Old 11-14-2015, 11:13 PM   #1
Senior Member
 
Name: K
Trailer: C
Iowa
Posts: 327
Can Casita 110v outlet power a 120v ceramic heater?

I got a little Lasko #754200 Ceramic Heater. The instruction book says it is a 1500w heater and it needs a 120v power source. My Casita is on shorepower (30amp), and I think the outlets are only 110v. Is it safe to plug the Lasko heater in to the Casita's internal outlet?

I actually got the heater to put underneath the skirted Casita to try and make it through the winter. When it is under the Casita, I plan to plug it in to the outside electrical socket, but I wanted to test it inside first.
whoot is offline   Reply With Quote
Old 11-14-2015, 11:32 PM   #2
Senior Member
 
Byron Kinnaman's Avatar
 
Trailer: Scamp
Posts: 7,056
Registry
The current house current standard is 120 Volt. That said most electrical devices designed for home are designed to operate anywhere between 90 volts and 130 volts 60HZ.
If you have any doubt look at the specifications in the owners manual.

The outlets are at what ever the voltage is where the trailer is connected to electricity.
__________________
Byron & Anne enjoying the everyday Saturday thing.
Byron Kinnaman is offline   Reply With Quote
Old 11-15-2015, 06:34 AM   #3
Senior Member
 
Name: bob
Trailer: 1996 Casita 17 Spirit Deluxe; 1946 Modernistic teardrop
New York
Posts: 5,415
We ran a 1500W heater all last winter in our Casita with no problem. Regularly used a toaster oven plugged into the outside outlet with no problem there.
mary and bob is offline   Reply With Quote
Old 11-15-2015, 08:43 AM   #4
Senior Member
 
honda03842's Avatar
 
Name: Norm and Ginny
Trailer: Scamp 16
Florida
Posts: 7,517
We have run a 1500 watt heater for years, usually in the morning when we first wake up. We make coffee, toast and have the heater on all at the same time. The coffee pot and toaster are on the same breaker. The heater on another breaker. By the time Ginny starts making bacon and eggs, the place is usually so warm, the vent and window are usually open and the heater off.

Byron's comment about the voltage of AC is absolutely correct. I note the time to make toast seems to vary. I attribute this to differences in the AC voltage.

By the way, we rarely find it necessary to run on 1500 watts at least in our little Scamp. We found the point where the heater thermostat cuts off at 70 F and usually set it there and usually on 800 watts.
__________________
Norm and Ginny

2014 Honda Odyssey
1991 Scamp 16
honda03842 is offline   Reply With Quote
Old 11-15-2015, 09:56 AM   #5
Senior Member
 
Name: bob
Trailer: 1996 Casita 17 Spirit Deluxe; 1946 Modernistic teardrop
New York
Posts: 5,415
William, you may want to look at what you have for breakers in your Casita. Ours only had one double 15 amp breaker.
mary and bob is offline   Reply With Quote
Old 11-15-2015, 10:06 AM   #6
Senior Member
 
Trailer: 2002 19 ft Scamp 19 ft 5th Wheel
Posts: 3,640
Send a message via Yahoo to Darwin Maring
Amps times Volts = Watts.
Take the 15 Amps and times it by 120 Volts and you have the wattage of your 15 Amp breaker.
Darwin Maring is offline   Reply With Quote
Old 11-15-2015, 11:26 AM   #7
Senior Member
 
WaltP's Avatar
 
Name: Walter
Trailer: 2017 Escape 17B
SW Virginia
Posts: 2,255
I know it's a bit confusing to see some appliances and systems rated at 120v and others at 110v, but it's really all the same. It would be best if everyone would standardize on the same stated voltage. There are not two different standards.

