Ground Wire Gauge
Is there a rule of thumb to determine what gauge the ground wire should be both in the trailer and through the harness?
|
|
|
04-23-2014, 08:00 AM
|
#2
|
Senior Member
Name: Greg
Trailer: 2008 Casita 17' SD
Washington
Posts: 1,997
|
10 gauge is typical.
|
|
|
04-24-2014, 05:26 AM
|
#3
|
Senior Member
Name: David
Trailer: Scamp
Michigan
Posts: 140
|
Is this a safety issue? Would 12 gauge cut it?
|
|
|
04-24-2014, 06:32 AM
|
#4
|
Senior Member
Name: Randy
Trailer: 1980Trillium 1300
Ontario
Posts: 373
|
Very good question. Here is simple quote.. .".. Remember that common ground wires must be adequate to carry the TOTAL amperage of the circuit, even when separate hot wires are used..."...
Wire Gauge Specification - TECHNICAL REFERENCE
|
|
|
04-24-2014, 07:00 AM
|
#5
|
Senior Member
Name: David
Trailer: Scamp
Michigan
Posts: 140
|
Thank you! There's my answer!
|
|
|
04-24-2014, 07:28 AM
|
#6
|
Senior Member
Trailer: Casita Spirit Deluxe 2003 16 ft
Posts: 1,899
|
You question can be answered with as much complication as you desire. If you’re looking for a simple, no-thought answer I think 10 ga. is a good one.
In general (and I’m no EE) you get to make your first decision as to how much voltage drop you want to tolerate. Voltage drop is a function of wire gauge, round trip wire length and amperage. There are all sorts of tables and calculators to help determine what wire gauge to use. West Marine has one I use, mostly because I’ve had a sailboat for longer than I’ve had the trailer. I generally shoot for 3% drop in the 12V side. Why? No reason. I did more boondocking in the past and I wanted as little loss as practical without going into room temperature superconductors. From the table, assuming a 32 foot round trip (I have a Casita 16’ SD) and 10 amps moving to the trailer from the tow, then that puts me right in the green band, or 10 ga.
I have one circuit I have fused for 20 amps that supplies the macerator pump I sometimes use to dump uphill or to speed the dump process. The outlet for that is right behind the fuse panel on the streetside of the trailer. Round trip length of inside and outside wiring is about 12-14 feet. That puts me again in the 10 ga band which is what I used.
Do you need 3% drop? No. Paraphrasing the Gallagher routine, it’s about style. Just watch out for the Sledge-O-Matic and the exploding watermelon…
|
|
|
04-24-2014, 09:39 AM
|
#7
|
Senior Member
Name: David
Trailer: Scamp
Michigan
Posts: 140
|
Again, thanks.
|
|
|
04-24-2014, 09:45 AM
|
#8
|
Senior Member
Name: Steve
Trailer: 2018, 21ft escape— 2019 Ram 1500 Laramie
NW Wisconsin
Posts: 4,500
|
Quote:
Originally Posted by Steve L.
You question can be answered with as much complication as you desire. If you’re looking for a simple, no-thought answer I think 10 ga. is a good one.
In general (and I’m no EE) you get to make your first decision as to how much voltage drop you want to tolerate. Voltage drop is a function of wire gauge, round trip wire length and amperage. There are all sorts of tables and calculators to help determine what wire gauge to use. West Marine has one I use, mostly because I’ve had a sailboat for longer than I’ve had the trailer. I generally shoot for 3% drop in the 12V side. Why? No reason. I did more boondocking in the past and I wanted as little loss as practical without going into room temperature superconductors. From the table, assuming a 32 foot round trip (I have a Casita 16’ SD) and 10 amps moving to the trailer from the tow, then that puts me right in the green band, or 10 ga.
I have one circuit I have fused for 20 amps that supplies the macerator pump I sometimes use to dump uphill or to speed the dump process. The outlet for that is right behind the fuse panel on the streetside of the trailer. Round trip length of inside and outside wiring is about 12-14 feet. That puts me again in the 10 ga band which is what I used.
Do you need 3% drop? No. Paraphrasing the Gallagher routine, it’s about style. Just watch out for the Sledge-O-Matic and the exploding watermelon…
|
'll
The 3% voltage drop rule is a standard from the NEC .The NEC has rules for allowable % voltage drop for both feeders and branch circuits. A # 10 AWG
is sufficient based on voltage drop ,ampacity and mechanical strength. Using a larger gauge wire in many cases does nothing but increase the cost.
|
|
|
04-24-2014, 10:39 AM
|
#9
|
Senior Member
Trailer: Casita Spirit Deluxe 2003 16 ft
Posts: 1,899
|
Quote:
Originally Posted by steve dunham
'll
The 3% voltage drop rule is a standard from the NEC .The NEC has rules for allowable % voltage drop for both feeders and branch circuits. A # 10 AWG
is sufficient based on voltage drop ,ampacity and mechanical strength. Using a larger gauge wire in many cases does nothing but increase the cost.
|
Cool! I love it when I do the right thing for the wrong reason. Sort of offsets the karma of those doing the wrong thing for no reason...
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
» Upcoming Events |
No events scheduled in the next 465 days.
|
|