new Casita . It's nice to be able to run the coffee pot at the same time as the toaster. The cost for a few extra feet of wire and a couple of circuit breakers is minor when compared to the time to redo the wiring once the trailer is finished.
__________________
steve dunham is offline   Reply With Quote
Old 08-10-2013, 01:47 PM   #12
Senior Member
 
Name: Randy
Trailer: 1980Trillium 1300
Ontario
Posts: 355
My diy electrical project of Trillium 1300 includes one single wire feeder to connect to shore power AC at park-30feet, rated 30Amp and an extension cable with it when necessary-75feet, rated 50Amps-When comes into the trailer, it first reaches a single adjustable breaker, rated at 30amps. From there it goes into converter after main circuit panel. Within converter housing, it has 2 branches of 110VAC and one input into converter. It is very simple, saving cost and wires with assurance of utilization of power supplies. Before distributing to equipments, light bulbs, pumps...ect...it goes thru: a home-made panel with 4 DC fuses(4 DC branches) and 4 AC fuses(4 AC branches). The designed capability could handle more than it needs, including air conditioner and 110vac heater. All went thru: tests and trials with...more than 5 camping trips without a single blown fuse so far. Inside the Trillium, it has 4 12VDC outlets, 4 110VAC outlets plus one 110VAC exterior. Trust me, this is my own design and experiences after all of my hard works. References thru: my photos...Thanks for reading..
Attached Thumbnails
IMG080.jpg   IMG578.jpg  

IMG580.jpg   IMG581.jpg  

IMG584.jpg   IMG533.jpg  

__________________
Thinh is offline   Reply With Quote
Old 08-10-2013, 01:49 PM   #13
Senior Member
 
Name: Cathy
Trailer: 1973 Love Bug '13
Florida
Posts: 400
Registry
If we have a 30 amp service and Use a 15 amp circuit for the converter, then we only have 15 amps left. Why does it matter if a kitchen outlet pulling 5 amps is on its own circuit? Doesn't it add the same load to the power supply as it would on a shared circuit?
Cat futrell is offline   Reply With Quote
Old 08-10-2013, 02:04 PM   #14
Senior Member
 
Name: Randy
Trailer: 1980Trillium 1300
Ontario
Posts: 355
Quote:
Originally Posted by Cat futrell View Post
If we have a 30 amp service and Use a 15 amp circuit for the converter, then we only have 15 amps left. Why does it matter if a kitchen outlet pulling 5 amps is on its own circuit? Doesn't it add the same load to the power supply as it would on a shared circuit?
...When the supply service could give you 30Amps and you only need 15Amps, you'd better be happy with it. The latter phrase of your quote is actually in need to be straighten out, Buddy. AC circuitry must be separated from DC, 12 volt circuitry. No matter kitchen outlet has it's own fuse or share with others, the designer/owner must have it in his/her mind of choice-For example, I design my 110VAC air conditioner connection with THE SAME OULET of 110VAC for electrical heater because of course, I wouldn't plug both air conditioner and heater in the same outlet/otherwise, using them AT THE SAME TIME, would you?..Just my input...
__________________

__________________
Thinh is offline   Reply With Quote
Reply

Tags
electrical


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
All new electrical system kyle minor Modifications, Alterations and Updates 4 06-04-2010 12:02 PM
12 Volt Electrical System From Scratch Al POGUE Problem Solving | Owners Helping Owners 2 09-17-2007 09:20 PM
Adding 2 - 6 volt Batteries John Blair Electrical | Charging, Systems, Solar and Generators 4 03-09-2007 11:08 PM
Electrical System Barbara Gardin Electrical | Charging, Systems, Solar and Generators 2 04-18-2006 04:37 PM
Help adding a 12 volt system to a scamp 13 UncleJosh Electrical | Charging, Systems, Solar and Generators 10 03-31-2006 09:30 PM

» Upcoming Events
No events scheduled in
the next 465 days.
» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 11:36 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.