Walt
WaltP is offline   Reply With Quote
Old 11-15-2015, 11:28 AM   #8
Senior Member
 
Bob in Mb's Avatar
 
Name: Robert
Trailer: Surf-Side
Manitoba
Posts: 287
A 1500 watt heater just about max's out the 15 amp circuit so any other draw on the circuit will have to be small . That is - if your fridge or a pump is on the same circuit it would be overloaded.
Bob in Mb is offline   Reply With Quote
Old 11-15-2015, 11:57 AM   #9
Senior Member
 
NASA42's Avatar
 
Name: Frank
Trailer: Casita
Pennsylvania
Posts: 108
whoot....

WaltP and Bob in Mb are both right.

And....I have had the same Lasko heater for years and used it without problem. That said, I do not run it on high heat when the AC heatstrips or microwave are in use.

Frank
NASA42 is offline   Reply With Quote
Old 11-15-2015, 01:24 PM   #10
Senior Member
 
Name: K
Trailer: C
Iowa
Posts: 327
Thanks for all the advice, I ran it last night on the "low" setting (900 watts). I don't think I will ever run it at 1500 watts. I think the AC's heat-strip is 1500 watts, so maybe I can save some power by running the Lasko at 900 watts. The heat seemed better distributed inside the Casita, probably because the Lasko is on the floor, instead of in the ceiling. The Lasko is also a lot quieter than the AC unit.
whoot is offline   Reply With Quote
Old 11-15-2015, 03:15 PM   #11
Senior Member
 
Name: Steve
Trailer: 2018, 21ft escape— 2019 Ram 1500 Laramie
NW Wisconsin
Posts: 4,500
The NEC has changed the voltage rating of circuits from 110/220 to 115/230 to 120/240.
My Casita (2013) is wired with 12-2 NM which is rated for 20 amps. One problem you may encounter is that Casita uses 15 amp residential grade receptacles . Residential grade receptacles when subject to a continuous load that exceeds 80% of their amp rating have a tendancy to heat and self destruct. A thermostatically controlled heater in many jurisdictions located in colder climates is considered to be a continuous load. An easy solution is to change out the existing receptacle to a commercial grade receptacle . Make sure and connect the wires to the terminal screws of the receptacle. Do not use the pushin terminals on the back of the receptacle !
steve dunham is offline   Reply With Quote
Old 11-15-2015, 03:42 PM   #12
Senior Member
 
WaltP's Avatar
 
Name: Walter
Trailer: 2017 Escape 17B
SW Virginia
Posts: 2,255
Just a little addition to Steve's comment. The commercial receptacles he refers to are rated at 20 amps instead of 15 and can be recognized by the "lazy T" hole for the hot terminal.

Walt
WaltP is offline   Reply With Quote
Old 11-15-2015, 04:39 PM   #13
Senior Member
 
Name: Steve
Trailer: 2018, 21ft escape— 2019 Ram 1500 Laramie
NW Wisconsin
Posts: 4,500
Quote:
Originally Posted by WaltP View Post
Just a little addition to Steve's comment. The commercial receptacles he refers to are rated at 20 amps instead of 15 and can be recognized by the "lazy T" hole for the hot terminal.

Walt
They make commercial grade receptacles rated for both 15 & 20 amps
The T slot on 120 volt 20 amp NEMA receptacles is on the left or neutral side
steve dunham is offline   Reply With Quote
Old 11-15-2015, 04:42 PM   #14
Senior Member
 
WaltP's Avatar
 
Name: Walter
Trailer: 2017 Escape 17B
SW Virginia
Posts: 2,255
Thanks for the corrections Steve. I was not aware of commercial 15 amp receptacles.
WaltP is offline   Reply With Quote
Old 11-15-2015, 04:45 PM   #15
Senior Member
 
Name: Steve
Trailer: 2018, 21ft escape— 2019 Ram 1500 Laramie
NW Wisconsin
Posts: 4,500
Quote:
Originally Posted by WaltP View Post
Just a little addition to Steve's comment. The commercial receptacles he refers to are rated at 20 amps instead of 15 and can be recognized by the "lazy T" hole for the hot terminal.

