Old 01-13-2015, 11:42 PM   #1
Member
 
Name: Captain Longbelly
Trailer: Lots
Kentucky
Posts: 56
Grounding 120v to the frame...

Hello I am currently upgrading an old Hunter Compact II and have a question about the 120v...I am replacing the original 15 amp breaker box with a new 30 amp...I am using a 30 amp shore power cord and locking inlet...




The original breaker box had a ground wire ran from the ground bar to a frame/body bolt(the large aluminum wire)



I was wondering if I need to reinstall it from the ground bar to the frame again with new breaker box?



Thanks for any information you may share
KyMoonshine is offline   Reply With Quote
Old 01-14-2015, 01:20 AM   #2
Senior Member
 
Borrego Dave's Avatar
 
Name: Dave
Trailer: Casita SD17 2006 "Missing Link"
California
Posts: 3,738
I would certainly ground it to the frame as it was but with copper wire.
Borrego Dave is offline   Reply With Quote
Old 01-14-2015, 06:19 AM   #3
Senior Member
 
John Linck's Avatar
 
Trailer: 1990 Scamp 16 ft
Posts: 654
Given the varieties of electrical standards in campgrounds I wonder if the principle of "double insulation" used in power tools might be a better way. Thoughts?

John
John Linck is offline   Reply With Quote
Old 01-14-2015, 09:02 AM   #4
Moderator
 
Jim Bennett's Avatar
 
Trailer: 2009 19 ft Escape / 2009 Honda Pilot
Posts: 6,228
Registry
I have the same thing on the Trillium I am rebuilding. I question the logic of grounding the frame to the ground from the service. This would be akin to grounding any metal framing in a building, and is not done. Though there is little harm in doing it, I just don't see the need for it.

12V DC is a different thing, where you are really not grounding, but using the frame as a negative bus in many situations. Might there be a conflict 12V negative, and the 120V ground, are both bonded to the frame?

As well, if all the 12V circuits use wires for both the positive and negative, I can't see any reason that the negative to be bonded either. Am I missing something?
__________________
2017 Escape 5.0 TA
2015 Ford F150 Lariat 3.5L EcoBoost
2009 Escape 19 (previous)
“Most folks are about as happy as they make up their minds to be.” — Abraham Lincoln
Jim Bennett is offline   Reply With Quote
Old 01-14-2015, 09:09 AM   #5
Senior Member
 
Timber Wolf's Avatar
 
Name: Tim
Trailer: '88 Scamp 16, layout 4
North Florida
Posts: 1,547
Quote:
Originally Posted by Jim Bennett View Post
I question the logic of grounding the frame to the ground from the service. This would be akin to grounding any metal framing in a building, and is not done. Though there is little harm in doing it, I just don't see the need for it. Am I missing something?
Every metal building and metal stud framing job I was ever on was grounded. The building was grounded to the grounding electrode and the metal studs where grounded by the metal electrical boxes screwed to them (the box itself was grounded with a bonding jumper).

On the trailer, I would hook it up like it was, but with better, newer, stronger stuff. We have at least a couple of folks on the board who have self-identified themselves as Electrical Engineers and hopefully they will chime in.
Timber Wolf is offline   Reply With Quote
Old 01-14-2015, 09:57 AM   #6
Senior Member
 
Name: Steve
Trailer: 2018, 21ft escape— 2019 Ram 1500 Laramie
NW Wisconsin
Posts: 4,500
Quote:
Originally Posted by Jim Bennett View Post
I have the same thing on the Trillium I am rebuilding. I question the logic of grounding the frame to the ground from the service. This would be akin to grounding any metal framing in a building, and is not done. Though there is little harm in doing it, I just don't see the need for it.

12V DC is a different thing, where you are really not grounding, but using the frame as a negative bus in many situations. Might there be a conflict 12V negative, and the 120V ground, are both bonded to the frame?

As well, if all the 12V circuits use wires for both the positive and negative, I can't see any reason that the negative to be bonded either. Am I missing something?
The frame / structure of metal frame bldgs are required by the NEC to be part of the electrical grounding system . Agricultural bldgs which house livestock have higher grounding requirements than bldgs housing humans . The electrical advice on this forum is often in contradiction to the code. Refer to Art 250 of the NEC -Grounding, .Refer to Art 100 - The code is not a design standard ,intended to be a manual for the untrained , or best practice The purpose of the code is to insure that an installation is basically safe and is the bare minimum,
steve dunham is offline   Reply With Quote
Old 01-14-2015, 10:25 AM   #7
Senior Member
 
honda03842's Avatar
 
Name: Norm and Ginny
Trailer: Scamp 16
Florida
Posts: 7,517
Definitely ground the frame. Just imagine what would happen if the frame ever became electrically 'hot'.
__________________
Norm and Ginny

