Kay, the 10 ga wire is fine, but since you will be tying into 30 amp shore power, unless your breaker box is rated for 30 amps or higher, you definitely have a problem.
John in Michigan is offline   Reply With Quote
Old 07-10-2017, 03:48 PM   #22
Senior Member
 
likeair2me's Avatar
 
Name: KAY
Trailer: SCAMP
Missouri
Posts: 377
Registry
The box already has two 15A breakers in it. Wouldn't that be a 30A box?
likeair2me is offline   Reply With Quote
Old 07-10-2017, 03:55 PM   #23
Senior Member
 
John in Michigan's Avatar
 
Name: John
Trailer: 1979 Boler 1700
Michigan
Posts: 2,049
Registry
Probably a 15 or 20 amp sub-panel box with no main breaker. There should be a label somewhere on the box indicating its rating.

Edit: Just as with any breaker/fuse panel, you can't base the box rating on the values of the breakers/fuses that are installed. For example, with a 30 amp rated distribution box, there could be 4 15 amp circuits installed (Steve Dunham's example).
John in Michigan is offline   Reply With Quote
Old 07-10-2017, 05:07 PM   #24
Senior Member
 
Name: Steve
Trailer: 2018, 21ft escape— 2019 Ram 1500 Laramie
NW Wisconsin
Posts: 4,500
The amp rating of a load center is based on the size of the bus and how the bus is braced for fault current. The breakers have no bearing on the rating.
steve dunham is offline   Reply With Quote
Old 07-10-2017, 05:37 PM   #25
Senior Member
 
rbryan's Avatar
 
Name: Robert
Trailer: 2015 Escape 19 "Past Tents" 2018 F150 Lariat 2.7L EB SuperCrew
Arkansas
Posts: 1,298
Registry
Quote:
Originally Posted by steve dunham View Post
The amp rating of a load center is based on the size of the bus and how the bus is braced for fault current. The breaker have no bearing on the rating.
[emoji106] [emoji106] [emoji106]
__________________
"You can't buy happiness, but you can buy an RV. And that is pretty close."
rbryan is offline   Reply With Quote
Old 07-10-2017, 07:44 PM   #26
Senior Member
 
Name: Steve
Trailer: Scamp 13
California
Posts: 1,889
Quote:
Originally Posted by likeair2me View Post
The box already has two 15A breakers in it. Wouldn't that be a 30A box?
Remove the cover there should be a rating label on the back side. If your Scamp was wired like mine from the factory the incomming cord was wired to the buss inside. Attached to that bus was 2 -15 amp breakers. This is closer to a sub panel as the main supply protection comes from the outlet you plug into. Look at your power cord, you you should see embossed numbers. My origional cord was stamped 14-3 recrecational 15 amp and a series of code numbers. If you use an adapter and plug this cord into a 30 amp supply and overload the 2- 15 amp breakers you could easily melt the cord or burn up the 15 amp plug which ever would go first.
stevebaz is offline   Reply With Quote
Old 07-10-2017, 08:13 PM   #27
Senior Member
 
likeair2me's Avatar
 
Name: KAY
Trailer: SCAMP
Missouri
Posts: 377
Registry
So I pulled the cover off of the breaker panel and these are the labels. One says 30Amp Main. Does that mean it is NOT a 30Amp panel and I am not reading it correctly?

And I have no intention of using the original cord with a 30A draw. That is the reason for the 30A Marinco inlet and the 30A cord. That is why I intend to replace the feed wire from the inlet to the box with 10ga wire, if indeed, the box is a 30A box.

Ding.
Come out of your corners fighting.
Attached Thumbnails
inside door panel.jpg   inside panel side.jpg  

likeair2me is offline   Reply With Quote
Old 07-10-2017, 08:22 PM   #28
Senior Member
 
John in Michigan's Avatar
 
Name: John
Trailer: 1979 Boler 1700
Michigan
Posts: 2,049
Registry
OK, then it IS a 30 amp rated panel. In theory you should be able to run 30 amp shore power to it, but I'm NOT a licensed electrician, just an electrical engineer (with little experience with this type of equipment).
John in Michigan is offline   Reply With Quote
Old 07-10-2017, 08:40 PM   #29
Senior Member
 
likeair2me's Avatar
 
Name: KAY
Trailer: SCAMP
Missouri
Posts: 377
Registry
As a EE, I am sure you spotted the rust. I believe that is because the panel is under the 12v water faucet (that failed some years before I got it), and the water discharge for the sink is right in front of the breaker panel, which does not have a front cover or NEMA waterproof box. Minimal at best. I guess they never heard about running the electrical ABOVE any potential leaking fluids.

