Generator Grounding

I finally bought a new generator and the manual (yes, I did read it) mentions to be sure to ground it. Now I realize that I haven't really paid attention, but I don't remember seeing a ground wire to earth ground on the few portable generators I've seen operating. Please advise if that if really necessary. It's not going to be a problem, but it is one more thing to remember and that seems to be getting harder as the years charge on.
Rod D is offline   Reply With Quote
Old 06-01-2018, 06:05 PM   #2
Senior Member
 
rbryan's Avatar
 
Name: Robert
Trailer: 2015 Escape 19 "Past Tents" 2018 F150 Lariat 2.7L EB SuperCrew
Arkansas
Posts: 1,298
Registry
Quote:
Originally Posted by Rod D View Post
I finally bought a new generator and the manual (yes, I did read it) mentions to be sure to ground it. Now I realize that I haven't really paid attention, but I don't remember seeing a ground wire to earth ground on the few portable generators I've seen operating. Please advise if that if really necessary. It's not going to be a problem, but it is one more thing to remember and that seems to be getting harder as the years charge on.
Can you tell me what kind of generator it is Rod? Make and model? If it's one of the more common 2000W inverter generators, external grounding isn't really necessary. However, you can rig up a "gen plug" which is nothing more than an edison plug with a wire between the neutral post and the ground post inside. That plug is then inserted in an unused receptacle on the generator, which bonds neutral to ground. Doing this allows you to use an EMS if your trailer is equipped with one.

If you want to externally ground it, you can use a rod pounded into the ground attached to the grounding post on the generator, but I've used generators like the Honda eu2000i a ton and never found it necessary.
__________________
"You can't buy happiness, but you can buy an RV. And that is pretty close."
rbryan is offline   Reply With Quote
Old 06-01-2018, 07:35 PM   #3
Senior Member
 
Name: Steve
Trailer: 2018, 21ft escape— 2019 Ram 1500 Laramie
NW Wisconsin
Posts: 4,500
A generator is a separately derived system and the neutral conductor is not grounded
Power supplied from a utility has an intentionally grounded neutral
Small portable generators are normally not intentionally grounded
If you are concerned drive a 1/2” x 8 ft ground rod and bond the generator but that kind of takes away the portability .
steve dunham is offline   Reply With Quote
Old 06-01-2018, 09:07 PM   #4
Senior Member
 
John in Santa Cruz's Avatar
 
Name: John
Trailer: Escape 21, behind an '02 F250 7.3 diesel tug
Mid Left Coast
Posts: 2,940
the portable DC inverter generators we're using, the neutral is NOT connected to the chassis ground internally, so ideally you use a plug adapter that bonds ground to neutral. These can very easily be made, and plugged into an empty outlet on the generator. http://noshockzone.org/generator-gro...utral-bonding/

If your RV has a EMS like the Progressive used optionally on Escape's, then you MUST use one of these, or your EMS will trip a ground fault.
John in Santa Cruz is offline   Reply With Quote
Old 06-02-2018, 08:26 AM   #5
Senior Member
 
Name: Steve
Trailer: 2018, 21ft escape— 2019 Ram 1500 Laramie
NW Wisconsin
Posts: 4,500
Quote:
Originally Posted by John in Santa Cruz View Post
the portable DC inverter generators we're using, the neutral is NOT connected to the chassis ground internally, so ideally you use a plug adapter that bonds ground to neutral. These can very easily be made, and plugged into an empty outlet on the generator. Generator Ground-Neutral Bonding | No~Shock~Zone

If your RV has a EMS like the Progressive used optionally on Escape's, then you MUST use one of these, or your EMS will trip a ground fault.
The adaptor plug you describe may fool the EMS but it does not ground the generator IE ; The generator is not intentionally or effectively connected to an earth ground .
Again a generator is a separately derived system similar to a transformer
steve dunham is offline   Reply With Quote
Old 06-02-2018, 09:44 AM   #6
Raz
Senior Member
 
Raz's Avatar
 
Trailer: Trillium 2010
Posts: 5,185
You will want to check your trailer frame is grounded as well, especially if you start adding ground rods. A fault to the frame needs to open the breaker.
Raz is offline   Reply With Quote
Old 06-02-2018, 01:12 PM   #7
Senior Member
 