Walt
Commercial grade receptacles are available in both 15 or 20 amp ratings.
The T slot on a 20 amp-120 VAC receptacle is on the left or neutral side of the receptacle.
steve dunham is offline   Reply With Quote
Old 11-15-2015, 05:11 PM   #16
Senior Member
 
Name: Lee
Trailer: Casita
Texas
Posts: 493
Registry
You can buy an inexpensive multi meter and check to see what your supply voltage is at the receptacle but more than likely the voltage will be 120 volts. If it was me I would consider getting a couple of heat lamps and the brooders lamp they screw into. The red bulbs are 250 watts apiece so two of them would only be 500 watts or 4.2 amps at 120 volts instead of 12.5 amps or 1500 watts at 120 volts. Tractor Supply Co. - Enjoy searching: heat lamps
__________________
Lee
Captleemo is offline   Reply With Quote
Old 11-15-2015, 05:47 PM   #17
Junior Member
 
Name: Tony
Trailer: In the Market
Texas
Posts: 3
Heater

1500 watts divided by 120 volts = 12.5 amps

If the circuit breaker is 15 amps and not much else on the same circuit then yes.
TCMac is offline   Reply With Quote
Old 11-15-2015, 07:22 PM   #18
Senior Member
 
Byron Kinnaman's Avatar
 
Trailer: Scamp
Posts: 7,056
Registry
110, 115, 120? Can be confusing. Just remember these number are approximate not absolute. Also you can be fooled if you try to do the math with a wrong variable. And if you try to do Ohm's law according to manufacturer's specifications you could miss.

All that said, if the power (watts) of a heater is in fact 1500 watts with a voltage of 100 Volts AC RMS you will have a current of 15 Amps RMS. It gets rather complicated.

For trailer use I don't think it would be problem, depending on how your trailer is wired. If it wired like mine every 120 volt outlet has it own 15 amp breaker.

A 15 amp breaker isn't going to trip at exactly 15 amps. Again most these number are close but not exact.
__________________
Byron & Anne enjoying the everyday Saturday thing.
Byron Kinnaman is offline   Reply With Quote
Old 11-15-2015, 07:58 PM   #19
Senior Member
 
WaltP's Avatar
 
Name: Walter
Trailer: 2017 Escape 17B
SW Virginia
Posts: 2,255
Most small, 1500 watt heaters have a low range of about 8-900 watts that'll draw a lot less current and I've never had to use mine on the high range anyway. The volume of space in our small trailers shouldn't need it. If it ever got cold enough that I felt my heater was heating too slow on low range, I'd just turn on the furnace for a short time to speed it up. So far, never happened. Even here.

Walt
Attached Thumbnails
IMG_0505 (Small).JPG  
WaltP is offline   Reply With Quote
Old 11-16-2015, 05:37 AM   #20
Raz
Senior Member
 
Raz's Avatar
 
Trailer: Trillium 2010
Posts: 5,185
Quote:
Originally Posted by steve dunham View Post
.........One problem you may encounter is that Casita uses 15 amp residential grade receptacles . Residential grade receptacles when subject to a continuous load that exceeds 80% of their amp rating have a tendancy to heat and self destruct.
Wow. I have to say I'm surprised that the testing agencies, especially the ones funded by the insurance companies, allow this. I guess everything has mouse print these days. Raz,
Raz is offline   Reply With Quote
Reply

Tags
casita


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Does adding multi-outlet to 12v outlet diminish output? Kudzu Asheville Electrical | Charging, Systems, Solar and Generators 8 05-08-2014 05:05 AM
Source for a 110v exterior outlet FlyboyTJ Modifications, Alterations and Updates 49 10-20-2012 06:38 PM
Ceramic Heater Safety melissab General Chat 24 11-08-2011 09:12 PM
Ceramic heater recommendations? Cam A Care and Feeding of Molded Fiberglass Trailers 16 04-19-2006 03:38 PM

» Upcoming Events
No events scheduled in
the next 465 days.
» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 03:09 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.