Grounding Generator

Do you ground your generator when camping?
__________________

Huck is offline   Reply With Quote
Old 12-07-2018, 07:42 AM   #2
Senior Member
 
Steve L.'s Avatar
 
Name: Steve
Trailer: 2003 Casita 16' SD
Michigan
Posts: 1,778
Registry
Quote:
Originally Posted by Huck View Post
Do you ground your generator when camping?
No.

I do put it ON the ground, however.
__________________

__________________
Quando omni flunkus, moritati.
Also,
I'm a man, but I can change, if I have to, I guess.
Steve L. is offline   Reply With Quote
Old 12-07-2018, 08:58 AM   #3
Senior Member
 
Name: Steve
Trailer: Casita 17 ft DLX SD
NW Wisconsin
Posts: 3,322
If you wish to assure that your generator is properly grounded , you could drive 4- 12 ft ground rods around the generator perimeter approx 12 ft apart . With a #6 continuos solid copper conductor bond the ground rods together and connect the #6 to the ground lug on the generator frame .

Most people follow follow Steve L and set it on the ground
steve dunham is online now   Reply With Quote
Old 12-07-2018, 10:17 AM   #4
Senior Member
 
Bruce H's Avatar
 
Name: Bruce
Trailer: Bigfoot 25 ft RQ
Missouri
Posts: 540
Has anyone here ever experienced a shock from an un-grounded generator? Or do you know anyone who has?



Those questions being asked, It is certainly prudent to avoid running a wet generator. Or running one in the rain, grounded or not.
Bruce H is offline   Reply With Quote
Old 12-07-2018, 10:27 AM   #5
Senior Member
 
Name: Steve
Trailer: Casita 17 ft DLX SD
NW Wisconsin
Posts: 3,322
A generator is a separately derived system .
The neutral is not intentionally or effectively grounded
There is basically no potential to ground or it can be described as a floating system
Running a portable generator with it just sitting on the ground poses no real hazard
The only time I was ever required to ground portable generators was at fairs where they were used to run amusement rides / equipment.
steve dunham is online now   Reply With Quote
Old 12-07-2018, 10:36 AM   #6
Senior Member
 
Name: Huck
Trailer: ParkLiner
Virginia
Posts: 660
The reason I asked is harbor freight has their 2000 watt generator on sale for $449 through Sunday (12/9), and I am considering getting one. This is copied from the manual. I have never seen anyone ground their generator, so was interested in seeing if anyone here did.

Grounding

1.The Generator must be properly grounded in accordance with all relevant electrical codes and standards before operation. Have the unit grounded by a qualified electrician if you are not qualified to do so.
2.To ground the Generator, connect a #6 AWG grounding wire (not included) from the Grounding Terminal on the Control Panel to a grounding rod (not included). The grounding rod must be an
earth-driven copper or brass rod (electrode) which can adequately ground the Generator.
3.Refer to local regulations for ground source information
Huck is offline   Reply With Quote
Old 12-07-2018, 11:02 AM   #7
Senior Member
 
Name: Steve
Trailer: Casita 17 ft DLX SD
NW Wisconsin
Posts: 3,322
Check NEC Art # 445 ( Generators) and Art #250 ( Grounding)
Normally portable generators used to feed cord connected equipment can be frame grounded . Grounding a generator can introduce hazards if not done properly .
steve dunham is online now   Reply With Quote
Old 12-07-2018, 11:26 AM   #8
Senior Member
 
Raspy's Avatar
 
Name: John
Trailer: 2015 Oliver 23, Ram Cummins
Northern Nevada
Posts: 1,017
Steve,

That Harbor Freight warning seems like CYA, but having never grounded a generator, and always being suspicious of anything electrical from Harbor Freight, I'm curious.

