10-18-2017, 11:47 AM
25 or 30 amp main breaker on WF-8725-PB
My WFCO WF-8725-PB Black 25 Amp Power Center came in, so I ran over to Home Depot to get the breakers. I got a Square D 30 amp type HOM, and a Square D 15/15 amp type HOMT.
Then I checked the documentation again, and it says:
"One 30 Aac "Main circuit"........
and below it it says:
"UL-Listed Main Circuit Breakers, rated for 120 Vac, maximum 25 Aac"
"UL-Listed Branch Circuit Breakers, rated for 120 Vac, maximum 20 Aac"
So, does the main have to be 25 or 30amp?
10-18-2017, 12:08 PM
Trailer: Escape 21C
I have to admit the instructions have me scratching my head, but all the WFCO panels I've seen have 30 amp main breakers.
10-18-2017, 12:22 PM
After looking at the wiring some more I've decided to put a 20 and a 15 in. The 20 will feed the converter (4.4 amp) and 15 amp for several 120v outlets. The 15 amp will feed my AC.
I thought that the main breaker would be wired before all the branch breakers (and then 30 amp would make sense), but the way the thing is set up there is no difference between 'main' breaker and 'branch' breakers. They're all connected to the same bus.
10-18-2017, 04:16 PM
I received a private message on this and since I cannot post pictures there I've attached them here to explain.
10-18-2017, 06:11 PM
Here's a picture I just took. If I wanted the left breaker (main) to protect the other breakers (2 half ones on the right spot), wouldn't it make sense to get rid of the wire that is hooked up to the hot bar, hook up the 120V AC in to the main breaker on the left at the bottom, and hook up all 120V outputs at the 2 x 15 amp split breaker on the right?
That is assuming breakers work in both directions, because I would be feeding the shore 30amp into the 30amp breaker from the bottom instead of the top.
10-18-2017, 06:31 PM
Trailer: Escape 21C
Back wiring (the second schematic) the main breaker is standard practice.
10-18-2017, 09:49 PM
Trailer: Playpac
OH
Ok. Go slow. This is high voltage.
If you use the main breaker separately in addition to the two smaller breakers, you will have a total potential amp load that exceeds the maximum for your distribution box.
The main breaker has to protect the entire distribution box from the loads being pulled by the two smaller breakers. The main breaker also protects the trailer-to-shore cord which is pulling all the amps from the shore power. The shore power should have its own breaker as well and the one you'll be plugging into will likely be 30 amps. But don't trust the shore power breaker that was wired by some campgrounds teenage helper that summer. So you definitely don't want a system that can pull more than 30 amps for that reason as well.
Each of the two smaller breakers protects the wires they are feeding.
The two smaller breakers should be no larger than 15 amps each.
If you put a 20 amp breaker in one of those small places you'll have to make sure that the wires leading from that into your camper is sufficient to handle a 20 amp load. That means a thicker wire than might be in there. Also, you will need to make sure that you have 20 amp switches and 20 amp outlets as well and those are different than the 15 amp switches and outlets that are standard.
The idea is that your breaker should never be bigger than the stuff it is protecting because you want the breaker to pop before one of those things pops. If your breaker is larger than the stuff downstream, then the stuff downstream is forced to act as a fuse so to speak and really ends up acting more like the filament in light bulb catching things on fire.
But don't take my word for this, I'm just some fool typing stuff on the internet. Research the h... e... double hockey sticks out of this stuff so that you're comfortable that you are your own expert it's not rocket science but it is science.
10-19-2017, 04:42 AM
I will go with the 30AMP main back wired, followed by a dual 15 amp breaker. However, look at this video: https://youtu.be/o_kEAvJWKiM?t=309. It's the same unit and it was wired in some RV factory the way the documentation describes: with the shore black directly on the main/hot bar, so the setup that we all agree is somewhat questionable.
I'm glad I questioned the documentation/instructions....
10-19-2017, 01:41 PM
Of coarse the main breaker and the other breakers are connected to the same buss. That is how you power the buss. Hook up the main breaker and turn it on and now the buss is energized so when you add breakers for branch circuits those breakers will have power and provide overload protection to the circuits they supply. You can turn off the main breaker and it will DE-energize the whole buss. It would be the same principle for your house. If you wanted to add a circuit or something to your house you would turn off the main breaker which would DE-energize the panel so it would be safe to work on. Of course if you don't feel comfortable working with electricity you might find somebody who is.
Lee
10-19-2017, 01:52 PM
Yes, that's what we all expect and how we all agree that it should be. But if you look at the diagram for the unit listed above ( http://wfcoelectronics.com/wp-conten...ion-Manual.pdf) you see that shore power is fed onto the bus directly (see "BLACK WIRE (TO AC SHORE - HOT)"). That's what surprises everybody including me who has looked at this.
