Old 08-01-2013, 04:36 PM   #29
Senior Member
 
Name: None
Trailer: None
None
Posts: 2,730
Resetting Breakers

[QUOTE=lamimartin;406836]Hi Paul,
As you suspected, some bad contact or corrosion appear to have created conditions for a resistance that went hot or sparked and burned the fuse panel. Note that battery Inline fuse are often replaced by a auto reset breaker such as this one: so sparks on connecting the battery or very short power surge will not cut the main power.

I for one am not partial to resetting breakers for circuit overcurrent protection .I would install an inline fuse in the incoming DC line at the battery and at the converter . Fuses offer positive, dependable and consistent overcurrent protection ,breakers do not. Breakers are electrical mechanical devices that are affected by age ,corrosion and temperature and have inconsistent trip points. Overcurrent devices protect the equipment as well as the trailer wiring and breakers often allow too much pass thru current to protect equipment . Look at a car radio or a microwave or a TV and they have fuses for overcurrent protection . The advantages of a circuit breaker are the ability to be turned on and off and they are convenient to reset but offer far less protection than a fuse
__________________

__________________
steve dunham is offline   Reply With Quote
Old 08-01-2013, 05:38 PM   #30
Senior Member
 
Name: Steve
Trailer: Scamp 13
California
Posts: 1,418
Quote:
Originally Posted by glennco View Post
Yeah, solid vs stranded wire debate.


1 additional vote for stranded.

An additional question. Does scamp typically use 12awg wire for a power feed? Even fused at 20 amps, 10awg seems like it would be safer, or is that just overkill?
12awg wire is OK for the 20 amps that Scamp origonally installed but that was with limited power useage. By someone changing to a power distribution pannel you are changing the design peramaters. so the incomming line must be upgraded to the power capabilities of the pannel. I doubt that #12 @ 20 amps is up to snuff. Your figures will vary but for example about 5 amps for the fridge, 5 amps for the fan, 5 amps for the water pump. Examples but not limited to 5 amps for each lighting circut and 15 amps for each lighter style socket all this power can be concivably turned on at the same time even if its intermitant it all counts, that 20 amp fuse is gonna blow. It is far safer to upgrade the incoming wire to pannel rating including run wire length. Then fuze limit the incomming line to a load your comfortable with. Go to Walmart in the sterio section or any sterio supplier they have some nice large blade fuze holders with covers if you want to upsize your incomming power line.
My old Scamp had very limited power supplied by Scamp but when I wanted to add more convience items an upgrade had to be done. Right now your system is very suspect and should be wrought out and please follow the proper color codes and wire markings so anyone trouble shooting knows what was actually done.
__________________

__________________
stevebaz is offline   Reply With Quote
Old 08-01-2013, 06:54 PM   #31
Senior Member
 
Jared J's Avatar
 
Name: Jared
Trailer: 1984 19' scamp
Kansas
Posts: 1,610
Quote:
Originally Posted by glennco View Post
Yeah, solid vs stranded wire debate.

1 additional vote for stranded.

An additional question. Does scamp typically use 12awg wire for a power feed? Even fused at 20 amps, 10awg seems like it would be safer, or is that just overkill?
When I pulled my old converter out of the scamp, it was 12 gauge…with. 30 amp bullet fuse!!! The converter was rated for 15! That made me curious, so I hooked it back up and put a 15 amp in it. Smoked it. 20 amp…smoked it, 25 amp…smoked it after a minute or two. With the 30, I could barely touch the wire!!

I have no idea why it was that way, if scamp did that, or the p.o. did. That thing was a hair away from bursting into flames. I was ripping out the wiring anyway, so I quit investigating at that point.

I have 4 gauge on a 50 amp marine breaker now.

The other issue I have is with them branching circuits off of circuits. Well, if both require a 10 amp fuse, now you need a 20 amp. What if one of those is off, and the other starts pulling 18 amps?

Originally, all 12v was one circuit. Now it's:

fridge
furnace
water pump
lights
12v power receptacles

The 120v had the ac on one circuit, and the water heater and everything else on the other.