2014 Honda Odyssey
1991 Scamp 16
honda03842 is offline   Reply With Quote
Old 01-14-2015, 10:40 AM   #8
Senior Member
 
Jon Vermilye's Avatar
 
Trailer: Escape 17 ft Plan B
Posts: 2,388
Registry
The NEC requires that the frame of a RV is connected to ground. If you never connected to a utility supplied power source, (i.e. only used an ungrounded generator) it would be safe to go without a grounded frame, but the problem is the utilities ground their systems to the earth. If you have a fault in the trailer that connects any appliance to the trailer frame (converter, AC, water heater (even through the water in it)), or a wiring failure, the ground connect will carry the fault current. If it is large enough, it will trip the supplying breaker. If it is a low current fault, most of the current will be carried by the ground connection, lowering the shock hazard to the earth.

If you didn't connect the frame to ground, a fault to it would raise it to the fault's voltage level. Since the earth IS ground (because of the utilities using it), touching the frame while standing on the ground presents a shock hazard. Since it only takes a 1/10th of an amp to kill you, even small fault currents are dangerous.
Jon Vermilye is offline   Reply With Quote
Old 01-14-2015, 12:08 PM   #9
Senior Member
 
Name: JD
Trailer: Scamp 16 Modified (BIGLY)
Florida
Posts: 2,448
Another reason to ground to the frame is if a short from hot to the frame were to occur the current to the frame to ground (connected to neutral at the incoming boa and at the transformer) would draw enough current to trip the breaker and clear the voltage from the frame. A poor ground might not draw enough current to trip the breaker leaving enough voltage on the metal frame to be dangerous.
Follow the manufacturer's wiring diagrams if available.
GFCI (ground fault circuit interrupters) can be irritating when they might trip for no discernible reason sometimes, but add safety margins for the operator (you).
redbarron55 is offline   Reply With Quote
Old 01-14-2015, 12:27 PM   #10
Senior Member
 
Name: Steve
Trailer: 2018, 21ft escape— 2019 Ram 1500 Laramie
NW Wisconsin
Posts: 4,500
There are limited applications allowed by the NEC for high impedance grounds .Your trailer is not one of those applications . The trailer frame is supposed to be intentionally and effectively grounded ( See the NEC for definitions of the terms intentionally and effectively)
Establishing a ground point on a trailer frame is often done using a lug and a sheet metal screw neither of which is approved or best practice ..Standard ALCU lugs do not hold up well to road chemicals and the threads on sheet metal screws are too coarse to bond properly to the frame . A copper lug attached to the frame with a fine thread machine screw / tapped hole is a better method .A 10x32 screw is the standard grounding screw for grounding boxes and enclosures.
steve dunham is offline   Reply With Quote
Old 01-14-2015, 06:47 PM   #11
Senior Member
 
Trailer: 2002 19 ft Scamp 19 ft 5th Wheel
Posts: 3,640
Send a message via Yahoo to Darwin Maring
Look at harbor freight for:
Electrical Receptacle Tester with GFCI Diagnosis

Always co ect according to the code. A ground connection to the frame provides a level of safety.

And always use one of these when you connect to any receptacle. First: Test the camp ground power B 4 you connect then after you connect, go inside the camper and check again. Should you not have a ground connection correct, this little device will tell you.
Darwin Maring is offline   Reply With Quote
Old 01-15-2015, 02:28 AM   #12
Member
 
Name: Captain Longbelly
Trailer: Lots
Kentucky
Posts: 56
Thanks everyone for the information...I will ground it back to the frame using one of the bolts that hold the floor to the frame...I also will install CFI outlets first in both runs of outlets...
KyMoonshine is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Solar Panel Set up Question - Grounding the panel? Anne H Electrical | Charging, Systems, Solar and Generators 2 09-07-2012 04:48 PM
Grounding Tail Lights with no White Wire Tim Bas Problem Solving | Owners Helping Owners 2 08-11-2010 03:27 AM
SOLD---120v/12v/propane Refrig/freezer Phillip Classified Archives 2 06-03-2009 01:40 PM
Frigerator 120V Not Working Patrick M. Problem Solving | Owners Helping Owners 8 07-28-2006 10:11 AM
13 Scamp 120V, 12V, Propane Switches LeBoutillier Problem Solving | Owners Helping Owners 8 03-18-2006 05:39 PM

» Upcoming Events
No events scheduled in
the next 465 days.
» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:18 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.