Whether the trailer is connected to or separated from the earth by tires or stabilizers is not the point. The primary purpose of the ground wire & the bonding of all conductive parts of a system is to insure there is a low impedance path that will open the source circuit breaker of fuse when there is a fault to any conductive part of the system.

If you do not bond the frame of a trailer to the ground wire, a fault (connection) between a hot wire & the frame will put the frame at full line potential (120v). Since the utilities use connections to the earth (grounding) for a number of good reasons, there will be a potential difference between the hot frame & the earth. Since dirt isn't all that good a conductor, even with your stabilizers touching the earth there may not be enough current flow to open the source fuse or circuit breaker. Touching the frame (or anything bonded to it) and the earth (through your shoes, etc) in an ungrounded system will cause a shock.

Again, in a properly grounded & bonded system, the low impedance ground wiring will cause the fuse or breaker to open, protecting the user.

As to why utilities make an earth bond, there are many practical & safety reasons that make sense in a large distribution system. If there was no utility earth bond there would be no shock hazard to the earth, but there would be far greater problems caused by transformer failures, lightning strikes, etc. This is why small portable generators do not have to be "earthed", and are actually safer when not. But, since the utilities & service entrances of most homes & campgrounds are required to make an earth bond, not bonding the frame, gas lines, and all metal parts of a trailer does not meet code, and is unsafe.

An interesting PDF covering some of the advantages & disadvantages of grounding & earthing of generators is at This Link.
__________________

Jon Vermilye is offline   Reply With Quote
Old 09-02-2013, 11:08 AM   #16
Raz
Senior Member
 
Raz's Avatar
 
Name: Raz
Trailer: Trillium 2010
Vermont
Posts: 4,064
Quote:
Originally Posted by Byron Kinnaman View Post
Or the tongue jack is down.
Quite right. Mine has a wheel so it didn't occur to me.
__________________

__________________
Raz is offline   Reply With Quote
Old 09-02-2013, 05:33 PM   #17
Senior Member
 
Dan Meyer's Avatar
 
Name: Dan
Trailer: Scamp
Minnesota
Posts: 559
This happened to me years ago when camping in Ensenada, Mexico. In that case I troubleshot the issue down to a mis-wired plug in the campground.

On another note, the frame of my 2000 Scamp is connected to both the shore power ground, and also the negative terminal of the 12 volt DC power system. This is the factory configuration, and I would guess it is some sort of electrical code.

-- Dan Meyer
__________________

__________________
Dan Meyer is offline   Reply With Quote
Reply

Tags
boler


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Upcoming Events
No events scheduled in
the next 465 days.
» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 01:35 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.