For now, If I can just run some A/C in the unit I will be happy. No major upgrades will happen until I get something like a PD4045, or the WFCO unit that Johnny has dealt with. If I can figure out a reasonable mount for the window, the A/C will plug in to the unused breaker on the right side of the cabinet. At least that way, I will get to use the camper for something other than a sweat lodge.
likeair2me is offline   Reply With Quote
Old 07-10-2017, 08:52 PM   #30
Senior Member
 
John in Michigan's Avatar
 
Name: John
Trailer: 1979 Boler 1700
Michigan
Posts: 2,049
Registry
Good luck Kay! I have 15 amp service in my Trillium 4500. To run the electric heater, I just run a 2nd 15 amp extension cord back to the campsite power post...
John in Michigan is offline   Reply With Quote
Old 07-10-2017, 11:22 PM   #31
Senior Member
 
Johnny M's Avatar
 
Name: John
Trailer: '71 Boler, '87 Play-Mor II
Deep South
Posts: 1,261
Quote:
Originally Posted by likeair2me View Post
So Johnny, is your panel the WF-8540? And do you find it to have sufficient power distribution without tripping the breakers on 110V uses?
I actually have the 8725 which has a 30 amp main, and 3 branch circuits. It has what is called twin breakers - meaning 2 breakers in the space of a normal sized one so it is more compact and it has 4 DC circuits (1 for the battery) each with their own fuse. It will output up to 430 watts. It is a three stage type converter meaning it will do absortion mode, bulk mode and float charging of your battery(ies). It has a cooling fan, reverse polarity protection as well as over current, over temp & voltage protection too. The previous owner had it wired up with several a/c outlets powering a big 10000 btu Dometic roof top air, microwave, incandescent light fixture and a fluorescent light also. He also had wired in come dc incandescent lighting.

I reconfigured it on our reno, (2) 110 volt outlets 15 amps each 30 amp main 1 unused breaker, 4 dc circuits (water pump, led lighting, 12vdc outlets, and 1 spare circuit. We run our refrigerator and led tv on one outlet and our 5000 btu a/c on the other and can also charge phone off that one as needed. I can add another circuit if I need to but the need hasn't come up. We have never tripped a breaker or blown a fuse as we bought it or after the reno.
__________________
1971 Boler 1300 - "Suite 13"
1987 Play-Mor II - "The Beach House"
Johnny M is offline   Reply With Quote
Old 07-11-2017, 06:35 AM   #32
Senior Member
 
likeair2me's Avatar
 
Name: KAY
Trailer: SCAMP
Missouri
Posts: 377
Registry
Johnny, does the unit supply surge/brown out protection too?
likeair2me is offline   Reply With Quote
Old 07-11-2017, 07:12 AM   #33
Senior Member
 
Name: Gordon
Trailer: 2015 Scamp (16 Std Layout 4) with '15 Toyota Sienna LE Tug
North Carolina
Posts: 5,156
Quote:
Originally Posted by likeair2me View Post
Johnny, does the unit supply surge/brown out protection too?
FYI, for that I use (and recomend) Progressive Industries RV Surge and Electrical Protection industry lea
gordon2 is offline   Reply With Quote
Old 07-11-2017, 07:34 AM   #34
Senior Member
 
likeair2me's Avatar
 
Name: KAY
Trailer: SCAMP
Missouri
Posts: 377
Registry
Gordon, I see that the plug-in variety is much cheaper, but having it in a permanent location where it is protected is always better. One less thing to worry about breaking or getting crushed, or in my usual case, forgotten.

Is there a preferred mounting location min/max from the breaker box? Can I put one under the dinette bunk near the sink or does it need some distance?
likeair2me is offline   Reply With Quote
Old 07-11-2017, 08:48 AM   #35
Senior Member
 
Name: Gordon
Trailer: 2015 Scamp (16 Std Layout 4) with '15 Toyota Sienna LE Tug
North Carolina
Posts: 5,156
Quote:
Originally Posted by likeair2me View Post
Gordon, I see that the plug-in variety is much cheaper...
Be sure you are comparing apples to apples.

