15amp service OK for 30amp Bigfoot? - Fiberglass RV
Old 01-14-2019, 08:15 PM   #1
Ev in Oregon's Avatar
Oregon Coast
I live full-time in my 1988 Bigfoot in an RV park located in a magical forest. I have an opportunity to move to a larger space, but there may be an issue.
The electric hookup at the new space is 15-amps. My BF is 30-amps, and the space I'm currently in has 30-amp service. I do not have a microwave, electric kettle, instapot, or appliances that draw a lot of energy. I do have a portable 1500w electric heater, which is my main source of heat, a laptop, and a no-frills 2-slice toaster. The heater cycles on & off all day when I'm home, but it's turned off at night and when I'm gone. I've learned that I cannot run the heater & the toaster at the same time. Lastly, all but the light over the stove are LEDs. (This is probably more info than is needed, but sometimes more is better? )
So, bottom line is, Can I do this? It just seems risky to me; the last thing I want to do is burn down my home.
Ev in Oregon is offline   Reply With Quote
Old 01-14-2019, 08:34 PM   #2
John in Michigan's Avatar
Trailer: 1979 Boler 1700
Yes this is a risky set up and should only be used temporarily. If you are using appliances and accessories on more than one of the branch circuits, you may be using more than 15 amps, (EDIT: while each branch circuit breaker won't pop). Your heater is consuming 12 amps. (EDIT: Toaster consumes at least 7 amps, so already over 15 amps.) Also, the 110vac to 12vdc converter is drawing some amperage (indicated on the product label).
In theory, when your usage exceeds 15 amps, the circuit breaker at the campsite power source should pop, but will it? If it doesn't pop, your supply power cord will heat up and present a fire risk.
I recently upgraded my Boler 17 to 30 amp connection. While plugging into 15 amp power at home I watch the usage very closely.
Old 01-14-2019, 08:37 PM   #3
Most electric box heaters have two settings, 750 watts and 1500 watts. At 15 amps total for the rig you probably would be ok at the 750watt setting,
You may need to turn the heat off when you use the toaster. And I am assuming no AC, no hair drier, etc.
Good point that the converter will draw a little too plus the refrigerator.
Old 01-14-2019, 08:41 PM   #4
Byron Kinnaman's Avatar
The 1500 Watt heater is kind of marginal, but already know that. The 1500 watt heater will draw about 12.5 amp max. That's pretty close to the 15 Amp service. You might need to turn off the converter for a short period, but I don't think would be a problem. If is turn it in the morning and back on when you go to bed. That should keep all the 12VDC stuff working.
FYI the 30amp rating on your trailer is a maximum not a minimum or ever a nominal item.
Now next question is what you going to do with additional site space? I would suggest you think about it before you jump. Don't answer me, just you.
Old 01-14-2019, 08:43 PM   #5
Dennis mn's Avatar
Minnesota
Originally Posted by John in Michigan View Post
Yes this is a risky set up and should only be used temporarily. If you are using appliances and accessories on more than one of the branch circuits, you may be using more than 15 amps. Your heater is consuming 12 amps. (EDIT: Toaster consumes at least 7 amps, so already over 15 amps.) Also, the 110vac to 12vdc converter is drawing some amperage (indicated on the product label).
The power supply cord for the trailer will handle up to 30 amps, it should not overheat, but if the load exceeds 15 amps, and the breaker does not trip, any wiring before the breaker sized for a 15 amp load could overheat.
2021 Nissan Pro 4X. 2020 Scamp 19’ Deluxe.
Dennis mn is offline   Reply With Quote
Old 01-14-2019, 08:43 PM   #6
1500Watts = 1500/120 = 12.5 amps. Watts divided by volts = current
750 Watts = 750/120 = 6.25 amps
Old 01-14-2019, 08:44 PM   #7
Paul O.'s Avatar
You already have figured it out that you cannot run the toaster and the heater at the same time, so don't do it. The only downside is that if you forget, you may blow the 15Amp breaker on the pedestal where you are plugged in and you have to go out to reset it. All your LED lights are fed by the battery, and the converter should be able to keep it charged. Charge the laptop when you are not there and you are not using the heater.
In any case, nothing should catch on fire only because you are plugged into the 15A service.
Old 01-14-2019, 08:51 PM   #8
Yes the power cord won't smoke or catch fire as long as:
- the power post 15 amp circuit breaker is reliable
- you use one 15 amp rated power cord
(EDIT: OK as per Dennis MN comment, if you use your 30 amp power cord, then just need to worry about the 30 amp to 15 amp adapter overheating.)
Old 01-14-2019, 10:57 PM   #9
Steve Outlaw's Avatar
Trailer: Oliver
I live full-time in my 1988 Bigfoot in an RV park located in a magical forest. I have an opportunity to move to a larger space, but there may be an issue....
If there are any elves living in said magical forest have them cast a spell of electrical enrichment on your power pole. Do Not ask a gnome or a troll for help as they are generally not very knowledgeable about issues with electricity.