John in Santa Cruz's Avatar
 
Name: John
Trailer: Escape 21, behind an '02 F250 7.3 diesel tug
Mid Left Coast
Posts: 2,940
trailers aren't grounded anyways, they are sitting on rubber tires... the jumper will bond the generator neutral to the ground wire, which on the trailer side is connected to the trailer frame. this is no different than an RV with a built in generator.
John in Santa Cruz is offline   Reply With Quote
Old 06-02-2018, 01:27 PM   #8
Raz
Senior Member
 
Raz's Avatar
 
Trailer: Trillium 2010
Posts: 5,185
Quote:
Originally Posted by John in Santa Cruz View Post
trailers aren't grounded anyways, they are sitting on rubber tires... the jumper will bond the generator neutral to the ground wire, which on the trailer side is connected to the trailer frame. this is no different than an RV with a built in generator.
There are two types of ground. Earth gound which involves ground rods etc. and chassis ground which is simply using the metal chassis as a wire. Both are being talked about here which adds to the confusion. I am not advocating the use of ground rods with an RV but commented because it was mentioned earlier. My point is, the system be wired so should the trailer frame become energized, a breaker will trip.
Raz is offline   Reply With Quote
Old 06-02-2018, 02:44 PM   #9
Senior Member
 
John in Santa Cruz's Avatar
 
Name: John
Trailer: Escape 21, behind an '02 F250 7.3 diesel tug
Mid Left Coast
Posts: 2,940
a GFI won't even work without ground-neutral bonding somewhere....
John in Santa Cruz is offline   Reply With Quote
Old 06-02-2018, 03:23 PM   #10
Member
 
Name: Rod
Trailer: Scamp 16 Std Layout 4
West Virginia
Posts: 37
Gen Question Thanks

Thank you all for your help in determining the grounding of the generator. FYI it's a Westinghouse iGen2200, so it should be pretty much the same as all the other portables. Your answers explain why I couldn't remember seeing anyone add a ground wire to earth and I don't expect to do so either. I will need to add the adapter to bond the circuit as I have both an EMS and an inverter that indicates it needs one as well. Again, thank you; I knew you guys would help me out!
Rod D is offline   Reply With Quote
Old 06-02-2018, 03:47 PM   #11
Senior Member
 
Name: Gordon
Trailer: 2015 Scamp (16 Std Layout 4) with '15 Toyota Sienna LE Tug
North Carolina
Posts: 5,155
Quote:
Originally Posted by Rod D View Post
... will need to add the adapter to bond the circuit as I have both an EMS and an inverter that indicates it needs one as well. ...

Testing a Generator for a Floating Neutral
gordon2 is offline   Reply With Quote
Old 06-02-2018, 03:48 PM   #12
Senior Member
 
Name: Steve
Trailer: 2018, 21ft escape— 2019 Ram 1500 Laramie
NW Wisconsin
Posts: 4,500
Quote:
Originally Posted by John in Santa Cruz View Post
a GFI won't even work without ground-neutral bonding somewhere....
WHY ? A GFCI does not require an equipment ground to function
I have installed hundreds of GFCI’s on old knob & tube systems and the installation was fully code compliant and functioned as intended .
steve dunham is offline   Reply With Quote
Old 06-02-2018, 04:06 PM   #13
Senior Member
 
Name: JD
Trailer: Scamp 16 Modified (BIGLY)
Florida
Posts: 2,445
The thing that trips the GFCI is a difference on the power and neutral return.
Current through the ground instead of neutral at 5 mA or more should trip the breaker two wire or three.
redbarron55 is offline   Reply With Quote
Reply

Tags
generator


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Elec. Systems grounding BARNEYCONE Problem Solving | Owners Helping Owners 8 07-24-2017 11:10 AM
Grounding a Scamp Thee Jimbo Problem Solving | Owners Helping Owners 9 08-28-2015 07:39 PM
Grounding 120v to the frame... KyMoonshine Electrical | Charging, Systems, Solar and Generators 11 01-15-2015 02:28 AM
Solar Panel Set up Question - Grounding the panel? Anne H Electrical | Charging, Systems, Solar and Generators 2 09-07-2012 04:48 PM
Grounding Tail Lights with no White Wire Tim Bas Problem Solving | Owners Helping Owners 2 08-11-2010 03:27 AM

» Upcoming Events
No events scheduled in
the next 465 days.
» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 07:41 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.