I will wire it correctly by feeding shore hot onto the 30 amp breaker instead, which in turn will feed it onto the bus, but that doesn't change what the manufacturer's wiring diagram shows.
10-19-2017, 02:44 PM
Your sure right about that wiring diagram being confusing. Kinda looks like the main breaker is half 30 amp and half 15 amp.
Lee
10-19-2017, 02:59 PM
Never seen one like that. I have replaced some of the original ( fat ) breakers in my house panel with the slim line breakers but they were single breakers. Of course if hooking up the shore power right to the buss what good is the main breaker. It sounds like if you turned off the main breaker nothing would happen. Maybe somebody out there has actually worked on this brand of panel and can shed some light on it.
Lee
10-19-2017, 03:08 PM
If your trailer only has one or two 15 amp circuits then you are not required to have a main breaker. If your trailer service cord is 10/3 rated for 30 amps then you can have 2 -15 amp branch circuits (2x15=30) without a main breaker because the two circuits can not overload the 30 amp service cord. If you have 3 to 5 branch circuits in the trailer then you need a main breaker ( 30 amp ) in order to protect the 30 amp service cord.
Best practice is to install a main breaker.
I was a licensed electrician for over 40 years and if your looking for good electrical advice , I would listen to Jon Vermilye. He knows what he is talking about and is not a Wiki expert . He is a genuine , well educated and extremely smart electrician .
10-19-2017, 03:17 PM
ME - I would have a main breaker that turns everything off.
10-19-2017, 04:00 PM
photo of standard / "2nd schematic"....
a thousand words ???... (97 BF 17 from factory)
in the pic there is an abandoned circuit (AC) that used the red (20A) breaker (hot and neutral disconnected)...not a good idea to leave unprotected like that but it's the way I found it.... a marette/wire nut was used to lengthen the hot wire of first 15A breaker, I presume...
tripping the MAIN (green) breaker shuts off power to the bar above that the rest of the breakers hang on / get their power from (power is then off EVERYWHERE)
note: I am in no way an electrician....but I do take a lot of pictures
10-19-2017, 05:07 PM
That makes an awful lot of sense! Thank you! This explains the wire to the hot bus! Mystery solved!
I'll still go and wire the hot to the 30amp, and then use a tandem 15/15 after that. One goes to the 5 amp converter pigtailed to the outlets, the other goes to the AC. That leaves me with 10 amp on the extra outlets if the converter is drawing full amps, which will be rare. I'll post a pic after I wire it and before I plug it in, but I'm 100% confident that I understand it.
10-19-2017, 05:45 PM
yep...IIRC that's the way mine was hooked up (110 outlets and converter wire twisted together and plugged into the first 15A breaker)....the breaker for the AC was 20A though (????)....then a "stand alone" 15A breaker that went to an outlet for the microwave above the kitchen
hard to see in first pic because the hot wire coming from converter had a label attached to it.....
second pic wiring cleaned up...after getting rid of the converter
third pic panel relocation
fourth pic finished product
Trailer: Escape 21C
Steve gave a good description of the basic requirements for 30 amp RV 120v electrical distribution.
You do not have to limit the branch breaker amperage to the main. Look at your house & you will see the amperage total of the branch circuits far exceeds the main. You can do the same for a RV.
The main protects the panel, and provides some protection to the #10 power cord, although technically at the wrong end of the cord. The branch breakers protect the branch wiring, i.e., #14 wire should be protected by a 15 amp breaker, & #12 wire protected by a 20 amp breaker. The load determines the choice of breaker & wire size. The actual NEC requirements are more involved, but I'm on the road & don't have my code book with me.
Tandem breakers are often used in RV distribution panels because of the limit of 4 breaker spaces in a 30 amp RV distribution panel. You may need to do a bit of searching to find a 30 / 15, but they do exist.
With Air Conditioners, Microwaves, Electric water heating, and high current plug in appliances such as hair dryers, electric frying pans, toasters, etc, it is easy to overload the 30 amp main, which is why 2 leg 50 amp distribution panels are used in larger RVs. If the loads are balanced between the two legs, up to 100 amps of load can be used. With our normal 30 amp service, we are limited to two high current devices at the same time...
10-20-2017, 06:20 AM
Trailer: 1981 Trillium 5500
John's description is spot on, I have a 17 Trillium, with 4 breaker spaces, I run with a 15amp main, and using the small breakers have 6 branch circuits all at 15 amps (rated)
with everything I run- 1500 watt heater, converter, toaster, kettle I have never tripped the main breaker, you Just need to be aware of what loads are on at the time- don't run all three at same time