Now it's
Outside/couch/bunk outlets
Rh kitchen outlets/electric fireplace
Fridge/fluorescent light/Lh kitchen outlets
Ac
12v dc converter
Water heater

I prefer to keep everything separate with the lowest fuse/breaker rating needed. Otherwise, you might need one of these:

__________________
Jared J is offline   Reply With Quote
Old 08-01-2013, 08:21 PM   #32
Senior Member
 
Roy in TO's Avatar
 
Name: Roy
Trailer: 1972 boler American and 1979 Trillium 4500
Ontario
Posts: 4,954
I'll have to order some of those 530433's. Where did you source it?
__________________
Roy in TO is offline   Reply With Quote
Old 08-01-2013, 10:18 PM   #33
Senior Member
 
Jared J's Avatar
 
Name: Jared
Trailer: 1984 19' scamp
Kansas
Posts: 1,610
I wish I knew. You'll have to break into the garage of somebody with a british car. Lucas the inventor of the intermittent wipers…and headlights…and gauges…
__________________
Jared J is offline   Reply With Quote
Old 08-08-2013, 04:36 PM   #34
Member
 
Name: JD
Trailer: Fiber Stream
Maryland
Posts: 32
Registry
Sae j1292

This is a great discussion and very helpful in understanding concerns with trailer wiring in general.

You might be interested in the national standard that covers this type of wiring. SAE (Society of Automotive Engineers) J1292

SAE J1292: Automobile, Truck, Truck-Tractor, Trailer, and Motor Coach Wiring

Nothing in it will surprise any of us, but it's nice to see there are standards.

Dave in Baltimore
__________________
JD1994 is offline   Reply With Quote
Old 08-08-2013, 05:19 PM   #35
Senior Member
 
Name: Randy
Trailer: 1980Trillium 1300
Ontario
Posts: 355
...This is my thought thru: experiences... The over-kill wire(bigger size) will not hurt your electrical circuitry but it will add more weights and costs. THE OVER-KILLED FUSE RATINGS WILL COST YOU A WHOLE TRAILER ELECTRICAL CIRCUITRY. Pls do not forget that. That's why hydro suppliers use high voltage; 6000VAC, 230KVAV to deliver hydro to your home for long distance. They want to save cost with smaller size of their wires....Hopefully it helps...
__________________
Thinh is offline   Reply With Quote
Old 08-08-2013, 08:23 PM   #36
Senior Member
 
Brian B-P's Avatar
 
Name: Brian
Trailer: Boler (B1700RGH) 1979
Alberta
Posts: 5,000
Quote:
Originally Posted by JD1994 View Post
You might be interested in the national standard that covers this type of wiring. SAE (Society of Automotive Engineers) J1292

SAE J1292: Automobile, Truck, Truck-Tractor, Trailer, and Motor Coach Wiring

Nothing in it will surprise any of us, but it's nice to see there are standards.
I agree, it is good to have standards.

I note, though, that the common 7-pin flat-blade "RV" style electrical connection typically does not follow J1292 colour coding. Common 4-pin flat and 7-pin round-pin commercial truck trailer connectors (which are unsuited to electric brake and battery charging functions and rarely used on RVs) do follow this standard.
__________________
1979 Boler B1700RGH, pulled by 2004 Toyota Sienna LE 2WD
Information is good. Lack of information is not so good, but misinformation is much worse. Check facts, and apply common sense liberally.
STATUS: No longer active in forum.
Brian B-P is offline   Reply With Quote
Old 08-08-2013, 09:23 PM   #37
Senior Member
 
Name: Paul
Trailer: '07 Scamp 16' SD
Wisconsin
Posts: 110
I figured I'd give everyone a status. I ordered a PD5000 panel and a charge wizard to attach to my PD9130.

Tomorrow I took the day off to work on the install this setup. The design of this PD panel is by far a better designed unit the. The 'American' unit that was in the scamp.

I intend to run new power and ground wires in a larger gauge as well. The previous setup had the power from the tug intersect with the battery + all the way back at the fuse panel. That is a poor design, and I will be moving it back up to the front as the camper would have been when it came from the factory. It will be isolated between two in-line fuses in the same style as per the factory. This effectively isolates the camper from the tug in case of any surges from the tug.

After it's all together, start testing individual devices to see if I can find something drawing too much current.