Quote:
Originally Posted by likeair2me View Post
... but having it in a permanent location where it is protected is always better. One less thing to worry about breaking or getting crushed, or in my usual case, forgotten.
That is my thinking also but there are advantages and disadvantages either way.

Quote:
Originally Posted by likeair2me View Post
Is there a preferred mounting location min/max from the breaker box? Can I put one under the dinette bunk near the sink or does it need some distance?
See Progressive Industries Support

I put mine in my port side dinette / bed bench near the converter. I do notice a very slight hum from the contactor but it is only noticeable if it is dead quiet and I am lying on the bed with my head over the unit. I have one with a remote display which is in a cabinet where I can open the door to read the display.
gordon2 is offline   Reply With Quote
Old 07-11-2017, 09:09 AM   #36
Senior Member
 
likeair2me's Avatar
 
Name: KAY
Trailer: SCAMP
Missouri
Posts: 377
Registry
Dead quiet is the sound of a power outage. LOL I keep the fan on when sleeping. When I travel I still use my white noise app on my phone. Saved me many sleepless nights.
Do the plug in types even have brownout protection?
likeair2me is offline   Reply With Quote
Old 07-11-2017, 09:39 AM   #37
Senior Member
 
Name: Gordon
Trailer: 2015 Scamp (16 Std Layout 4) with '15 Toyota Sienna LE Tug
North Carolina
Posts: 5,156
Quote:
Originally Posted by likeair2me View Post
Do the plug in types even have brownout protection?
Again, ... see comparing apples to apples. Under voltage protection is the first thing on the list.
gordon2 is offline   Reply With Quote
Old 07-11-2017, 12:11 PM   #38
Senior Member
 
Trailer: 2008 Casita 17 ft Spirit Deluxe
Posts: 2,020
Registry
Quote:
Originally Posted by likeair2me View Post
Do the plug in types even have brownout protection?
Of their portable (plug-in) units, only this one offers brown-out (aka low voltage) protection, and it is more expensive than the hard-wired unit.

https://progressiveindustries.myshop...ucts/ems-pt30x



I agree with Gordon, and I also installed the "hard-wired" 30 Amp PI unit. It is more expensive than the pedestal hanging types, (with the exception of the one noted above,) but they don't tend to grow legs quite as easily when you're not around. I also installed a larger access hatch with a keyed locking latch, which was needed to perform the installation due to the size of the circuit protector. It also serves to provide a much better access to what was useless space before. Not fighting with that silly little factory installed power hatch is so much nicer.

https://progressiveindustries.myshop.../ems-hw30c-pid
Attached Thumbnails
New Electrical Hatch1.JPG  
Casita Greg is offline   Reply With Quote
Old 07-11-2017, 12:17 PM   #39
Senior Member
 
likeair2me's Avatar
 
Name: KAY
Trailer: SCAMP
Missouri
Posts: 377
Registry
Now this is some helpful stuff. Are there space considerations when installing either the panels or the surge protectors? Does an offset space or ventilation space need to be part of the location plan? I've only got a 13' camper. Not much larger than a brief case, so it's all about location, location, location.
likeair2me is offline   Reply With Quote
Old 07-11-2017, 12:35 PM   #40
Senior Member
 
Trailer: 2008 Casita 17 ft Spirit Deluxe
Posts: 2,020
Registry
Most converters do require some ventilation around them, (and most have their own fans which kick on as needed to cool them.)

But the hard-wired PI circuit protectors are encased in a hard plastic case and are "O" ring gasketed, so there really isn't any need for ventilation. They are sealed solid state units.

The only space consideration would be an area sufficient in size to mount the unit, (and a little extra room to route your incoming and outgoing power lines between your shore power outlet and your electrical panel.) They can also be mounted vertically on a bulkhead as well if that works better for you.
Casita Greg is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
For Sale: Link to 30A ext. cord, folding ladder Timber Wolf Classified Archives 0 06-10-2016 01:34 PM
Installing a Marinco 30 amp plug in gihuff Electrical | Charging, Systems, Solar and Generators 4 08-18-2014 10:27 PM
Vehicle sun roof addition Mike jagular Modifications, Alterations and Updates 16 03-20-2006 08:20 AM
Newest addition to the family! Legacy Posts General Chat 9 06-01-2003 09:20 PM
Leaking water inlet Legacy Posts Problem Solving | Owners Helping Owners 11 04-27-2003 09:02 AM

» Upcoming Events
No events scheduled in
the next 465 days.
» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 08:35 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.