When you did ground one for use with an amusement ride, did you ground the ride itself, or the generator as previously described with a conductor between the generator and a ground rod? I seems like a hot wire shorted to the frame could lead to a shock on the ride, or a trailer, that would not be protected by a generator ground if there is no bond between the frame and the neutral, or the amusement ride frame and the generator frame.
__________________
I only exaggerate enough to compensate for being taken with a grain of salt.
Raspy is offline   Reply With Quote
Old 12-07-2018, 11:32 AM   #9
Senior Member
 
Steve L.'s Avatar
 
Name: Steve
Trailer: 2003 Casita 16' SD
Michigan
Posts: 1,778
Registry
If I were asked about grounding a generator tied into my house I would probably give a different answer but I'm not going around pounding 4-6' copper rods in my camp sites. I've read what Steve refers (post 7)to but I've never checked deeply enough to understand the cautions.
__________________
Quando omni flunkus, moritati.
Also,
I'm a man, but I can change, if I have to, I guess.
Steve L. is offline   Reply With Quote
Old 12-07-2018, 11:48 AM   #10
Senior Member
 
Name: Steve
Trailer: Casita 17 ft DLX SD
NW Wisconsin
Posts: 3,322
I purchased a Champion dual fuel generator this week for our hunting cabin
Printed on the face plate of the generator is “ Neutral is floating” or IE ; Not grounded .
If you take a meter and read from the line output to ground you would read 0 VAC.
steve dunham is online now   Reply With Quote
Old 12-07-2018, 11:54 AM   #11
Senior Member
 
Name: Steve
Trailer: Casita 17 ft DLX SD
NW Wisconsin
Posts: 3,322
Quote:
Originally Posted by Raspy View Post
Steve,

That Harbor Freight warning seems like CYA, but having never grounded a generator, and always being suspicious of anything electrical from Harbor Freight, I'm curious.

When you did ground one for use with an amusement ride, did you ground the ride itself, or the generator as previously described with a conductor between the generator and a ground rod? I seems like a hot wire shorted to the frame could lead to a shock on the ride, or a trailer, that would not be protected by a generator ground if there is no bond between the frame and the neutral, or the amusement ride frame and the generator frame.
We grounded the generator , associated equipment and the ride .
We usually drove two ground rods 8 ft apart and bonded all exposed metal / conductive parts .
There was no half way with grounding , you were required to comply with all relevant code articles. Since these rides were open to the public ( read children )
the State of Minnesota ( Inspectors )were extremely cautious .
Many of these rides came out of the Southern USA where the codes were often not strictly enforced so there was often some heated arguments between the ride owners and the local inspection authorities.
steve dunham is online now   Reply With Quote
Old 12-07-2018, 01:01 PM   #12
Senior Member
 
CarlD's Avatar
 
Name: Carl
Trailer: waiting for LiL Hauley
New York
Posts: 133
Steve is on the right track here. If the generator is grounded and you happen to be grounded and accidentally touch the hot wire you will get a shock. If it is not grounded you may still get a shock however it will be a small shock from capacitive coupling. The down side is if you touch the neutral wire or the floating ground you may also get a small shock. The amount of shock is dependent on many factors such as the total mass of the electrical system and moisture. Since most people know not to touch the hot wire and all metal enclosures of electrical equipment are supposed to be grounded it is better to have a grounded generator especially if it is wet out. In reality if it you are in a dry environment a shock from capacitive coupling is relatively small, most of the time undetectable and grounding the generator is not going to significantly reduce a shock hazard.


As a side note: Those handy little pocket testers used to check for voltage use capacitive coupling.
__________________
Every day is a Saturday
CarlD is offline   Reply With Quote
Old 12-07-2018, 03:02 PM   #13
Senior Member
 
Name: Greg
Trailer: 2008 Casita 17 SD
Washington
Posts: 1,266
Registry
Along a similar line to the "grounding" issue relative to small generators, is that certain EMS, (Electrical Management Systems,) which many people incorrectly call "surge protectors," have a problem of not allowing power from some small generators to enter the trailer due to it having sensed a lack of a ground. Some larger generators, which don't have "floating grounds," can run the trailer effectively through the EMS, but many small generators do have floating grounds, and thus, won't work unless you trick it into believing that a ground exists. One easy work-around is to buy a simple 120 VAC male plug, and install a short jumper between the White (larger blade) silver terminal screw and the green Ground screw. DO NOT HOOK EITHER END OF THE WIRE TO THE GOLD "HOT LEG" SCREW (SMALLER BLADE.) Just plug this into one of the unused outlets on the generator and it will fool the EMS into allowing the power to come in. Understand, this is not a ground, it is just a device to fool the EMS unit by making the generator appear to be grounded.
Attached Images
  
Casita Greg is offline   Reply With Quote
Old 12-07-2018, 03:15 PM   #14
Senior Member
 
Name: Greg
Trailer: 2008 Casita 17 SD
Washington
Posts: 1,266
Registry
This is a little description of the N-G bond plug that I wrote some time back which I posted on some forums:

Portable Inverter Generators and Neutral-Ground Jumper for RV Use
While we're on the subject of portable generators, all RV electrical systems are wired with their Ground and Neutral buses floated, (un-bonded from each other.) There’s lots of good reasons for this, most specifically it’s an NEC and RVIA code requirement that the safety ground wire never carries any load current, and there can be only one Ground-To-Neutral bonding point in any distributed electrical system in the USA. Now, when you’re plugging your RV into power from a building, such as your garage outlet or a campground pedestal outlet, your RV has its Ground and Neutral buses “bonded” (connected) together externally as part of the service panel’s earthed safety ground system. Again, lots of reasons for this, but the fact is you can only have a single G-N bonding point according to the National Electrical Code and RVIA building codes.

So when your RV is powered by a portable generator, and if you have an inline voltage monitor system from a manufacturer such as TRC or Progressive Industries, (like the EMS-30 that I installed in my trailer,) your voltage monitor is checking for the Neutral and Ground voltages to be very close to each other, probably within 3 volts or so. This works well if you’re plugged into shore power that’s properly grounded and bonded, but this voltage protector can be tripped off by plugging your RV shore power plug into a portable generator without an internal Ground-Neutral bond. If you don’t have a voltage protection device on your RV, then you may never know that your generator has a floated neutral (un-bonded G-N bus).

Contractor-type generators, such as a Coleman 5000 for example, are generally G-N bonded internally, which is why it runs your RV just fine. However, many portable inverter generators from companies such as Yamaha and Honda (such as a Honda 2000i or EU3000 for example) have floated Neutrals (i.e. no internal Ground-Neutral Bond) since they expect an external G-N bond to happen somewhere else. And while RV-approved generators may have an internal G-N bond, it seems that many of the most popular portable inverter generators from Honda and Yamaha have floating neutrals. So your 2000i or your EU3000 isn’t providing the Ground-Neutral Bond that your RV requires to think it’s getting properly grounded power, while a Coleman 5000 has a Ground-Neutral bond already so it operates your RV properly. Seems crazy, but that appears to be the scenario.

It’s pretty simple to wire a special “Ground-Neutral Bond” jumper cable for your Honda or Yamaha generator which will allow you to power your RV through its voltage protection device. You can obtain or make a dummy 15 or 20 amp “Edison” plug with the Neutral (white) and Ground (green) screws jumpered together with a piece of 12 or 14 gauge wire. This G-N jumper plug can be plugged into one of the generator’s unused 20-amp outlets, and the entire generator’s electrical system will be N-G bonded. You can then use the other 20-amp Edison outlet or the 30-amp outlet to power the RV.

Just be sure to mark this plug specifically for its intended purpose. It won’t really hurt anything if it’s plugged into a correctly wired home outlet, but it will create a secondary G-N bonding point that could induce ground loop currents and create hum or buzz in a sound system.

So this is a generator-only G-N bonding plug which should be only plugged into a portable generator while powering your RV.

What's going on inside the plug? Jumper wire between the silver screw terminal and the ground screw terminal. Be careful not to hook to the gold terminal screw. (Which is the "hot" prong and can be easily determined by looking at the two power prongs. The "hot" prong (usually the black wire,) will be the smaller of the two blades on the plug and is the power supply. Do not connect to this one.
__________________

Casita Greg is offline   Reply With Quote
Reply

Tags
generator


Currently Active Users Viewing This Thread: 2 (1 members and 1 guests)
Bill K
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Generator Grounding Rod D Electrical | Charging, Systems, Solar and Generators 12 06-02-2018 04:06 PM
Grounding a Scamp Thee Jimbo Problem Solving | Owners Helping Owners 9 08-28-2015 07:39 PM
Grounding 120v to the frame... KyMoonshine Electrical | Charging, Systems, Solar and Generators 11 01-15-2015 02:28 AM
Solar Panel Set up Question - Grounding the panel? Anne H Electrical | Charging, Systems, Solar and Generators 2 09-07-2012 04:48 PM
Grounding Tail Lights with no White Wire Tim Bas Problem Solving | Owners Helping Owners 2 08-11-2010 03:27 AM

» Upcoming Events
No events scheduled in
the next 465 days.
» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 11:11 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2018, vBulletin Solutions Inc.