Romex in RV

Do you use Romex cable for 120v in your RV?
I read on a marine web site the Romex cable is inappropriate in a boat because vibration. It is forbidden. What do you think about that ?
The vibration may broke the cable and cause fire.
__________________

Sebas is offline   Reply With Quote
Old 03-17-2019, 08:32 PM   #2
Senior Member
 
Byron Kinnaman's Avatar
 
Name: Byron
Trailer: 2006 Scamp 13' towed with a 2005 Dodge Dakota 4.7l Magnum W/full tow package (over kill)
Oregon
Posts: 6,833
Registry
Quote:
Originally Posted by Sebas View Post
Do you use Romex cable for 120v in your RV?
I read on a marine web site the Romex cable is inappropriate in a boat because vibration. It is forbidden. What do you think about that ?
The vibration may broke the cable and cause fire.
I don't think I would want to put Romex in my trailer. I believe Romex is solid copper wire. A stranded wire will work better in the trailer/vehicle environment. The other consideration is the insulation. Automotive wire has a non-fire sustaining insulation. It should be listed as either GXL or SXL. If the wire is going to be moving and against something that might cause abrasion you would want SXL which and thicker insulation.
__________________

__________________
Byron & Anne enjoying the everyday Saturday thing.
Byron Kinnaman is offline   Reply With Quote
Old 03-17-2019, 08:35 PM   #3
Senior Member
 
Name: Steve
Trailer: Casita 17 ft DLX SD & 21 ft SOB
NW Wisconsin
Posts: 3,485
The 120 VAC wiring in Scamps ,Casitas , Escapes , Forest River and most other trailers is done in type NM cable
( Romex) Wiring of RVs & travel trailer is covered in the NEC Art # 551 and type NM cable is legal ( Extension cord is not )
A boat is not a travel trailer nor is an automobile
steve dunham is offline   Reply With Quote
Old 03-17-2019, 08:46 PM   #4
Senior Member
 
Name: Jack L
Trailer: Bigfoot B-17 CB
Washington
Posts: 1,379
The cable used in boats consists of stranded conductors and anon metallic jacket that is much tougher than Romex. Romex has a paper filler but marine cable does not have any paper filler. Marine cable is LOTS more expensive.
Jack L is online now   Reply With Quote
Old 03-17-2019, 09:23 PM   #5
Senior Member
 
Raspy's Avatar
 
Name: John
Trailer: 2015 Oliver 23, Ram Cummins
Smith Valley, Nevada
Posts: 1,283
The marine type "Romex", as described by Jack, also has tinned wire. So it is very corrosion resistant. I would not hesitate to use it in my trailer, and have used it to wire utility trailers and a solar systems on my other travel trailer. Excellent stuff.

Standard household Romex is not a good idea since it is single strand and more likely to break with vibration, among it's other weaknesses.
__________________
I only exaggerate enough to compensate for being taken with a grain of salt.
Raspy is offline   Reply With Quote
Old 03-17-2019, 09:53 PM   #6
Senior Member
 
Name: Steve
Trailer: Casita 17 ft DLX SD & 21 ft SOB
NW Wisconsin
Posts: 3,485
Quote:
Originally Posted by steve dunham View Post
The 120 VAC wiring in Scamps ,Casitas , Escapes , Forest River and most other trailers is done in type NM cable
( Romex) Wiring of RVs & travel trailer is covered in the NEC Art # 551 and type NM cable is legal ( Extension cord is not )
A boat is not a travel trailer nor is an automobile
The NEC lists approved wiring methods for travel trailers in NEC 551-47 A
NEC 551-47A says the wiring method listed in Art #334 is an approved wiring method for travel trailers . Art #334 covers NM cable ( Romex)

My Scamp , Casita and Escape all were wired with NM cable from the factory
Type NM cable is an acceptable , code approved , cost effective wiring method
The idea that it is unsafe or a poor choice is BS
Romex has a plastic jacket that is flame resistant
steve dunham is offline   Reply With Quote
Old 03-18-2019, 06:45 AM   #7
Senior Member
 
Name: JD
Trailer: Scamp 16 Modified (BIGLY)
Florida
Posts: 1,512
If worried about fire from broken wires arcing replace your circuit breakers with the new arc detect breakers now required for bedrooms in houses.
Share
By William Atkinson Published In May 2017
An arc fault circuit interrupter (AFCI) is an advanced circuit breaker that, as a way to reduce electrical fire threats, breaks the circuit when it detects a dangerous electric arc in the circuit that it protects.

An AFCI is able to selectively distinguish between a harmless arc that is incidental to the normal operation of switches and plugs, versus a potentially dangerous arc that can occur, such as in a lamp cord with a broken conductor. An AFCI is designed to detect a wide range of arcing electrical faults that help reduce the electrical system from being an ignition source of a fire.
redbarron55 is offline   Reply With Quote
Old 03-18-2019, 08:07 AM   #8
Senior Member
 
Name: Steve
Trailer: Casita 17 ft DLX SD & 21 ft SOB
NW Wisconsin
Posts: 3,485
Quote:
Originally Posted by redbarron55 View Post
If worried about fire from broken wires arcing replace your circuit breakers with the new arc detect breakers now required for bedrooms in houses.
Share
By William Atkinson Published In May 2017
An arc fault circuit interrupter (AFCI) is an advanced circuit breaker that, as a way to reduce electrical fire threats, breaks the circuit when it detects a dangerous electric arc in the circuit that it protects.