Any other things anyone can think of?
__________________
glennco is offline   Reply With Quote
Old 08-20-2013, 10:48 PM   #38
Senior Member
 
Name: Paul
Trailer: '07 Scamp 16' SD
Wisconsin
Posts: 110
Wanted to give folks an update here. I tried to run some 8awg wire wire but was unable to fish the wire around the front bath. So, I added the proper fuses separating the battery and camper from the power coming in from the tug. If anyone has ever tried to run new power wire in a scamp with a front bath, I'd be interested in knowing how it was done.

After adding the fuses I found that I blew the fuse between the battery and the tug power on our last trip. This made me start looking more deeply to an issue with the wiring in the tug. I found it, the power wire had gotten too close to the muffler and melted. It as creating an intermittent short to ground when driving. My relay protected the power system of the tug, but the poor wiring from the PO caused the failure of the fuse panel.

Hopefully I won't have another failure on the tug, but am reassured that I've added the necessary segregation to the power system in the scamp to prevent another catastrophic failure if a similar situation arises again

I'd very much appreciate any thoughts folks would have on running new power wire in the scamp. The current 12awg wire scamp runs seems like a weak point in the system d like to eliminate.

Thanks,

Paul
__________________
glennco is offline   Reply With Quote
Old 08-20-2013, 11:58 PM   #39
Senior Member
 
Jared J's Avatar
 
Name: Jared
Trailer: 1984 19' scamp
Kansas
Posts: 1,610
I ran 4 gauge, but I went under the trailer with it.
__________________
Jared J is offline   Reply With Quote
Old 08-21-2013, 10:20 PM   #40
Senior Member
 
Name: Paul
Trailer: '07 Scamp 16' SD
Wisconsin
Posts: 110
I did consider running the wire under the camper, but I go concerned about punching new holes through the floor
__________________
glennco is offline   Reply With Quote
Old 08-22-2013, 07:51 AM   #41
Senior Member
 
Thomas G.'s Avatar
 
Name: Kinga DeRode
Trailer: For Sale Or Rent
Rooms to Let 50 Cents
Posts: 5,103
Quote:
Originally Posted by glennco View Post
I did consider running the wire under the camper, but I go concerned about punching new holes through the floor
As I've posted before, when I put a hole in the floor I drill an oversized hole, tape the bottom, fill with FG resin, then drill a centered, smaller hole once the resin has cured. That way the hole is completely sealed to water. I use butyl caulk on the bottom around the wire to finish it off.
__________________
UHaul and Burro owners, join the UHaul Campers on Facebook. https://www.facebook.com/groups/529276933859491/
Thomas G. is offline   Reply With Quote
Old 08-22-2013, 08:32 AM   #42
Senior Member
 
Ice-breaker's Avatar
 
Name: Dave W
Trailer: Escape 19 and Escape 15B
Alberta
Posts: 470
Quote:
Originally Posted by Thomas G. View Post
As I've posted before, when I put a hole in the floor I drill an oversized hole, tape the bottom, fill with FG resin, then drill a centered, smaller hole once the resin has cured. That way the hole is completely sealed to water. I use butyl caulk on the bottom around the wire to finish it off.
I have had some success making water tight wire connections using a cable gland such as this (Electrical Installation Accessories). Could even use Thomas' FG resin filled hole with one of these installed in the centre.

__________________

__________________
Dave W - 2013 Escape 19', 2013 Escape 15B and 2011 Toyota FJ Cruiser

"You've got to be very careful if you don't know where you are going, because you might not get there." - Yogi Berra
Ice-breaker is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bank of America honda03842 General Chat 11 04-14-2012 09:37 PM
Need some help, please Canadian Bank Cards at US Gas Sations Doug Mager Problem Solving | Owners Helping Owners 1 02-08-2011 12:06 AM
Battery Charging: what limits the amperage to the house bank? Evergreen Modifications, Alterations and Updates 3 01-19-2011 11:47 AM
Trailer Piggy Bank Andrew Gibbens General Chat 3 07-10-2006 04:30 PM
A link to a data bank of egg pictures. Yves Pelchat Forum Admin, News & Announcements 2 01-31-2006 04:23 PM

» Upcoming Events
No events scheduled in
the next 465 days.
» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 09:42 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.