Old 01-15-2019, 07:53 AM   #10
Trailer: 2003 21RB Bigfoot
Coos Bay, Oregon
It may be a little inconvenient but well worth it to live in a magical forest
South Coast Stu is offline   Reply With Quote
Old 01-15-2019, 08:26 AM   #11
Ed Harris's Avatar
So if you already can not run the toaster and heater together on a 30a supply from the park then I have to think the trailer is running both on a 15a circuit internally already.
If so there should really be no difference at all whether the trailer input is 15a or 30a as you are already limited to 15a on the breaker in the trailer.
At the same time you say you don't really use any heavy demand items but the heater and toaster are 2 of the higher demand items you might run in a trailer?
I also wonder about the logic of leaving a spot in a Magical Forest for any reason but maybe thats another conversation?
Ed Harris is offline   Reply With Quote
Old 01-15-2019, 08:35 AM   #12
Ed,
Problem is that with a 30 amp system in the camper, you are not limited to a 15 amp circuit in the camper. Typically a 30 amp camper system will have:
- 30 amp main breaker
- multiple 110vac branch circuits: one dedicated branch circuit for the AC to DC converter, two or more branch circuits for 110vac loads (usually for the AC outlets)
Yes apparently the toaster and heater are plugged into the same branch. What about the fridge?
As a result, there is really no protection in the camper if you feed the camper with a 15 amp supply line. Therefore you must rely on the supply cord, 30-to-15 adapter, and hope the power post 15 amp circuit breaker will protect them.
John
Old 01-15-2019, 08:59 AM   #13
For someone living full time in the camper (as the OP has indicated) and wants to park on a campsite with only 15 amp service, best change to reduce risk: replace the 30 amp main breaker with a 15 amp breaker. Can always switch back to a 30 amp breaker in the future.
Old 01-15-2019, 09:20 AM   #14
To me anyway, for a "full-timer," it just doesn't make a lot of sense to want to go "cramping" instead of "glamping". Why would you bother to own a trailer with the amenities you enjoy using every day, and then have to jockey them around for position in the electrical hierarchy of your trailer as to what you can use when and where, but not while this or that is running. What a self-imposed PITA that would be. For my take on it, I'd hold off until a spot with adequate 30 Amp power presents itself. Why make yourself miserable trying to make it work on a substandard electrical supply that doesn't meet your needs or requirements? It just makes no sense as to why someone would want to endure those hardships day after day if you're full-timing. Just my 2 cents.
Old 01-15-2019, 09:34 AM   #15
NW Wisconsin
I’m with Greg on this one the problem is more one of inconvenience then one of safety . Tripping a circuit breaker does not constitute a hazard , it’s what circuit breakers are designed to do . I’ve tripped the 30 amp main breaker in my trailer many times trying to run too much stuff at one time !
Old 01-15-2019, 10:21 AM   #16
Trailer: Bigfoot 17G
Why not just install an efficient propane heater -
https://www.amazon.com/dp/B000BUV1RK...v_ov_lig_dp_it
bobblangley is offline   Reply With Quote
Old 01-15-2019, 11:02 AM   #17
ZachO's Avatar
Trailer: Sasquatch
Montana
I'm jealous of your setup. Magical forest especially. A toaster would be nice! I use a very inefficient toaster: my oven. Oh well. Lots of propane and it takes maybe 15 min total to get a piece of toast, but it takes zero electricity
Old 01-15-2019, 08:15 PM   #18
If you move does the electric pedestal have a 15Amp switch? Some posts only have resets or switches for the 30Amp and 50Amp. We've been in a few campgrounds that said if you blow the 15Amp service you are responsible for any damages and for the person to come fix it. It sounds weird but very true.
Jann Todd is offline   Reply With Quote
Old 01-15-2019, 09:43 PM   #19
Oregon Coast
In spite of all the great and knowledgeable advice from all you fine folks, I like Steve's the best. In previous encounters, I learned about gnomes and trolls and their wily ways, but thanks for the reminder.
Old 01-15-2019, 10:22 PM   #20
Oregon Coast
Thank you!
Well, as usual, I've received lots of really good advice from you folks. There's lots to ponder, and some decisions to be made.
I failed to mention that the larger site is in the same park where I'm currently living. It's a rare day when a full-time site becomes available in this small park, so I really don't want to leave here. It truly is a magical forest.
I'll be doing some serious "cogitating" on this, as my Dad used to say. I'll make this work because it'll be worth it. Thanks for all the help!
bigfoot
30amp Scamp at 50amp park TheWanderers Electrical | Charging, Systems, Solar and Generators 17 06-29-2019 08:26 AM
120V / ~15AMP ac for a scamp 13 dcs02d Problem Solving | Owners Helping Owners 14 12-08-2016 08:24 PM
Question About 15amp & 30amp Hookups Seth and Desiree Electrical | Charging, Systems, Solar and Generators 22 07-12-2014 02:51 AM
50amp to 30amp adapter scamprookie Problem Solving | Owners Helping Owners 7 05-07-2013 08:16 AM
Wiring Diagram for 120v 30amp Burro entrance panel needed megatrack Problem Solving | Owners Helping Owners 1 03-27-2012 07:14 PM