An AFCI is able to selectively distinguish between a harmless arc that is incidental to the normal operation of switches and plugs, versus a potentially dangerous arc that can occur, such as in a lamp cord with a broken conductor. An AFCI is designed to detect a wide range of arcing electrical faults that help reduce the electrical system from being an ignition source of a fire.
I did electrical fire inspections in a large metropolitan city for several years
Red Baron is correct . Many of the fires I inspected were started by arcing faults ,often in small household cord connected appliances and overloaded receptacles
Many of these fires happened in winter by the use of portable electric space heaters
We are experiencing problems with the receptacles in our 2018 trailer
Our furnace failed so we plugged in a electric space heater The continuos load of the space heater caused the connection to the receptacle to fail
The connection to the receptacle is the crappy pushin type installed in a sloppy unprofessional manner .
The Romex used for the branch circuit wiring did NOT fail , the 37 cent device did
Most wiring fails at termination points !!
steve dunham is offline   Reply With Quote
Old 03-18-2019, 08:43 AM   #9
Senior Member
 
Name: Gordon
Trailer: 2015 Scamp (16 Std Layout 4) with '15 Toyota Sienna LE Tug
North Carolina
Posts: 3,135
Quote:
Originally Posted by steve dunham View Post
...
The connection to the receptacle is the crappy pushin type installed in a sloppy unprofessional manner ....
I too have had a failure at home from the push-in terminal that caused overheating, and I have a cousin who had a house fire from the same thing. They are only used because it saves the "professional" electrician a minute or two (per outlet). IMHO they should be outlawed.

Rather than worry about the wire that currently exist in a commercially built camper, I would sooner advise to redo all the 120 volt outlets using the screw terminals instead of the push-in's (if that is what they used).
gordon2 is offline   Reply With Quote
Old 03-18-2019, 08:59 AM   #10
Senior Member
 
Name: Steve
Trailer: Casita 17 ft DLX SD & 21 ft SOB
NW Wisconsin
Posts: 3,485
Quote:
Originally Posted by gordon2 View Post
I too have had a failure at home from the push-in terminal that caused overheating, and I have a cousin who had a house fire from the same thing. They are only used because it saves the "professional" electrician a minute or two (per outlet). IMHO they should be outlawed.

Rather than worry about the wire that currently exist in a commercially built camper, I would sooner advise to redo all the 120 volt outlets using the screw terminals instead of the push-in's (if that is what they used).
The NEC has placed more restrictions on where / when you can use pushin terminals on devices . When I wired homes I spliced everything out and used the screw terminals on plugs and switches not because it was code but I knew it was a better job for the homeowner
To be fair when we were doing tract homes our profit margin was under $200 per home so you used every legal shortcut available .

In my Casita they used # 12 AWG NM and connected the wires to the screw terminals
In my 21 ft SOB they used #14 AWG NM and they used the pushin type terminals
I will be rewiring my 21 SOB as soon as the weather warms up or more problems occur , whichever comes first
steve dunham is offline   Reply With Quote
Old 03-18-2019, 09:07 AM   #11
Senior Member
 
Name: Gordon
Trailer: 2015 Scamp (16 Std Layout 4) with '15 Toyota Sienna LE Tug
North Carolina
Posts: 3,135
Quote:
Originally Posted by steve dunham View Post
...
To be fair when we were doing tract homes our profit margin was under $200 per home so you used every legal shortcut available .
...
And therein lies the problem.

If I knew then what I know now, I would have personally paid the electrician extra out of my pocket to use the screw terminals.
gordon2 is offline   Reply With Quote
Old 03-18-2019, 07:23 PM   #12
Junior Member
 
Name: Sébastien
Trailer: Trillium 4500
Quebec
Posts: 19
I think Romex is use in new RV. I see this in the Progressive Dynamics installation guide named: How to Wire PD5000
"To wire this or any other 120 VAC outlet . Using Romex cable."
If PD or manufacturer use this wire, is it a good idea to use it ?
What type of wire I am supposed to use for my 120v if Romex is not good enough ?
Sebas is offline   Reply With Quote
Old 03-19-2019, 06:02 AM   #13
Senior Member
 
CarlD's Avatar
 
Name: Carl
Trailer: LiL Hauley
Syracuse, NY
Posts: 223
My R-Pod is wired with "Romex". You know it must be safe or Forest River wouldn't use it! Or maybe its just the lowest cost option!
__________________
Every day is a Saturday
CarlD is offline   Reply With Quote
Old 03-19-2019, 06:40 AM   #14
Senior Member
 
Name: bill
Trailer: 2013 Escape 19; 1977 Trillium 1300
The Mountains of North Carolina
Posts: 1,865
Registry
As a DIY'r, wiring outlets with the stranded cable is a major PITA and requires special outlets. Probably just a technique problem on my part. I thought long and hard about replacing it with Romex instead.

+100 Always use the screw terminals on outlets when using Romex.
__________________

thrifty bill is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Running Romex 14/3 with red wire as 12+ Ironhinge Electrical | Charging, Systems, Solar and Generators 29 12-02-2015 09:59 AM

» Upcoming Events
No events scheduled in
the next 465 days.
» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 06:17 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2019, vBulletin Solutions Inc.